    Honeywell BACnet FF TB3026 Stat

    Reviewed every point on the BACnet FF Tstat. Need to find a writable point that will permit the T-Stat to operate a Two Position Normally OPEN , 2 Position Fan coil Unit Valve,
    Most F.C.U. Valves are normally closed, we have a situation where some units were piped in with a Normally Open Valve. Twenty in all
    There is no JACE or Supervisor yet, to overwrite B.O.-3 ,So that it will energize on No call for heat and Cool. Application 15 works great, 2 Pipe FCU, With two position Open/Close valve, however, the N.O. valve Actuator is energized when it should be not. Web squad has not returned any suggestions yet. Do not think the firmware can be altered.

  2. #2
    Join Date
    Sep 2013
    Posts
    2,065
    Post Likes
    Add a relay to reverse the output.


    Sent from my iPad using Tapatalk

  3. #3
    Join Date
    Sep 2007
    Location
    Kenilworth NJ
    Posts
    7,926
    Post Likes
    That is a fun, low tech solution. Sometimes I also find myself looking so hard I miss the easy thing.