    Hello,
    I am trying to find an equation to figure out the amount of moisture being produced/added to an air stream. The situation is this:
    10lb/hr Nortec RH2+ steam humidifier
    2k cfm with 3 zones(each zone bypasses in order to keep from freezing the A coil etc)
    Distribution tube is in the return(not by choice)
    Humidifier is rated at 100% when drawing 16 amps, which it is.
    no ERV or HRV connected
    Space temp is maintained at 67
    Space has not been able to get over 37%
    FYI, the water has been tested due to a tank failing in less then 1 month. Water is within spec. Conductivity is at the low end, and salt was added to the tank to help in this matter
    This one is starting to get to me.
    Madison, WI/Cape Coral, FL
    I am impressed with 37%RH. As you go higher indoor %RH, expect condensation on the coldest windows in the home. Here is a good calculation program for moisture and heat changes to a air stream.
    Keep us posted.
    Regards Teddy Bear
    https://efficientcomfort.net/asp/Psy...ilCalc_Web.asp
  3. Likes Creed529 liked this post.
  4. #3
    Keep us posted.
    Regards Teddy Bear
    I am adding calc with numbers added.Name:  moisture added by humidifier maked up.png
    The in/out inputs predict 6 lbs. per hour.
    Measure return air temp/%RH and supply temp/%RH with 2,000 cfm to get an estimate.
  5. #4
    Jan 2021
    New Hampshire
    Thanks a lot! I will be sure to save this!