Results 1 to 5 of 5

Thread: Opinion on repair time

  1. #1
    Join Date
    Dec 2020
    Posts
    1
    Post Likes

    Opinion on repair time

    I manage a 20 month old self storage facility and we had two (of 12) Rheem air handlers, model #RH1P4821STANDA, which needed repairs. I used a reputable HVAC firm to perform the work and the repair on one of the units was performed as quoted. The repair quoted for the second unit was quoted as having a refrigerant leak in the evaporator coil. The evaporator coil and the liquid line dryer were to be replaced and the evaporator coil would be provided by the manufacturer under warranty. Upon completion the unit would be charged with refrigerant.

    The technician who initially diagnosed the problem was not the same technician to perform the repair/replacement work. When the technician visited the property to perform the repairs he instead discovered a flare joint at the TXV was leaking and not a bad evaporator coil. He repaired the leak, pulled a vacuum on the system, and charged the system with new refrigerant.

    When I received the invoice I expected there to be less time involved for the actual repair that took place and a subsequent reduction in the originally quoted amount. When I questioned this I was told repairing the leak was as time consuming as replacing the evaporator coil, liquid line dryer, pulling the vacuum and replacing the refrigerant so the cost was the same. In my limited understanding of what had to happen I believe the vacuum and refrigerant replacement would be required in either scenario.

    Thoughts?

  2. #2
    Join Date
    Sep 2015
    Location
    Ontari-ari-ari-o
    Posts
    2,372
    Post Likes
    It is the same amount of work. The only thing he didn't have to do was carry a coil to and from his truck. By the sounds of it the job was done properly since they knew enough to replace the filter drier.

  3. #3
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    11,887
    Post Likes
    If it was a leaking flare joint, thats a field made connection.

    Pending on terms of original labor warranty of the equipment, that possibly should be covered.

    You stated the coil would be under warranty. So logic follows that a general workmanship labor warranty may have similar term

    Sent from my SM-G930V using Tapatalk

  4. #4
    Join Date
    Apr 2006
    Location
    Tyler, Tx
    Posts
    1,371
    Post Likes
    That unit is a solder in unit, so no field installed flares, unless they used a flared filter drier.
    He may be calling the TXV connections flares, which can leak from factory.
    Based on what you said, it is the same about of time to either job correctly,: Recover refrigerant, fix leak, evacuate systems (pull vacuum), recharge, and do operational check.
    Philippians 4:13
    I can do all things in him that strengthen me.
    Apostle Paul inspired by GOD.

  5. #5
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,300
    Post Likes
    Quote Originally Posted by heatingman View Post
    If it was a leaking flare joint, thats a field made connection.

    Pending on terms of original labor warranty of the equipment, that possibly should be covered.

    You stated the coil would be under warranty. So logic follows that a general workmanship labor warranty may have similar term

    Sent from my SM-G930V using Tapatalk
    Standard labor warranty from installing contractor is 12 months.

    OP implies that company doing the work, may not be the same company that installed the equipment.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?