Results 1 to 16 of 16

Thread: Trane TD7 can not communicate with UC800

  1. #1
    Join Date
    Sep 2011
    Location
    Guangzhou,China
    Posts
    81
    Post Likes

    Trane TD7 can not communicate with UC800

    Hi, I buy a used TD7 which used to connect to UC600. Now I am going to connect it to a UC800 in RTHD. When I power it up and connect it with a ethernet cable to the UC800, the screen show "Display Failed to Establish Communication". The UC800 loads RTHD version 6.00 software. Which parts I do wrong?

    Regards

  2. #2
    Join Date
    Nov 2006
    Posts
    74
    Post Likes
    The Ethernet cable is not connected between the display and the UC800.
    • The UC800 is not powered.
    • The UC800 just has the backup application running as received from the vendor. Download the RTHD application software.
    • The UC800 has an invalid configuration. Download a valid configuration using the Tracer TU service tool. (I have meet it before. UC800 firmware is CTV.)

  3. #3
    Join Date
    Sep 2011
    Location
    Guangzhou,China
    Posts
    81
    Post Likes
    Thread Starter
    I don't know exactly what is "Download a valid configuration". Is it OK to configurate the UC800 as new one?

  4. #4
    Join Date
    Nov 2018
    Posts
    12
    Post Likes
    You need to clear the UC800 and upload a valid configuration for that specific chiller.

  5. #5
    Join Date
    Sep 2011
    Location
    Guangzhou,China
    Posts
    81
    Post Likes
    Thread Starter
    I keep pressing the service button when power up the uc800, and Confirn the operation in tracer tu. After the controller has been reset, I open a CH530 configuration in TU And save it into UC800. But the TD7 keeps showing comunication error.

  6. #6
    Join Date
    Nov 2014
    Location
    Australia
    Posts
    152
    Post Likes
    Hmmm, so you are connecting to the UC800 via TU program?

  7. #7
    Join Date
    Sep 2011
    Location
    Guangzhou,China
    Posts
    81
    Post Likes
    Thread Starter
    Yes. Is it the right way?

  8. #8
    Join Date
    Nov 2014
    Location
    Australia
    Posts
    152
    Post Likes
    If you have TU, then you should be able to fully reset the UC800, then configure it as a RTHD. if you have it configured as a CTV, then it wont work.

  9. #9
    Join Date
    Nov 2006
    Posts
    74
    Post Likes
    it's right. I have meet it before. UC800 firmware is CTV

  10. #10
    Join Date
    Nov 2014
    Location
    Australia
    Posts
    152
    Post Likes
    TD7 screens are for screw chillers, not CTV (Centravac)

  11. #11
    Join Date
    Nov 2014
    Location
    Australia
    Posts
    152
    Post Likes
    UC800 can be many things to many chillers But CTV no for RTHD.

  12. #12
    Join Date
    Sep 2011
    Location
    Guangzhou,China
    Posts
    81
    Post Likes
    Thread Starter
    I clear the UC800 and set it to RTHD v6.0. Still not work.


    I connect my PC to TD7 via ethernet cable. In the Wireshark, I can see the TD7 having a static IP, 192.168.1.30, and looking for 192.168.1.4.


    While UC800 looking for a DHCP Server.

  13. #13
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    2,318
    Post Likes
    The problem isn’t your UC800, it’s your display. You bought a display configured for a UC600, not UC800. I hope you didn’t screw up the settings in your UC800…
    The 2nd most important amendment is to protect the 1st....

    Free Air Conditioner Sizing Chart

  14. #14
    Join Date
    Sep 2011
    Location
    Guangzhou,China
    Posts
    81
    Post Likes
    Thread Starter
    So is there a way to update the TD7 software or re-configure the TD7 for UC800?

    Regards.

  15. #15
    Join Date
    Oct 2005
    Location
    USA
    Posts
    569
    Post Likes
    What exactly are you trying to do? If you have a RTHD with a UC800 that means it already has a TD7 display.
    RTFM!!!

  16. #16
    Join Date
    Sep 2011
    Location
    Guangzhou,China
    Posts
    81
    Post Likes
    Thread Starter
    I want to upgrade a CH5CH-based RTHD to UC800 with TD7

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •