    Some questions about converting an Intellipak to 407C.

    Hi,
    With the rising cost of R22 I’ve been thinking about retrofit options. These intelipaks have CSHA 3-D scroll compressors. I’m wondering how difficult would it be to change the oil to POE on them? They have schrader ports or service valves for oil access but I was wondering if they have dip tubes so that the oil can be drained completely? Would appreciate any insight.

    We had a customer request a conversion to R422D a while back and had some serious issues with oil return. I’m thinking that may have been because the oil was not converted to POE. I imagine with only one out of two compressors running on a circuit POE would be needed for oil return.


    Sent from my iPhone using Tapatalk

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,745
    Post Likes
    Fix the leaks and stick with 22

  3. Likes R600a, Zamoramax, GoCougs, Nuclrchiller liked this post.
  4. #3
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Quote Originally Posted by pecmsg View Post
    Fix the leaks and stick with 22
    Yup.

  5. #4
    Join Date
    Nov 2011
    Location
    CO
    Posts
    17,439
    Post Likes
    Danfoss does not recommend retrofit on the 3D scrolls.

  6. #5
    Join Date
    Dec 2018
    Location
    Phoenix, AZ
    Posts
    788
    Post Likes
    Make R22 Great Again.


    Sent from my iPhone using Tapatalk

  7. Likes CEAS-AC-TECH liked this post.
  8. #6
    Join Date
    Jan 2020
    Location
    Winnipeg Canada
    Posts
    2,507
    Post Likes
    Or forget the oil change and run mo99.
    I've been running it for a few years now and it's been good zero issues, really close on capacity and no oil change

  9. #7
    Join Date
    Jul 2011
    Location
    DFW, TX.
    Posts
    2,826
    Post Likes
    Rs44b when the cost of r22 is up. You nor the client will be unhappy. No drier, oil, or metering device change needed.

    Sent from my LM-G820 using Tapatalk

  10. #8
    Join Date
    Apr 2021
    Location
    San Diego
    Posts
    56
    Post Likes
    Thread Starter
    Quote Originally Posted by Restaurant mech View Post
    Or forget the oil change and run mo99.
    I've been running it for a few years now and it's been good zero issues, really close on capacity and no oil change
    Looking at some of the refrigerant properties it looks like mo99 is the best, no oil change, replacement. But chemours does recommend changing the oil in certain situations. I’d want to change the oil on these Intellipaks since they can have impaired oil return during low load.


    Sent from my iPhone using Tapatalk

  11. #9
    Join Date
    Apr 2021
    Location
    San Diego
    Posts
    56
    Post Likes
    Thread Starter
    Quote Originally Posted by CEAS-AC-TECH View Post
    Rs44b when the cost of r22 is up. You nor the client will be unhappy. No drier, oil, or metering device change needed.

    Sent from my LM-G820 using Tapatalk
    I’ll have to look into that one, out of all the others I’ve compared MO99 looks like the best. I don’t trust not changing the oil on these systems so I figured I’d go with 407C since I’d be changing the oil and 407C looks like the best option in that situation.


    Sent from my iPhone using Tapatalk

  12. #10
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    7,033
    Post Likes
    Quote Originally Posted by Shane Bird View Post
    Looking at some of the refrigerant properties it looks like mo99 is the best, no oil change, replacement. But chemours does recommend changing the oil in certain situations. I’d want to change the oil on these Intellipaks since they can have impaired oil return during low load.


    Sent from my iPhone using Tapatalk
    You need to pay attention to some of the first few comments. There is some documentation where Trane does not recommend retrofits from R22 due to incidents of compressor failure with their compressors.

    Sent from my SM-G965W using Tapatalk

  13. #11
    Join Date
    Apr 2021
    Location
    San Diego
    Posts
    56
    Post Likes
    Thread Starter

    Some questions about converting an Intellipak to 407C.

    Quote Originally Posted by BALloyd View Post
    You need to pay attention to some of the first few comments. There is some documentation where Trane does not recommend retrofits from R22 due to incidents of compressor failure with their compressors.

    Sent from my SM-G965W using Tapatalk
    I understand, that’s something that I’ll be looking into and taking into consideration. I have seen Trane advertisements for a 407C intellipak conversion though. I’d definitely read any documentation and I plan on being very cautious.


    Sent from my iPhone using Tapatalk

  14. Likes CEAS-AC-TECH liked this post.
  15. #12
    Join Date
    Jul 2011
    Location
    DFW, TX.
    Posts
    2,826
    Post Likes
    Quote Originally Posted by BALloyd View Post
    You need to pay attention to some of the first few comments. There is some documentation where Trane does not recommend retrofits from R22 due to incidents of compressor failure with their compressors.

    Sent from my SM-G965W using Tapatalk
    Trane does not use rs44b either. The rest including 407c are garbage. Thats a fact. Lennox has tested rs44b and found it to be just like r22. We have all had this conversation. We all know trane wants to be proprietary, so...

    I encourage anyone to test rs44b out vs 407c. You'd find rs44b to be superior to al else but r22.

    Sent from my LM-G820 using Tapatalk

  16. Likes Shane Bird liked this post.
  17. #13
    Join Date
    Nov 2011
    Location
    CO
    Posts
    17,439
    Post Likes
    Quote Originally Posted by Shane Bird View Post
    I understand, that’s something that I’ll be looking into and taking into consideration. I have seen Trane advertisements for a 407C intellipak conversion though. I’d definitely read any documentation and I plan on being very cautious.


    Sent from my iPhone using Tapatalk
    Better put some wording in your quote that clears you of responsibility for any failed components after the conversion.

  18. Likes heatingman, GoCougs liked this post.
  19. #14
    Join Date
    Apr 2021
    Location
    San Diego
    Posts
    56
    Post Likes
    Thread Starter
    Quote Originally Posted by 71CHOPS View Post
    Better put some wording in your quote that clears you of responsibility for any failed components after the conversion.
    I think that’d be a good idea. Do you happen to have any literature warning against conversion. I know the MO99 literature requires an oil conversion with 3-D scrolls because they draw oil from the bottom of the compressor and with the poor miscibility of retrofit refrigerants that can lead to liquid refrigerant being drawn up instead of oil.


    Sent from my iPhone using Tapatalk

  20. #15
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,745
    Post Likes
    Quote Originally Posted by Shane Bird View Post
    I think that’d be a good idea. Do you happen to have any literature warning against conversion. I know the MO99 literature requires an oil conversion with 3-D scrolls because they draw oil from the bottom of the compressor and with the poor miscibility of retrofit refrigerants that can lead to liquid refrigerant being drawn up instead of oil.


    Sent from my iPhone using Tapatalk
    We will not be responsible for any damages to equipment due to your insistence to convert to a nonmanufacturer approved alternative refrigerant! This unit was designed and tested for use of R-22 only.

  21. #16
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    7,033
    Post Likes
    Quote Originally Posted by CEAS-AC-TECH View Post
    Trane does not use rs44b either. The rest including 407c are garbage. Thats a fact. Lennox has tested rs44b and found it to be just like r22. We have all had this conversation. We all know trane wants to be proprietary, so...

    I encourage anyone to test rs44b out vs 407c. You'd find rs44b to be superior to al else but r22.

    Sent from my LM-G820 using Tapatalk
    If you want to experiment knock yourself out.

    Pretty sure no one commenting in this thread cares either way about the conversion just because it is a Trane. It was more advice for fellow techs.

    If it works great.

    Sent from my SM-G965W using Tapatalk

  22. #17
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    If your customer wants to just leak cheaper refrigerant, then go for it. 1 compressor failure will wipe out any refrigerant cost savings. If they want to save money, fix the leaks, clean the coils (all of them) and maintain it properly.

  23. Likes CHAINIK, heatingman, pecmsg, Nuclrchiller liked this post.
  24. #18
    Join Date
    Jun 2009
    Location
    Florida
    Posts
    217
    Post Likes
    Several years ago Trane had an Intellipak refresh, R'newal program for converting the Intellipak I from R-22 to R-407c. As long as said unit has the CSHA compressors post 1996 and not the original CSHS 3-d scrolls. It needed an oil flush during replacement and only a certain percentage of mineral/POE mix allowed verified by lab testing, use of a refractometer, only a certain percentage of the original R-22 charge, new labels, pressure switches, schrader cores etc, etc. Trane is going to want to do all that themselves. I don't see the value (only liability) in doing that work yourself, personally. Like Jay said, fix it and maintain it.
    ...a relay... controlling a relay... controlling a relay... controlling a relay...

  25. Likes heatingman, Shane Bird liked this post.
  26. #19
    Join Date
    Apr 2021
    Location
    San Diego
    Posts
    56
    Post Likes
    Thread Starter
    Quote Originally Posted by 7point62 View Post
    Several years ago Trane had an Intellipak refresh, R'newal program for converting the Intellipak I from R-22 to R-407c. As long as said unit has the CSHA compressors post 1996 and not the original CSHS 3-d scrolls. It needed an oil flush during replacement and only a certain percentage of mineral/POE mix allowed verified by lab testing, use of a refractometer, only a certain percentage of the original R-22 charge, new labels, pressure switches, schrader cores etc, etc. Trane is going to want to do all that themselves. I don't see the value (only liability) in doing that work yourself, personally. Like Jay said, fix it and maintain it.
    Sounds reasonable.


    Sent from my iPhone using Tapatalk

  27. #20
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,457
    Post Likes
    I probably have the documentation somewhere, just don't have the time right now. Both Trane and ICOR stated absolutely do not use the 422 in a 3-D. I think the only approved conversions are with 407c, but they do have disclaimers. The first disclaimer goes something like: If you really have to convert or 22 is not available, then . . .

    Even on an Intellipac, we only use the original refrigerant.

    Spend the time with a quality leak checker. Do a pressure test with nitro observing the changes in temp. Pull a deep vacuum and be sure it holds.


    Quote Originally Posted by Shane Bird View Post
    I think that’d be a good idea. Do you happen to have any literature warning against conversion. I know the MO99 literature requires an oil conversion with 3-D scrolls because they draw oil from the bottom of the compressor and with the poor miscibility of retrofit refrigerants that can lead to liquid refrigerant being drawn up instead of oil.


    Sent from my iPhone using Tapatalk
    I do a triple evac with nitro to remove non condensables.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •