Results 1 to 10 of 10

Thread: Heatcraft walkin fridge. 404a/507

  1. #1
    Join Date
    May 2021
    Posts
    12
    Post Likes

    Heatcraft walkin fridge. 404a/507

    I'm about to leak check this unit. But I want to order refrigerant for it first but I'm unable to determine which refrigerant I should get. It says both 404a and 507. I could go give it a temp check but weather isn't cooperating. Is that the only way is to check it myself? Or does it matter. I'm assuming it does. Or does it?

  2. #2
    Join Date
    Jan 2020
    Location
    Winnipeg Canada
    Posts
    1,155
    Post Likes
    It's probably 404......
    That is if it's more than a year old.
    But I'd be checking the txv to be sure
    You don't squat with your spurs on.
    And you NEVER put the torches away before pressure testing.

  3. Likes flangatang7 liked this post.
  4. #3
    Join Date
    Sep 2002
    Posts
    29,865
    Post Likes
    Take both and return the one you don't need.

    PHM
    --------


    Quote Originally Posted by Joeshmowyaknow View Post
    I'm about to leak check this unit. But I want to order refrigerant for it first but I'm unable to determine which refrigerant I should get. It says both 404a and 507. I could go give it a temp check but weather isn't cooperating. Is that the only way is to check it myself? Or does it matter. I'm assuming it does. Or does it?
    PHM
    --------
    The conventional view serves to protect us from the painful job of Thinking

  5. Likes Restaurant mech liked this post.
  6. #4
    Join Date
    May 2021
    Posts
    12
    Post Likes
    Thread Starter
    That exactly what I ended up doing was checking the Txv. Super easy. Its 404a. Thank you!

  7. Likes flangatang7 liked this post.
  8. #5
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    4,977
    Post Likes
    404A and 507A are so similar in composition it doesn't even matter which one you use.

    Sent from my SM-G965W using Tapatalk

  9. #6
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    32,802
    Post Likes
    Quote Originally Posted by Joeshmowyaknow View Post
    That exactly what I ended up doing was checking the Txv. Super easy. Its 404a. Thank you!
    Now clearly mark the proper refrigerant on the unit!

  10. #7
    Join Date
    Jan 2010
    Posts
    22,831
    Post Likes
    Aren't the new power elements marked with both refrigerants ?
    Is it possible the TXV is original ( before R507 ) yet the condensing unit has been upgraded ?
    Also it's best to not mix refrigerants as I get the impression you want to top off the charge.

  11. #8
    Join Date
    May 2021
    Posts
    12
    Post Likes
    Thread Starter
    Yes. Definitely

  12. #9
    Join Date
    May 2021
    Posts
    12
    Post Likes
    Thread Starter
    Balloyd just said it doesnt matter which one I used but I know your not supposed to mix them. The TV has been replaced before and it says 504 and 404. So I'm assuming its 404 in there and went ahead and got a tank. Thank you all

  13. #10
    Join Date
    Jan 2010
    Posts
    22,831
    Post Likes
    I'll assume he was under the impression you were starting fresh because I know he knows better than to mix gasses.
    There's a chance he may have superpowers I'm not aware of.
    😃

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •