    Quote Originally Posted by flangatang7 View Post
    EDIT: For those looking for more information see below.

    Thank you!


    COMPRESSOR WHILST RUNNING
    these 3 don't tell you much except they are energized (hot)
    Ground to #5 on Potential Relay = 120v
    Ground to #1 on Potential Relay = 120v
    Ground to # 2 on Potential Relay = 120v

    Start Capacitor
    Ground to either terminal = 120v
    L1 (Common) to either terminal = 208v This tells you the terminals are powered through L2

    Run Capacitor
    Ground to either terminal = 208v
    L1 (Common) to either terminal 250v yep..... 250v

    L1 (Common) to Start winding = 250v

    L1 (Common) to Run winding = 208v Shows common is powered by L1, run is powered by L2

    L2 to Run winding = 0V
    proof of above, R and L2 are the same potential


    You should really take a class on electrical theory or read up on it, or get a senior tech to help you understand what you are looking at. It will also keep you safer!

  2. Likes flangatang7 liked this post.
  3. #22
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    7,951
    Post Likes
    Both windings are both powered by L1 & L2.

  4. Likes flangatang7 liked this post.
  5. #23
    Join Date
    Apr 2021
    Location
    Canada
    Posts
    23
    Post Likes
    Thread Starter
    Quote Originally Posted by BNME8EZ View Post
    proof of above, R and L2 are the same potential


    You should really take a class on electrical theory or read up on it, or get a senior tech to help you understand what you are looking at. It will also keep you safer!

    100% electrical has never been my strong point coming from Australia where we don't use 208v it's a little harder. I am trying and taking time out to learn though. Will see if I can find some classes.
    Can you explain to me what #5 does on the potential relay? All I can say for certain is it has 120v coming in from L1.

    Thanks for your response!

  6. #24
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    14,262
    Post Likes
    Quote Originally Posted by flangatang7 View Post
    100% electrical has never been my strong point coming from Australia where we don't use 208v it's a little harder. I am trying and taking time out to learn though. Will see if I can find some classes.
    Can you explain to me what #5 does on the potential relay? All I can say for certain is it has 120v coming in from L1.

    Thanks for your response!
    Terminal 5 is one end of the relay coil, it is the same power leg as C terminal on the compressor.

  7. Likes flangatang7 liked this post.
  8. #25
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    8,985
    Post Likes
    If you took that relay apart , you would be like .... oh .... so thats how it works

    Its just a magnetic coil , and a set of points

    The magnetic coil kicks the points open , and that drops out the Start Cap

  9. Likes flangatang7 liked this post.
  10. #26
    Join Date
    Apr 2021
    Location
    Canada
    Posts
    23
    Post Likes
    Thread Starter
    Quote Originally Posted by Snapperhead View Post
    If you took that relay apart , you would be like .... oh .... so thats how it works

    Its just a magnetic coil , and a set of points

    The magnetic coil kicks the points open , and that drops out the Start Cap
    Yep!

    Is it fair to say that the contact on terminal 1 opens once compressor reaches 75% running capacity?

  11. #27
    Join Date
    Sep 2013
    Location
    Wi
    Posts
    754
    Post Likes
    The voltage is generated in the start winding. If the pick up voltage of your relay is higher than what you measure it won't pick up. if you take 80% of it you are close to the proper pu voltage. I have used potential relays on farm motors to replace the switches in the end caps.

  12. #28
    Join Date
    Jan 2010
    Posts
    22,854
    Post Likes
    Would that be the centrifugal switches ?

  13. #29
    Join Date
    Jul 2019
    Location
    Oklahoma home its in the name
    Posts
    7,603
    Post Likes
    Quote Originally Posted by Snapperhead View Post
    I have gotten bad motors straight out the box ....

    Maybe you finally got yours
    I have got several over the last couple years.

    Sent from the Okie state usin Tapatalk

  14. #30
    Join Date
    Mar 2021
    Posts
    21
    Post Likes
    Quote Originally Posted by flangatang7 View Post
    100% electrical has never been my strong point coming from Australia where we don't use 208v it's a little harder. I am trying and taking time out to learn though. Will see if I can find some classes.
    Can you explain to me what #5 does on the potential relay? All I can say for certain is it has 120v coming in from L1.

    Thanks for your response!
    Is 208v in canada a twin phase circuit?

  15. #31
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    32,894
    Post Likes
    Quote Originally Posted by MadeInAustralia View Post
    Is 208v in canada a twin phase circuit?
    Here in the States we use the term single phase or 3 phase. 208 / 230 can be both. (I know gets confusing) 3 phase does not get start components.

  16. #32
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    32,894
    Post Likes
    A little reading material

    Hope it helps
    Attached Images Attached Images

  17. Likes R600a liked this post.
  18. #33
    Join Date
    Mar 2021
    Posts
    21
    Post Likes
    So you call a circuit with active and neutral 1ph

    and also call a circuit between two phases of a three phase supply 1ph as well?

  19. #34
    Join Date
    Jan 2010
    Posts
    22,854
    Post Likes
    YES

  20. #35
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    32,894
    Post Likes
    Quote Originally Posted by MadeInAustralia View Post
    So you call a circuit with active and neutral 1ph

    and also call a circuit between two phases of a three phase supply 1ph as well?
    Our 115 Volt can use any of the 3 phases with a Neutral. Phase to Phase is 208 / 230 Single phase

    I believe you use 230 volt for standard power supply. Each leg to ground shows 110 volts?

  21. #36
    Join Date
    Jan 2010
    Posts
    22,854
    Post Likes
    .
    Attached Images Attached Images  

  22. #37
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    32,894
    Post Likes
    Quote Originally Posted by VTP99 View Post
    .
    Now I'm confused!

  23. #38
    Join Date
    Mar 2021
    Posts
    21
    Post Likes
    Quote Originally Posted by pecmsg View Post
    Our 115 Volt can use any of the 3 phases with a Neutral. Phase to Phase is 208 / 230 Single phase

    I believe you use 230 volt for standard power supply. Each leg to ground shows 110 volts?
    415v 3ph standard supply, 230 any phase to neutral.

  24. #39
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    32,894
    Post Likes
    Quote Originally Posted by MadeInAustralia View Post
    415v 3ph standard supply, 230 any phase to neutral.
    OK that's the difference.

  25. #40
    Join Date
    Mar 2021
    Posts
    21
    Post Likes
    maneurope made a 415v phase to phase sump heater back in the day.