    Refrigeration theory question

    Refrigeration theory question;

    If we have two evaporators in parallel (equal piping sizes, lengths etc.), but one evaporator is hotter than the other, will it (or the cooler evaporator) see more flow? Wondering if the higher temp one (with correspondingly higher pressure) will ‘lock out’ flow through the lower temp one. Happy to provide more specifics...

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Made this irs own thread.

  3. #3
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Suction pressure & saturated temp will be the same. Can only be differences in ssh if no components in suction line. So only minor differences in coil lat if coils same.

  4. #4
    Join Date
    Nov 2009
    Location
    Richmond, working under tarps
    Posts
    1,051
    Post Likes
    Quote Originally Posted by Flane View Post
    Refrigeration theory question;

    If we have two evaporators in parallel (equal piping sizes, lengths etc.), but one evaporator is hotter than the other, will it (or the cooler evaporator) see more flow? Wondering if the higher temp one (with correspondingly higher pressure) will ‘lock out’ flow through the lower temp one. Happy to provide more specifics...
    what do mean by hotter?

  5. #5
    Join Date
    Apr 2003
    Location
    Maple Grove, MN
    Posts
    5,136
    Post Likes
    The expansion valve on the evap in the colder part of the box will be coasting along and maintaining it's superheat, while the expansion valve on the evap in the warmer part of the box will be struggling to bring down it's superheat, meaning that valve will be more open. Therefore, I'd say the "hotter" evap would have more refrigerant flow.

    This is assuming that these aren't pressure limiting (ZP) expansion valves. If they are, then the results would be flip-flopped, as the TXV on the warmer coil would likely be throttled closed to limit the flow.

    And if they were cap-tubes, then I'd say the one over the colder part of the box would have more flow, since it would have the bigger pressure differential through it.

    In other words, I guess it depends.

    Would you like to add the "more specifics" that you promised?
    If at First You Don't Succeed, Skydiving Is Not for You.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •