    Don't diy

    Customer installed a furnace that they bought From home depot I guess. It wouldn't do anything, they couldn't figure it out, they call me.
    So I find a neutral wire was not in a wire but. Now the furnace turns on, but fuse blows immediately. Cool. Find the old two wire tstat wire was clamped so tight that the coating sheered so it was grounded on the furnace. Get that handled and now the furnace lights, blower tries to turn but the fan wheel is grinding on the housing and needs aligned. Now we start up and the fan turns on, and I hear in the drastically undersized and poorly installed return ducting- bing, bang, boom. Open the filter access, and a dogs ball made it down the trunk, past the filter, and fortunately was stopped by the furnaces metal.
    So the filter is wrongly sized so much a rubber ball can get through, nevermind about dust
    5 ton furnace I believe, 110k btu and the return has 4 six inch rounds supplying it, and (if you can see in the pictures) is cut into the back of the furnace (I've never seen a manufacturer allow this), and the opening is roughly 8x12
    The vent looks awfull. I'm not sure how they got away with it but somehow there's a tag of approval from the city on they're water heater they put in at the same time. Look at the pics and tell me, that flexy crap (is that legal for appliance venting??) Is definitely not 6" from combustibles, and not only that, we have roughly 160k btus going into that tiny oval asbestos chimney? How did they get away with that?
    Oh and he didn't understand why I had to charge money.. "it's a brand new furnace!"... Uh ya, I didn't put it in bud, just cuz it's new doesn't mean I give away free work
    Attached Images Attached Images          

  2. #2
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    13,169
    Post Likes
    Isn't the chimney liner supposed to be in the ...chimney?
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  3. Likes joemach, Lahrs liked this post.
  4. #3
    Join Date
    Nov 2014
    Location
    Portland, Oregon, United States
    Posts
    539
    Post Likes
    Damn that looks like.dr octopus from the old spider man comics

    Sent from my SM-N986U using Tapatalk

  5. #4
    Join Date
    Feb 2018
    Location
    Bay Area, Ca
    Posts
    1,361
    Post Likes
    Gah. The 2nd pic didn't come through for me. Im betting its the top of the water heater. Its pretty bad. As much as I want to say I would only replace not repair.. i would want to see it work properly just to say all this... was wrong.
    About the only thing I've seen worse was a 4ton 100k horizontal with a 14" cut into the bottom shoved in until the duct touched the blower and had all 6 in ducts. Fed from a 6" trunk line.. 1-6" take off.

    Sent from my SM-N960U using Tapatalk

  6. #5
    Join Date
    Jul 2019
    Location
    Montana
    Posts
    127
    Post Likes
    Thread Starter
    I thought I took a pic of the wh but I guess not, you can see most of its venting though.
    It's brand new like the day was this week with city tag on it, which means somehow they passed inspection...

  7. #6
    Join Date
    Jul 2019
    Location
    Oklahoma home its in the name
    Posts
    7,551
    Post Likes
    Quote Originally Posted by 406Tinner View Post
    I thought I took a pic of the wh but I guess not, you can see most of its venting though.
    It's brand new like the day was this week with city tag on it, which means somehow they passed inspection...
    The inspector made some extra one that one.

    Sent from the Okie state usin Tapatalk

  8. Likes Zamoramax, stumpdigger liked this post.
  9. #7
    Join Date
    Feb 2018
    Location
    Bay Area, Ca
    Posts
    1,361
    Post Likes
    Quote Originally Posted by R600a View Post
    The inspector made some extra one that one.

    Sent from the Okie state usin Tapatalk
    Signed it from Starbucks 3 towns over.

    Sent from my SM-N960U using Tapatalk

  10. #8
    Join Date
    Jul 2019
    Location
    Oklahoma home its in the name
    Posts
    7,551
    Post Likes
    Quote Originally Posted by Zamoramax View Post
    Signed it from Starbucks 3 towns over.

    Sent from my SM-N960U using Tapatalk
    Yep.

    Sent from the Okie state usin Tapatalk

  11. #9
    Join Date
    Jul 2019
    Location
    Oklahoma home its in the name
    Posts
    7,551
    Post Likes
    A lot of thst looks better than some local installs i have seen displaying their company pride sticker proudly.

    Sent from the Okie state usin Tapatalk

  12. #10
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    8,164
    Post Likes
    That asbestos oval ir really special. Just where does it go to?
    Is that the "chimney"?
    United Technologies should be so proud.
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  13. #11
    Join Date
    Jul 2019
    Location
    Montana
    Posts
    127
    Post Likes
    Thread Starter
    I run into that asbestos stuff every once in a while. However most of the time when I see it it's abandoned and bigger

  14. #12
    Join Date
    Jan 2014
    Location
    New England
    Posts
    8,848
    Post Likes
    What?...it’s not a Goodman.

    “ United Technologies should be so proud “...No such company anymore, UTC jettisoned Carrier and the other HVAC brands along with Otis Elevator that where under their umbrella when they merged with Raytheon last year, focusing on Aerospace. New company is called Raytheon Technology Corporation. Furnace certainly could have been made under their watch thou...

  15. #13
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    7,219
    Post Likes
    did they teflon tape the union threads too?
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

  16. #14
    Join Date
    Nov 2006
    Location
    Athens, Ohio
    Posts
    8,622
    Post Likes
    I might have just red tagged it and walked away.

    Was a combustion analysis performed to keep them from dying after you left? Common venting an 80% furnace with a natural draft water heater has an enormous risk of spilling at the draft hood.
    *********
    https://www.hvac20.com/ High efficiency equipment alone does not provide home comfort and efficiency. HVAC2.0 is a process for finding the real needs of the house and the occupants. Offer the customer a menu of work to address their problems and give them a probability of success.

    Find contractors with specialized training in combustion analysis, residential system performance, air flow, and duct optimization https://www.myhomecomfort.org/


    Site member map HERE!

  17. Likes joemach liked this post.
  18. #15
    Join Date
    Jun 2020
    Location
    CHICAGO IL
    Posts
    1,386
    Post Likes
    I like galvanized gas pipe.
    " The more I learn the more I realize how much I don't know"

  19. #16
    Join Date
    Aug 2001
    Location
    Pavilion, NY
    Posts
    3,669
    Post Likes
    Other than the tee connection and transite pipe i don't see an issue with the venting? It is a listed connector i believe.
    Of course the back return and electrical connection is terrible

    Sent from my SM-N960U using Tapatalk
    ...

  20. #17
    Join Date
    Apr 2010
    Location
    Texas
    Posts
    784
    Post Likes
    Quote Originally Posted by 406Tinner View Post
    Is definitely not 6" from combustibles,
    Where is that required? Seems like a lot.


  21. #18
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    4,987
    Post Likes
    Quote Originally Posted by CHAINIK View Post
    Where is that required? Seems like a lot.
    Everywhere with single wall pipe. 1 inch for B Vent.

    Sent from my SM-G965W using Tapatalk

  22. Likes Zamoramax liked this post.
  23. #19
    Join Date
    Feb 2018
    Location
    Bay Area, Ca
    Posts
    1,361
    Post Likes
    If I'm not mistaken that flexvent is considered b-vent... we don't use it. Matter of fact I have rarely seen it. Its the unicorn of venting... the box stores sell it but none of my suppliers do.

    Sent from my SM-N960U using Tapatalk

  24. #20
    Join Date
    Apr 2010
    Location
    Texas
    Posts
    784
    Post Likes
    Quote Originally Posted by BALloyd View Post
    Everywhere with single wall pipe. 1 inch for B Vent.

    Sent from my SM-G965W using Tapatalk
    That flex pictured appears to be B-vent, judging by its connections.
    http://www.mtlfab.com/media/L1940.pdf