    Using Water to chill a condenser

    I apologize in advance for the long story. When we moved into our home 30 years ago, it had gas fired hot water baseboard heat and no air conditioning. I wanted air conditioning. Our domestic water supply is from a well that has 12 psi natural pressure at ground level, and a water temperature is 52-deg F. I added a secondary tap off the well casing, and ran an 1.25" line into the house. I purchased two coils that were designed for chilled water, and I have successfully used this to cool my 3800 square foot home for 30 years. It is getting to be time to replace the air handlers and the coils and there are several design issues I wanted to fix.

    1. While this systems cools well, it does not reduce the humidity enough. The delta temp at the coil is not high enough.
    2. Because this was a retrofit project, I ended up putting one cooling coil in the attic to support the second floor cooling. I have always worried about having water leaking in the attic, and that I have to blow the water out of the lines in the winter. So my preference is to switch to refrigerant based cooling instead of water.

    My question is, do they make residential HVAC systems where I could use a water based heat ex-changer instead of air to cool the condenser unit. This would enable me to use a much smaller compressor, and be able to run the coolant cycle at lower pressures and temperatures. Everyone wants to sell me a full blown heat pump, which I don't think I need. I have seen a "This Old House" episode where they used the swimming pool water and a heat ex-changer to cool/condense the refrigerant, but I have not be able to find a manufacturer willing to explore this.

    thanks in advance for the help!

  2. #2
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,328
    Post Likes
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  3. #3
    Join Date
    Jan 2020
    Location
    Winnipeg Canada
    Posts
    2,507
    Post Likes
    You are looking for what amounts to a geothermal household system.
    Both climate master and water furnace make excellent units.
    You'd also likely save on heating costs in the winter if you found a way to dispose of the used water

  4. #4
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    Sounds like a pump and dump set-up.

  5. Likes R600a liked this post.
  6. #5
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Quote Originally Posted by VTP99 View Post
    Sounds like a pump and dump set-up.
    But where’s the Dump?

  7. #6
    Join Date
    Feb 2021
    Posts
    6
    Post Likes
    Thread Starter
    Everyone,
    Thanks for the quick response. I will review the specs on those 2 manufacturers.

  8. #7
    Join Date
    Feb 2021
    Posts
    6
    Post Likes
    Thread Starter
    pecmsg,
    Originally the dump was directly to my pond. About 10 years ago, I rerouted it to my shop/out building, run it through a couple of coils, and now my shop is air conditioned as well.

  9. #8
    Join Date
    Feb 2021
    Posts
    6
    Post Likes
    Thread Starter
    We live in Michigan and the natural gas here is pretty cheap, especially compared to electricity. Also since my heat is a gas fired hydronic boiler, if the power goes out, I can still heat my house with a car battery and an inverter to power the furnace circulator.

  10. #9
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    Quote Originally Posted by pecmsg View Post
    But where’s the Dump?
    Post #7 😉

  11. #10
    Join Date
    Sep 2008
    Location
    VA
    Posts
    6,217
    Post Likes
    You can also fit a standard AC with a desuperheater. The better quality plate exchangers are expensive though. Strongly advise cupronickel with any option using a salt pool.
    "The only true wisdom is in knowing you know nothing" Socrates

  12. #11
    Join Date
    Apr 2003
    Location
    Maple Grove, MN
    Posts
    5,135
    Post Likes
    Quote Originally Posted by tonyzarger View Post
    ....This would enable me to use a much smaller compressor, and be able to run the coolant cycle at lower pressures and temperatures.
    It don't work that way. The compressor would be the same size weather it's water or air cooled. You may have meant the "condensing unit", and if so, then yes, it would be physically smaller. Also, generally speaking, your pressures/temperatures would need to be about the same also.

    Water cooled condensing units for refrigeration systems do exist. You could certainly use one of those to do what you want. You would need someone who's good with commercial hvac and refrigeration in order to get one installed. R410A (which is the refrigerant that most residential air conditioners use these days) probably won't be an option, therefore whatever evap coil you get will probably need to get converted to run on R404a or a R22 substitute. Also, these things aren't setup to work with 24V residential thermostats, and not just anybody would be able to figure out how to make it work. Not really that difficult or complicated, just different than what most residential guys normally have to deal with.

    It can be done. Finding someone to do it will likely be the hardest part.
    If at First You Don't Succeed, Skydiving Is Not for You.

  13. #12
    Join Date
    Feb 2021
    Posts
    6
    Post Likes
    Thread Starter
    Ammoniadog,
    thanks for that. I grew up in a plumbing and heating business and I am familiar with the thermostat issue. I agree that the condensing unit would be smaller when using water as the coolant. I have even looked at the plate type heat exchangers to perform that function. I have studied the phase diagram for several of the refrigerant types, that is how I concluded that using 50 degree-F water to cool the refrigerant would allow me to reach the saturation/condensation line at a lower pressure and this could potentially reduce the required size of the compressor. I also agree that this is not a typical application for residential work, and I may need a commercial HVAC designer to be involved. Silly me thinking I may be able to get something off the shelf.
    Thanks again for the feed back.

  14. #13
    Join Date
    Apr 2003
    Location
    Maple Grove, MN
    Posts
    5,135
    Post Likes
    Quote Originally Posted by tonyzarger View Post
    I have studied the phase diagram for several of the refrigerant types, that is how I concluded that using 50 degree-F water to cool the refrigerant would allow me to reach the saturation/condensation line at a lower pressure and this could potentially reduce the required size of the compressor.
    Most condensing units are designed to operate with a condensing temperature of around 85 degrees. Doesn't matter if it's air or water. On the water cooled units, there is a water regulating valve that will slow the water down to keep the refrigerant discharge pressure where it needs to be, so you really aren't gaining anything by having cold water. Air cooled condensing units that have to run in the winter (i.e. most walk-in coolers/freezers) work the same way. They have head pressure controls to keep the pressure up. Otherwise they won't work right. Just because it's zero degrees outside, it doesn't mean that the unit will be saving all kinds of money on the electric bill.

    I would recommend recalibrating your phase diagrams to 85 degrees and then see what kind of numbers you come up with.
    If at First You Don't Succeed, Skydiving Is Not for You.

  15. #14
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes
    I had a P&D job in NJ and we used the discharge water for a 'water feature' in the back yard. It was a really nice arrangement of statures and water cascades about 6' tall and maybe 10-12' diameter. The water drained away into a wooded area. I guess the top froze or something because one time when I got there for a no heat call they showed me their 'ice sculpture'. When the heat pumps were running the water sprayed straight up probably 5' higher that the water feature and in very cold weather it all froze into a gigantic ice-sculpture. It was pretty cool looking.

    We also did one at a large estate-type property in Philadelphia - actually past City Line Ave. so maybe Roxboro. The discharge water supplied antique fountains in the back yard. They (obviously <g>) flowed at random intervals - which somehow delighted the woman. I never saw it in the winter but I imagine it also froze over in really cold weather.


    PHM
    --------


    Quote Originally Posted by pecmsg View Post
    But where’s the Dump?
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  16. #15
    Join Date
    Feb 2021
    Posts
    6
    Post Likes
    Thread Starter
    ammoniadog,
    That was very useful information. that is also the difference between knowledge and experience. I will study what happens, if I constraint the condensing temperature to 85 degrees. That will definitely change the balance a bit. Thanks!

  17. #16
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes
    Maybe you should put down your pencil and crumble up that sheet of paper?

    Why don't you address the issues separately - which is how they should best be addressed anyway.

    Design your new hydronic cooling system along the same lines as the one you are presently happy with. And then design your dehumidification system as a separate entity. Leave the cooling that you already know you like as it is and just add a whole-house dehumidifier.

    Otherwise you are adding horsepower and complication that could both be easily avoided in your case.
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  18. Likes R600a liked this post.
  19. #17
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    Hold on now, if you lower condensing temperature/pressure you will gain in capacity.
    One only has to look at a compressor proformence chart to see that.
    I'll use this Copeland CRN5 as an example. Was quite popular back in the day.
    Can be used for A/C or medium temperature refrigeration.
    Look how your capacity goes up as the condensing temperature goes down.
    Attached Images Attached Images  

  20. #18
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    7,033
    Post Likes
    Your power consumption also drops as your compression ratio decreases.....although may amount to nickels per month in this case.

    I agree that this is trying to reinvent the wheel in a very expensive manner that is likely to not see the ROI that might be expected, especially if it breaks down.

    Sent from my SM-G965W using Tapatalk

  21. #19
    Join Date
    Apr 2003
    Location
    Maple Grove, MN
    Posts
    5,135
    Post Likes
    Quote Originally Posted by VTP99 View Post
    Hold on now, if you lower condensing temperature/pressure you will gain in capacity.
    One only has to look at a compressor proformence chart to see that.
    I'll use this Copeland CRN5 as an example. Was quite popular back in the day.
    Can be used for A/C or medium temperature refrigeration.
    Look how your capacity goes up as the condensing temperature goes down.
    Yes, but notice how the numbers on the left side of that chart don't go down to the 52° water that we have to work with. There definitely are savings to be had if the unit can always run at a constant 80° condensing temp vs. having to float up to whatever the outside air temperature is though.

    If at First You Don't Succeed, Skydiving Is Not for You.

  22. Likes R600a, VTP99 liked this post.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •