Results 1 to 3 of 3

Thread: Is refrigerant level sensor calibration required as part of annual shutdown maintena?

  1. #1
    Join Date
    Mar 2021
    Posts
    2
    Post Likes

    Is refrigerant level sensor calibration required as part of annual shutdown maintena?

    During my York Chiller annual shutdown maintenance, is it required to recalibrate the refrigerant level sensor?

  2. #2
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    7,274
    Post Likes
    Depending on what chiller you have, you may not be able to calibrate the FULL setpoint. You can double check the EMPTY setpoint but most of the time that doesn’t really change.

  3. #3
    Join Date
    Mar 2021
    Posts
    2
    Post Likes
    Thread Starter
    Thanks for responding. Recently my York chiller went through an annual shutdown maintenance. And right after that, the chiller kept tripping on the following faults
    1) Discharge superheat overload fault
    2) Low discharge superheat detected
    3) Evaporator- Low Pressure

    This is why I am asking. I wonder if it is the refrigerant level control valve that is faulty or it is because a refrigerant level sensor recalibration was not done.