    It’s done for at least 2 years do with it as you please

    My house. Pulled 120k 80% installed 80k 96% 2 stage. Thermostat and wire is temp (for the foreseeable future). The wire and local used was the old humidifier wire. Have yet to install my iwave r back. Humidifier not installed yet.

    In addition to furnace and coil, added 4 new returns to system and replaced all attic duct. I think that’s it.



    Old HX.



    I guess I realize I don’t have a pick with the doors on. O well....


    Sent from my iPhone using Tapatalk

  2. Likes dieseldude liked this post.
  3. #2
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    8,494
    Post Likes
    I'm trying to figure out the 2" ball valve.
    Is that thing in the intake??
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  4. Likes HVACmedic911 liked this post.
  5. #3
    Join Date
    Mar 2016
    Location
    Dayton Oh
    Posts
    6,632
    Post Likes
    Thread Starter

    It’s done for at least 2 years do with it as you please

    Lol looking at my post i need better pic. I also forgot my drain line is half ass waiting to do correct.

    No the coil is not brazed/sweet in as ima buy a new ac/hp and install hopefully in the next 30 days. And with such I’ll be running a new 7/8 lineset.

    Will pull 42k ac and put in a 36k ac/hp setup.

    I will say the ion (icp) stat is nice(ish).

    Old return into furnace was 14” square. New return is 33”x21”.

    Static per unit was .47.

    One day I will do a full start up lol.

    When your. It getting paid to do the work it seems to happen at a slower pace.

    Since install 2 months ago don’t think it’s come out of 1st stage...


    Sent from my iPhone using Tapatalk

  6. #4
    Join Date
    Mar 2016
    Location
    Dayton Oh
    Posts
    6,632
    Post Likes
    Thread Starter

    It’s done for at least 2 years do with it as you please

    Quote Originally Posted by dandyme View Post
    I'm trying to figure out the 2" ball valve.
    Is that thing in the intake??
    So yes it is on the intake. “When” I run my CA and if I cannot get my O2 down I can play with that. Odds are less than 50% I need it but I figured it’s easier now then later to put in.

    Yes that valve was $40 but wtf I will only replace the furnace in this house once.


    Sent from my iPhone using Tapatalk

  7. Likes kdean1 liked this post.
  8. #5
    Join Date
    Jul 2019
    Location
    Montana
    Posts
    260
    Post Likes
    Is it sitting on the coil case or is there a transition?

  9. #6
    Join Date
    Mar 2016
    Location
    Dayton Oh
    Posts
    6,632
    Post Likes
    Thread Starter
    Here she is with my dry fit pvc drain and stat wire blowing in the wind. I’ll get around to the fine details at some point. Maybe when I put my outdoor unit in and new lineset.


    Sent from my iPhone using Tapatalk

  10. #7
    Join Date
    Mar 2016
    Location
    Dayton Oh
    Posts
    6,632
    Post Likes
    Thread Starter
    Quote Originally Posted by 406Tinner View Post
    Is it sitting on the coil case or is there a transition?
    Transition. 22” furnace and 24” coil. 6” transition.


    Sent from my iPhone using Tapatalk

  11. #8
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    Quote Originally Posted by dandyme View Post
    I'm trying to figure out the 2" ball valve.
    Is that thing in the intake??
    Yes to regulate air flow on shot runs typically.

  12. #9
    Join Date
    Oct 2011
    Location
    Culver, Oregon (Central OR)
    Posts
    5,051
    Post Likes
    Quote Originally Posted by jbhenergy View Post
    Transition. 22” furnace and 24” coil. 6” transition.


    Sent from my iPhone using Tapatalk
    I wouldve made that transtion taller and the transiton between the filter and return drop smaller. Those N coils suck when restricted, as I'm sure you know.

  13. #10
    Join Date
    Mar 2016
    Location
    Dayton Oh
    Posts
    6,632
    Post Likes
    Thread Starter
    Swore I posted this the other day. Need to lay off the boos or something.

    This spring when I do my ac I’ll do the drain....




    Sent from my iPhone using Tapatalk

  14. #11
    Join Date
    Mar 2016
    Location
    Dayton Oh
    Posts
    6,632
    Post Likes
    Thread Starter

    It’s done for at least 2 years do with it as you please

    Quote Originally Posted by Adlerberts-Protege View Post
    I wouldve made that transtion taller and the transiton between the filter and return drop smaller. Those N coils suck when restricted, as I'm sure you know.
    Factory transition is 6” I believe. I just don’t like the 2 piece design so had the guys make the one.

    Need to install new drywall over the old as well. Holes and water stains from old flu. Just don’t feel like patching so I’ll put a whole new sheet in.

    Sent from my iPhone using Tapatalk

  15. #12
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,905
    Post Likes
    Quote Originally Posted by dandyme View Post
    I'm trying to figure out the 2" ball valve.
    Is that thing in the intake??
    The ball valve is a method taught for fine tuning the combustion process. When the PVC runs are short, the gases pass too quickly through the HX and the efficiency is reduced. By adjusting/restricting the intake while performing a combustion analysis the efficiency is maximized.
    I highly recommend the NCI combustion analysis class. It's a game changer.
    *********
    https://www.hvac20.com/ High efficiency equipment alone does not provide home comfort and efficiency. HVAC2.0 is a process for finding the real needs of the house and the occupants. Offer the customer a menu of work to address their problems and give them a probability of success.

    Find contractors with specialized training in combustion analysis, residential system performance, air flow, and duct optimization https://www.myhomecomfort.org/

  16. Likes VTP99 liked this post.
  17. #13
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,021
    Post Likes
    Quote Originally Posted by jbhenergy View Post
    Swore I posted this the other day. Need to lay off the boos or something.

    This spring when I do my ac I’ll do the drain....




    Sent from my iPhone using Tapatalk
    The spring, hell it was 80* here today.

  18. #14
    Join Date
    Sep 2007
    Location
    State College, PA
    Posts
    5,579
    Post Likes
    Quote Originally Posted by kdean1 View Post
    The ball valve is a method taught for fine tuning the combustion process. When the PVC runs are short, the gases pass too quickly through the HX and the efficiency is reduced. By adjusting/restricting the intake while performing a combustion analysis the efficiency is maximized.
    I highly recommend the NCI combustion analysis class. It's a game changer.
    That is a really cool way of getting proper combustion. I have had difficulty at times with gas furnaces getting the combustion levels I want to see and no way to adjust them.

    Very Cool indeed.
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?


    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241

    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113

  19. #15
    Join Date
    Mar 2016
    Location
    Dayton Oh
    Posts
    6,632
    Post Likes
    Thread Starter
    Quote Originally Posted by jtrammel View Post
    The spring, hell it was 80* here today.
    We like to see our new members gets 15 posts before they start criticizing others!!!!


    Good to see your name. Hope your doing well. Think the last I heard you were rehabbing a home or something like that.


    Sent from my iPhone using Tapatalk

  20. Likes heatingman liked this post.
  21. #16
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,021
    Post Likes
    Quote Originally Posted by jbhenergy View Post
    We like to see our new members gets 15 posts before they start criticizing others!!!!


    Good to see your name. Hope your doing well. Think the last I heard you were rehabbing a home or something like that.


    Sent from my iPhone using Tapatalk
    Im doing well, thanks for asking. Yea, I finished the majority of the house and we moved in about a year and a half ago. I’m still working on it some, in the process of rehabbing the master bed and bath right now which was put on the back burner for a while.

  22. #17
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    19,137
    Post Likes
    Quote Originally Posted by jbhenergy View Post
    So yes it is on the intake. “When” I run my CA and if I cannot get my O2 down I can play with that. Odds are less than 50% I need it but I figured it’s easier now then later to put in.

    Yes that valve was $40 but wtf I will only replace the furnace in this house once.


    Sent from my iPhone using Tapatalk
    You need to find a better valve supplier.

    I just bought a 2” pvc ball valve for 10 bucks at Menards.

    Hell a schedule 80 is like 20.

    Also, that 3rd 3” pvc drop, what’s that for? Line-set chase?


    Sent from my iPhone using Tapatalk

  23. #18
    Join Date
    Mar 2021
    Location
    Hendersonville NC
    Posts
    382
    Post Likes
    Quote Originally Posted by dandyme View Post
    I'm trying to figure out the 2" ball valve.
    Is that thing in the intake??
    2 inch ball valve used to dial in combustion analysis. lowers your excess air essentially creating a cleaner burn with less CO

  24. #19
    Join Date
    Mar 2016
    Location
    Dayton Oh
    Posts
    6,632
    Post Likes
    Thread Starter
    Quote Originally Posted by heatingman View Post
    You need to find a better valve supplier.

    I just bought a 2” pvc ball valve for 10 bucks at Menards.

    Hell a schedule 80 is like 20.

    Also, that 3rd 3” pvc drop, what’s that for? Line-set chase?


    Sent from my iPhone using Tapatalk
    Line set yes.

    It may have only been $20 I picked up a bunch of stuff that day and didn’t itemize it out. It is a schedule 80 as they didn’t have 40 in stock.


    Sent from my iPhone using Tapatalk

  25. #20
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes
    Still working . . . ten PM . . . . house is getting pretty chilly . . . . . no length of 2" long enough . . . . not a single damned 2" coupling Anywhere . . . and how the hell many times am I going to keep tripping over this ball valve! . . . . HEY! . . . . .

    I'm sure you know the drill. <g>

    PHM
    --------


    Quote Originally Posted by dandyme View Post
    I'm trying to figure out the 2" ball valve.
    Is that thing in the intake??
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  26. Likes joemach liked this post.
+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •