Originally Posted by
justin_
no they don’t have anything like that in the home (they have a boiler for heat) BUT just to make sure, I will double check to make sure they don’t have any room devices plugged in...
BUT YES!!! the powder does have shiny flakes in it!!!!
there is no condensate pump for this ductless unit
Right in.. I was trying to say I've cleaned that same crap out of 2 qt condo pump reservoirs on regular ducted systems.. never gave it a thought except one time I realize it caused the pump to fail or at least I thought it did
Sent from my SM-G998U using Tapatalk
Say "I just need a little Freon" one more time!

-

Originally Posted by
kdean1
Do you always shout in your posts?
Sorry.. my keyboard gets stuck like that once in a while.. I gave it a good swift shot of nitro and the keys unstuck.. I've spilled too many cups of coffee on it .
Sent from my SM-G998U using Tapatalk
Say "I just need a little Freon" one more time!

-

Originally Posted by
justin_
no they don’t have anything like that in the home (they have a boiler for heat) BUT just to make sure, I will double check to make sure they don’t have any room devices plugged in...
BUT YES!!! the powder does have shiny flakes in it!!!!
there is no condensate pump for this ductless unit
Boiler for heat could be your culprit. If it's releasing steam it's also likely releasing what I call boiler nasties which is a mixture of water and the remnants of the boiler piping. In other words the black water.
This steam can actually contain huge amounts of microscopic iron particles that actually remain airborne and will settle on the cold evaporator.
Then possibly clog up the drain.
I've never seen a case as bad as you are describing, but I did have one where an air handler was close to the steam vent and the iron in the air rotted out the a coil in 3 years.
You don't squat with your spurs on.
And you NEVER put the torches away before pressure testing.
-
Post Likes - 2 Likes, 0 Dislikes
-

Originally Posted by
justin_
no they don’t have anything like that in the home (they have a boiler for heat) BUT just to make sure, I will double check to make sure they don’t have any room devices plugged in...
BUT YES!!! the powder does have shiny flakes in it!!!!
there is no condensate pump for this ductless unit
any of those devices could be stand alone plug in the wall devices