Thread: Receiver goes back into cond coil ?

  1. #41
    Join Date
    Aug 2013
    Location
    Omaha
    Posts
    3,814
    Post Likes
    Quote Originally Posted by BobFrost View Post
    On condensing units wothout subcooling circuit there is no check valve.
    Why is here necessary?
    Because those condensing units.. like heatcraft, russell, trenton, etc have actually good low ambient controls like a headmaster or variable speed fans so theres no need for a check valve.

    Unlike a crappy low cost, cheaply designed kolpak unit.

    Sent from my SM-G975U using Tapatalk

  2. Likes VTP99 liked this post.
  3. #42
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    That check valve also prevents migration.

  4. Likes R600a, BALloyd liked this post.
  5. #43
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    I wonder who figured out the check valve thing. Can they get away with less total charge that way or is it about the same?

  6. #44
    Join Date
    Apr 2008
    Location
    Michigan
    Posts
    148
    Post Likes
    Quote Originally Posted by Snapperhead View Post
    Ok .... but why

    Whats the benefit

    They have worked forever without them

    Does it stop the bubbles when the fan kick on and off ? I did notice there werent any bubbles ....
    It's not really a question of them working/not working, they will work fine with or without. It's an efficiency kick. The subcooling circuit, the check valve preventing temporary flashing at the expansion valve, variable speed fans, etc. are all a direct result of the AWEF mandates imposed on the industry in 2020. The cheaper units in particular had to make some efficiency improvements in order to meet the new regulations.

  7. #45
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    Quote Originally Posted by itsiceman View Post
    I wonder who figured out the check valve thing. Can they get away with less total charge that way or is it about the same?
    I would say this style of x-tra SC'ing cond unit thing needs a little x-tra freon for the slightly x-tra liquid line length.

  8. #46
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Thread Starter
    Thats just what we need .... more crap that can go bad

  9. Likes R600a liked this post.
  10. #47
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    Quote Originally Posted by TechmanTerry View Post
    I would say this style of x-tra SC'ing cond unit thing needs a little x-tra freon for the slightly x-tra liquid line length.
    Maybe it's a wash then. I can't see them adding the check valve with the sole purpose of it running better with the fan cycle.

  11. #48
    R600a's Avatar
    R600a is offline Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    31,873
    Post Likes
    Quote Originally Posted by itsiceman View Post
    Maybe it's a wash then. I can't see them adding the check valve with the sole purpose of it running better with the fan cycle.
    Unless that's what it took to get them to break down past warranty instead of in warranty.

    Sent from the Okie state usin Tapatalk
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

  12. #49
    Join Date
    Dec 2014
    Posts
    3,941
    Post Likes
    Quote Originally Posted by TechmanTerry View Post
    That check valve also prevents migration.
    Hey Terry!

    Sent from my SM-G950U using Tapatalk

  13. Likes R600a, BALloyd, bacciagalupe liked this post.
  14. #50
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    I've always added a check valve when adding a HPC valve.
    I believe it's in a Sporlan bulletin as well.
    As for the migration I've never added a heat tape to a condenser but I have on a receiver.

  15. #51
    Join Date
    Apr 2003
    Location
    Maple Grove, MN
    Posts
    5,136
    Post Likes
    Interesting. Thanks for posting that icy78. But why would we care if refrigerant migrates from the "warm receiver to the cold condenser" during the off cycle? I suppose it's so you don't have a few seconds with a flashing sight glass upon startup again? Doesn't seem like a big deal to me. Am I missing anything?

    I'm guessing the scroll compressor has a check valve built into it as well, correct?
    If at First You Don't Succeed, Skydiving Is Not for You.

  16. #52
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    Quote Originally Posted by ammoniadog View Post
    Interesting. Thanks for posting that icy78. But why would we care if refrigerant migrates from the "warm receiver to the cold condenser" during the off cycle? I suppose it's so you don't have a few seconds with a flashing sight glass upon startup again? Doesn't seem like a big deal to me. Am I missing anything?

    I'm guessing the scroll compressor has a check valve built into it as well, correct?
    They have a hard time starting back up when it cold out.

  17. #53
    Join Date
    Apr 2008
    Location
    Michigan
    Posts
    148
    Post Likes
    Quote Originally Posted by Snapperhead View Post
    Thats just what we need .... more crap that can go bad
    Can't argue with that!🙂

  18. #54
    Join Date
    Apr 2008
    Location
    Michigan
    Posts
    148
    Post Likes
    I may be wrong here but here's what I think they are trying to accomplish.

    We often install outdoor units with heated and insulated recievers around here for extreme cold conditions. Its necessary to keep receiver pressures high enough to come out of pumpdown after long off periods when it's -20F or colder outside. A unit with an HPR or "headmaster" acts as a quasi-check valve since it closes to the condenser when the receiver pressure drops, thus helping prevent (but not necessarily eliminating) migration back into the condenser which would happen readily when its cold outside since the condenser is obviously designed for heat rejection. Since this unit has only fan cycling they may have added it to discourage migration and low head pressure when it comes out of pumpdown. I have seen several of these units however that work just fine in pretty cold weather without the check valve. I think it also serves the purpose of preventing flashing due to the fan cycling as mentioned too.

  19. Likes UmmScott liked this post.
  20. #55
    Join Date
    Apr 2021
    Location
    East ohio area
    Posts
    21
    Post Likes
    Would there be a different best practice for charging this unit in regards to this design?
    Not sure if there would be any idiosyncrasies

  21. #56
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,749
    Post Likes
    Quote Originally Posted by Swf View Post
    Would there be a different best practice for charging this unit in regards to this design?
    Not sure if there would be any idiosyncrasies
    Normal charging when warm outside but extra refrigerant is needed for the flooded condenser. Its in the IOM.

  22. Likes BobFrost liked this post.
  23. #57
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    The need for a receiver heater is based on 0*F and colder and a few other reasons.

  24. #58
    Join Date
    Apr 2008
    Location
    Michigan
    Posts
    148
    Post Likes
    Quote Originally Posted by pecmsg View Post
    Normal charging when warm outside but extra refrigerant is needed for the flooded condenser. Its in the IOM.
    Except it doesn't have an HPR valve?

  25. #59
    Join Date
    Jun 2012
    Posts
    33
    Post Likes
    Quote Originally Posted by pecmsg View Post
    ICM control will work with that motor.
    Which one do you prefer?

  26. #60
    Join Date
    Nov 2009
    Location
    Richmond, working under tarps
    Posts
    1,051
    Post Likes
    Quote Originally Posted by ttowngremlin View Post
    Which one do you prefer?
    you should be able to pick the one best for your application

    https://www.icmcontrols.com/products/?category=41

+ Reply to Thread
Page 3 of 4 FirstFirst 1234 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •