Thread: Some matchup help please....guys, please :).

  1. #1
    Join Date
    Oct 2011
    Location
    Culver, Oregon (Central OR)
    Posts
    4,052
    Post Likes

    Some matchup help please....guys, please :).

    So, I have an existing 3.5T Lennox coil and heat pump that I am replacing. The existing coil is 20" tall. Unfortunately, my Rheem matchup to an RP1442 is a 27" tall RCF4821 coil.

    I looked on AHRI, and it shows an RCF3624 as a matchup but looks like that one either isn't made anymore, or that Gensco doesn't supply it? Ruud?

    Anyway, I can get an RCF3621, but shows nominal tonnage at 3 tons. Am I getting myself in trouble going this route? Anybody have any better ideas on a 3.5 ton matchup that I can use a 20" tall coil on? I can't get Lennox stuff but I can get just about any other manufacturer. Looks like even the Aspen and Mortex coils are 24" or taller.

    Thoughts?
    "Life, Liberty, and Levin!"

  2. Likes catherinesmith liked this post.
  3. #2
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    11,888
    Post Likes
    Is there absolutely not room to cut a few inches off the plenum?

    I know sometimes there is not, just curious how dire the situation is.


    Sent from my iPhone using Tapatalk

  4. #3
    Join Date
    Oct 2011
    Location
    Culver, Oregon (Central OR)
    Posts
    4,052
    Post Likes
    Thread Starter
    Quote Originally Posted by heatingman View Post
    Is there absolutely not room to cut a few inches off the plenum?

    I know sometimes there is not, just curious how dire the situation is.


    Sent from my iPhone using Tapatalk
    No room whatsoever.
    "Life, Liberty, and Levin!"

  5. #4
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    11,888
    Post Likes
    If you can do an uncased coil, Im pretty sure that ADP has coils that are 19” tall in 3.5 ton.

    Model/Part # : M36E591


    Sent from my iPhone using Tapatalk

  6. Likes theoldscroll liked this post.
  7. #5
    Join Date
    Oct 2011
    Location
    Culver, Oregon (Central OR)
    Posts
    4,052
    Post Likes
    Thread Starter
    Quote Originally Posted by heatingman View Post
    If you can do an uncased coil, Im pretty sure that ADP has coils that are 19” tall in 3.5 ton.

    Model/Part # : M36E591


    Sent from my iPhone using Tapatalk
    Havent found a match for the equipment I get though. What matches can I get with those coils?
    "Life, Liberty, and Levin!"

  8. #6
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    11,888
    Post Likes
    Quote Originally Posted by Adlerberts-Protege View Post
    Havent found a match for the equipment I get though. What matches can I get with those coils?
    If you’re talking AHRI, I cant help you there.

    The AHRI testing is paid for by the OEM. And they may only test what they produce themselves, or only one coil for all I know.

    ADP is owned by Lennox. So I would think Lennox may test their equipment against them. But I dont know.


    Sent from my iPhone using Tapatalk

  9. #7
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    11,888
    Post Likes
    Back to your original post, that second coil you stated you can get, if its a listed AHRI match, then thats good enough no?


    Sent from my iPhone using Tapatalk

  10. #8
    Join Date
    Oct 2011
    Location
    Culver, Oregon (Central OR)
    Posts
    4,052
    Post Likes
    Thread Starter
    Quote Originally Posted by heatingman View Post
    Back to your original post, that second coil you stated you can get, if its a listed AHRI match, then thats good enough no?


    Sent from my iPhone using Tapatalk
    Too wide. 24" wont work, I need a 21".
    "Life, Liberty, and Levin!"

  11. #9
    Join Date
    Apr 2020
    Location
    Garner NC
    Posts
    3,516
    Post Likes
    Let me guess what you didn’t post.....old system is R-22...so the coil is shorter because it’s a lower speed refrigerant...
    The R410a is larger being a higher speed refrigerant needing more surface area for the same output..

    Or a compact/smaller matching AH instead of just coil
    Last edited by Unlimited1; 04-12-2021 at 10:11 PM.

  12. #10
    Join Date
    Oct 2011
    Location
    Culver, Oregon (Central OR)
    Posts
    4,052
    Post Likes
    Thread Starter
    Quote Originally Posted by Unlimited1 View Post
    Let me guess what you didn’t post.....old system is R-22...so the coil is shorter because it’s a lower speed refrigerant...
    The R410a is larger being a higher speed refrigerant needing more surface area for the same output..

    Or a compact/smaller matching AH instead of just coil
    Nope. Existing is R410. Lennox is a *****.
    "Life, Liberty, and Levin!"

  13. #11
    Join Date
    Oct 2011
    Location
    Culver, Oregon (Central OR)
    Posts
    4,052
    Post Likes
    Thread Starter
    Quote Originally Posted by heatingman View Post
    If you can do an uncased coil, Im pretty sure that ADP has coils that are 19” tall in 3.5 ton.

    Model/Part # : M36E591


    Sent from my iPhone using Tapatalk
    Oh, and now just checked. The outdoor units stop at 036. No higher.
    "Life, Liberty, and Levin!"

  14. #12
    Join Date
    Apr 2020
    Location
    Garner NC
    Posts
    3,516
    Post Likes
    https://www.evapco-alcoil.com/sites/...ct%20Guide.pdf

    Lookup Goodman coils also since its 20” tall

  15. #13
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    11,888
    Post Likes
    Sell them a new furnace if it would be shorter then existing.

    If not, then in the past when I worked for a York dealer and all the coils where 3 ft tall.

    On occasion I would remove from the case, make a new plenum, and then extend the top of the A up into the trunk an inch or so to make if fit.

    Way less then ideal. I always told the boss it would have been better to use an aftermarket coil.

    But he had the must be AHRI syndrome.

    Ironically, once a cased coil is removed from the case, its not technically a match anymore, or it derates the seer, cause they assume the plenum is un insulated.


    Sent from my iPhone using Tapatalk

  16. Likes R600a liked this post.
  17. #14
    Join Date
    Apr 2006
    Location
    Tyler, Tx
    Posts
    1,371
    Post Likes
    Give this guys a call:
    https://www.sustainablecoils.com/
    Philippians 4:13
    I can do all things in him that strengthen me.
    Apostle Paul inspired by GOD.

  18. #15
    Join Date
    Mar 2018
    Location
    Kansas Flatlands
    Posts
    746
    Post Likes
    Quote Originally Posted by Unlimited1 View Post
    https://www.evapco-alcoil.com/sites/...ct%20Guide.pdf

    Lookup Goodman coils also since its 20” tall
    I just don't like unmatched coils with heat pumps. Askin for trouble. Try ADP as suggested before. We have done it, but you kinda gotta throw the T&P chart out, and can expect high subcooling in the cooling mode, like 18 or 19 degrees sometimes. Hope it works out bro.

  19. #16
    Join Date
    Oct 2011
    Location
    Culver, Oregon (Central OR)
    Posts
    4,052
    Post Likes
    Thread Starter
    Quote Originally Posted by theoldscroll View Post
    I just don't like unmatched coils with heat pumps. Askin for trouble. Try ADP as suggested before. We have done it, but you kinda gotta throw the T&P chart out, and can expect high subcooling in the cooling mode, like 18 or 19 degrees sometimes. Hope it works out bro.
    I have decided to just pull the furnaces and restack them. This is adding a day to the project, but I was able to go back to the customer and get more money out of him. I need to redo the god-awful transitions above that the previous guy did anyway.

    I have another thread on this about the Emme zoning that is attached to these systems. The furnaces are twinned, the heat pumps have a silly twinning kit for them as well. The Emme zoning has this stupid air pump/logic system that has these stupid bladders to every heat run, it is way way way way over-engineered.

    I wish he had the coin to do some real zoning and get rid of the Emme garbage but that isn't happening.
    "Life, Liberty, and Levin!"