    Taylor 791

    I need help on this Taylor 791-27 machine. It is air cooled, 208-230v, 1 phase, 30 amp. When turning the main switch on and pressing the standby & auto buttons the fan, beater motor come on, but the compressor does not start. When testing the compressor pushing contactor in the compressor starts.

  2. #2
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Start with a wiring diagram.

  3. #3
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,749
    Post Likes
    Quote Originally Posted by VTP99 View Post
    Start with a wiring diagram.
    and stop pushing in the contactor, that's what your volt ohm amp meter is for!