Results 1 to 12 of 12
Thread: New System Issues?
    Apr 2010
    New System Issues?
    New Trane 14seer with VS blower installed Friday, Today's outdoor temperature reading was 90 degrees, 80 degrees attic temperature (Spray Foamed), But there's only a 10 degree difference measuring from the supply and return duct! Thermostat set @ 72, return duct reads 70 and supply reads 60 degrees. Unit was running over 25 minutes, 12 years old system was a R-22.
    Jan 2014
    New England
    Call the installing Contractor back, thinking you should have at least a one year labor warranty and have them recheck everything, and check the final field refrigerant charge is to manufacturers specifications. Usually manufacturers charge by subcooling, in cool mode if your system has a TXV metering device and even added superheat when the minimum OD and indoor temperatures are meet, system needs to stabilize for 15 minutes before making adjustments. Check for severely kinked lineset if new lineset run, blower speed is set to your ductwork etc.
    Two stage or one stage outdoor unit?
    What’s the brand and model numbers of both section?
    Double check return ducts are not sucking in hot attic air into the duct and mixing with the return air.
    Did they install AHRI matched systems?
    Make sure to register your system ( both sections ) as manufacturers warranty decreases if system never gets registered. California or Quebec need not be registered to receive the manufacturers maximum warranty.
    Southold, NY
    Quote Originally Posted by proofturn View Post
    90° OAT
    70° Return air
    What's the problem?
    Madison, WI/Cape Coral, FL
    MOre feed back. Return and supply temp/%RH! Temp/%RH in attic?
    Age of the home? Spray foam where??
    Regards Teddy Bear
    Apr 2010
    1. RH 56
    2.Return temperature 70
    3. Supply 60
    4. Second unit Supply temperature 53
    5. Attic temperature 80, did not get humidity reading.
    6. Attic roof deck spray foamed 6 inches.
    7. Age of the home 12 years old.
    As Bazooka Joe said, single or two stage?
    Apr 2010
    Single
    Could be they didn't set the blower to proper speed/CFM.
    Apr 2010
    The unit did not come with a TXV! Is this normal? The tech have to order the part, he stated that the pressure was unstable.
    Jan 2014
    New England
    Why don’t you post model numbers and brands of both parts, if it’s a furnace also post the indoor coil, furnace and outdoor section. Should be able to tell if they at least installed a AHRI matched system. Also typically the metering device is already installed at the factory.
    If it did not come with a TXV it probably came with a piston metering device? Reason for asking the coil model number and brand along with the other model numbers. Should be able to tell one way or another.
    Apr 2010
    Sorry for the confusion,
    14 SEER XR14 Heat Pump 2 Ton Trane 4TWR4024G1000*
    210435ECBFTEM6A0B24H21S*Multi-Position, Variable Speed Air Handler 2 Ton.Trane TEM6A0B24H21S* 20382JPB3V
    BAYHTR1505LUGB Heat Strip; Use with all TEM AHUs.
    Trane BAYHTR1505LUGB 2109B1GFFX
    TCONT824AS52DBXL824 Thermostat1
    Jan 2014
    New England
    https://www.google.com/url?sa=t&rct=...P4JhYGs16LTNW5
    “The unit did not come with a TXV! Is this normal“ maybe they told you that as they where having problems charging the system and replaced a perfectly good TXV?
    Dated 2017 should still be current? Says it comes with a TXV from the factory page 3 and 4
    Checking to see if system is a AHRI match,...
    Number 8938849 SEER 14.50 8.5 HSPF 12 EER on paper.
    To check
    https://www.google.com/url?sa=t&rct=...znxCFNAi8fJHHj
    Page 17 shows how to charge your system, wonder if they followed it as closely as possible? Course things need to line up, such as proper ductsize, CFM, static pressures
    https://www.google.com/url?sa=t&rct=...JJ-vYmXdPIL2h8