    Had a furnace that would overheat in 2nd stage and would reset the ecobee stat every time it overheated for like 10 minutes.
    Tesp was around 1.1 inwc
    Static between the filter and the return drop elbow was .6 to .7 inwc!
    Put in a trane cleaneffects and now my tesp is .4 inwc
    Not the most impressive job in the world but I was pleasantly surprised with the impact of what I did and figured I'd share it since the wall of pride has been dead lately
    Wish the apprentice didn't pucky the pittsburgh joints though!
    Attached Images Attached Images   

  2. Likes ksefan liked this post.
  3. #2
    Join Date
    Jan 2012
    Location
    Missouri, USA
    Posts
    3,963
    Post Likes
    Nice work. I love Clean Effects. Great TESP.

  4. Likes 406Tinner liked this post.
  5. #3
    R600a's Avatar
    R600a is offline Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    31,872
    Post Likes
    I am impressed. I would not have guessed thst that was an improvement.

    Sent from the Okie state usin Tapatalk
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

  6. #4
    Join Date
    Oct 2011
    Location
    Culver, Oregon (Central OR)
    Posts
    5,051
    Post Likes
    Quote Originally Posted by R600a View Post
    I am impressed. I would not have guessed thst that was an improvement.

    Sent from the Okie state usin Tapatalk
    It won't be after a month. OP, make sure the customer knows those things are very maintenance dependant.

  7. #5
    Join Date
    Apr 2020
    Location
    Garner NC
    Posts
    10,833
    Post Likes
    Good job! On my end, I never put the AH on the ground and have it on a 18-24” tall casket (matched to the AH size) with 4” solid concrete block with 4x4 vibration isolators on it. I get the full return airflow that way from under the unit...every little bit helps..

    I’ve seen plenty of flooded homes as well over the years..that’s why I don’t leave them on the floors to give them a better “survival” chance..

  8. #6
    Join Date
    Jul 2019
    Location
    Montana
    Posts
    260
    Post Likes
    Thread Starter
    Oh the furnace was exsisting, I quoted replacements but the customer just wanted to fix the airflow issue. The before picture makes it look like a different furnace I suppose haha

  9. #7
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    22,111
    Post Likes
    Good looking job. I think the improvement was from the difference at the elbow not the TCE. I have installed around a dozen TCE and have not been impressed. I see more dust in the blower compartment with the TCE than the Aprilaire that was in there before.

  10. #8
    Join Date
    Jul 2019
    Location
    Montana
    Posts
    260
    Post Likes
    Thread Starter
    Getting away from that elbow was the saving grace in my opinion. Sold the CE because of what they claim to do have only done a couple because of the cost of them so time will tell for me how they hold up

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •