Thread: New NEC 2020 change

  1. #1
    Join Date
    May 2004
    Posts
    2,622
    Post Likes

    New NEC 2020 change

    I noticed part of the new 2020 NEC requires a surge protector to be installed if any service equipment is replaced. I’m assuming that’s just electrical service equipment? I can’t imagine having to install a whole home surge protector if just changing out the A/c unit.


    Sent from my iPhone using Tapatalk

  2. #2
    Join Date
    Jan 2015
    Location
    Bellevue, Washington, United States
    Posts
    2,388
    Post Likes
    I can tell you here in Washington a lot of electricians I know have very strong feelings about the 2020 NEC. Basically what happened was a bunch of Representatives who work for leviton and other product manufacturers got elected to the board for the NEC and mandated all this new electronic equipment which their own company manufacturers. This new electronic equipment has proven to be extremely unreliable and results in countless callbacks because frustrated customers are sick and tired of their breakers tripping for no reason. I've literally seen electricians install arc fault breakers to be 2020 compliant and after the electrical inspection pull them out and pull regular breakers back in. The only reason why I was because the arc faults were terribly unreliable and they didn't want to get callbacks. It's a very weird time we are in right now and I fear fewer and fewer contractors are even going to pull permits in response to what has happened. for the last 10 years I've been in business I always prided myself that I always pulled permits. But if a contractor can't achieve a reliable result and have it be completely up to code what are you going to do........

  3. Likes 270wsm, DeltaT, strogen, VTP99 liked this post.
  4. #3
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes
    That reminds me of a funny thing. I went to a bankruptcy auction and one of the items was a stack of residential evaporators. New, never opened, still in the box. But from all different companies. After I bought them I found that one of the guys there at the auction had worked for the company. He told me that when matched-systems became a requirement for rebates and so forth his boss would buy the matching evaporators, add the cost of the coil to the proposal, but then never install the new coil - just re-use the existing coil. It was explained to the customer and reduced the price so a lot of them accepted it. Some were later used for coil-only replacements he said but most just stacked up in the warehouse.

    Even funnier (and ironically so <g>) is that I think I Still have one or two of those coils from that auction. Yeah; one more good deal . . . . <g>

    OH! That reminds me! A friend of mine is looking for a coil! How cool would that be? I'll have to check and see if one of those NOS coils will work.

    PHM
    --------



    Quote Originally Posted by James Colver View Post
    I can tell you here in Washington a lot of electricians I know have very strong feelings about the 2020 NEC. Basically what happened was a bunch of Representatives who work for leviton and other product manufacturers got elected to the board for the NEC and mandated all this new electronic equipment which their own company manufacturers. This new electronic equipment has proven to be extremely unreliable and results in countless callbacks because frustrated customers are sick and tired of their breakers tripping for no reason. I've literally seen electricians install arc fault breakers to be 2020 compliant and after the electrical inspection pull them out and pull regular breakers back in. The only reason why I was because the arc faults were terribly unreliable and they didn't want to get callbacks. It's a very weird time we are in right now and I fear fewer and fewer contractors are even going to pull permits in response to what has happened. for the last 10 years I've been in business I always prided myself that I always pulled permits. But if a contractor can't achieve a reliable result and have it be completely up to code what are you going to do........
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  5. #4
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes
    Thanks!

    I do have a CAPA036 coil sitting since way back then!

    Oh wait: that's a Goodman number? Right? When was the 'they all leak' period of time for Goodman coils?
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  6. #5
    Join Date
    Dec 2020
    Posts
    9
    Post Likes
    That is bad if that’s the truth! I haven’t read the 2020 code yet. Bad enough we have to deal with the cost and expense of unreliable arc fault breakers.

  7. #6
    Join Date
    Aug 2001
    Location
    Pavilion, NY
    Posts
    4,437
    Post Likes
    Quote Originally Posted by parsky1 View Post
    That is bad if that’s the truth! I haven’t read the 2020 code yet. Bad enough we have to deal with the cost and expense of unreliable arc fault breakers.
    And just wait for the enforcement of outdoor disconnects for all residential homes. Midnight drunks walking down the block shutting off everyone's electric..

    Sent from my SM-N960U using Tapatalk
    ...

  8. #7
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,905
    Post Likes
    Quote Originally Posted by kangaroogod View Post
    And just wait for the enforcement of outdoor disconnects for all residential homes. Midnight drunks walking down the block shutting off everyone's electric..

    Sent from my SM-N960U using Tapatalk
    Not much a problem here in our rural area.
    I have always thought someone with a grudge could cause a lot of trouble for somebody by pulling the disconnect and walking away with it.
    *********
    https://www.hvac20.com/ High efficiency equipment alone does not provide home comfort and efficiency. HVAC2.0 is a process for finding the real needs of the house and the occupants. Offer the customer a menu of work to address their problems and give them a probability of success.

    Find contractors with specialized training in combustion analysis, residential system performance, air flow, and duct optimization https://www.myhomecomfort.org/

  9. #8
    Join Date
    May 2004
    Location
    Salt Lake City/Tooele
    Posts
    9,679
    Post Likes
    Quote Originally Posted by kdean1 View Post
    Not much a problem here in our rural area.
    I have always thought someone with a grudge could cause a lot of trouble for somebody by pulling the disconnect and walking away with it.
    About 7 or 8 years ago we had an apartment complex with about 40 units. I can only assume one of the renters p!ssed or something. But everyone of the removable stab connectors in all of those AC unit disconnects was pulled and gone. You can't just buy those, that was a busy day replacing all those disconnects.



    For ongoing training out here for our electricians, they have a UL guy fly in and teach for 2 days (two 8 hour courses) for their on-going education. In any case I may not be a licensed electrician but since I work along side them, I attend the classes. The most recent one was all about the NEC 2020 changes coming up.

    Obviously as an HVAC guy I perk up a bit when HVAC stuff comes into the conversation, usually just start to doze when the number of receptacles and spacing along a wall or kitchen island are being discussed.

    But the change in the NEC 2020 is to have GFCI protection for ALL electric appliances, including the outdoor HVAC equipment. We were told by the UL guy that this was driven by numerous electrocutions of children. Apparently one was between the washer and the wall getting a sock or something that fell behind and was smoked, a PTAC unit wiped another kid out somewhere, and another kid was climbing on the outdoor AC unit and touched the chain link fence and he/she was smoked. And many other similar situations where it may not have ended with death, but reported.

    It is only code if your jurisdiction adopts the code. I think we are still using NEC 2015 here where I am at and no future talk about changing any time soon.

  10. Likes kdean1, R600a liked this post.
  11. #9
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    14,090
    Post Likes
    I believe the term "service equipment" refers to the mains from the utility.
    The outdoor disconnect I believe is a choice of either /or. Next to the entrance
    within a certain distance or outside. Shutting off power can be a problem for fire
    responders if the service main is no where in sight. CA, I don't know about.

    Codes are like middle managers, they just keep adding more.
    We are here on Earth to fart around ......Kurt Vonnegut

    You can be anything you want......As long as you don't suck at it.

    USAF 98 Bomb Wing 1960-66 SMW Lu49

  12. #10
    Join Date
    May 2020
    Location
    NJ
    Posts
    13
    Post Likes
    Quote Originally Posted by kdean1 View Post
    Not much a problem here in our rural area.
    I have always thought someone with a grudge could cause a lot of trouble for somebody by pulling the disconnect and walking away with it.
    I think you're picturing an HVAC style pull-out disco lol.

    A 100 or 200A service rated disconnect won't have anything for the assailant to walk away with, the disco is made up of a lever or breaker.

  13. #11
    Join Date
    May 2020
    Location
    NJ
    Posts
    13
    Post Likes
    Quote Originally Posted by kangaroogod View Post
    And just wait for the enforcement of outdoor disconnects for all residential homes. Midnight drunks walking down the block shutting off everyone's electric..

    Sent from my SM-N960U using Tapatalk
    I don't like the code requirement at all, but I have to say that this isn't going to be an issue. There are already areas around the country that have their own code requiring disconnects to be outside. There are also many areas where the entire main panel is located outside, such as California, Oregon, Arizona, etc.

    Further, even in areas like mine in which outside disconnects are not required, they are widely used on apartments and condo buildings, and even sometimes houses.

    But we never hear of issues with this, so I don't think it will be a thing. It will just be a much larger bill that the homeowner will have to pay for a service upgrade.

  14. #12
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,456
    Post Likes
    I've seen those pull out disconnects up to 100 amps, maybe even greater.


    Quote Originally Posted by Bythenumbers View Post
    I think you're picturing an HVAC style pull-out disco lol.

    A 100 or 200A service rated disconnect won't have anything for the assailant to walk away with, the disco is made up of a lever or breaker.
    I do a triple evac with nitro to remove non condensables.

  15. #13
    Join Date
    May 2020
    Location
    NJ
    Posts
    13
    Post Likes
    Quote Originally Posted by BBeerme View Post
    I've seen those pull out disconnects up to 100 amps, maybe even greater.
    SUSE (Suitable for Use as Service Equipment)?

    I'm really doubting it.

  16. #14
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,456
    Post Likes
    Quote Originally Posted by Bythenumbers View Post
    SUSE (Suitable for Use as Service Equipment)?

    I'm really doubting it.
    They were in an electrical Room and fed breaker panels inside the building. The one that is burned into my memory fed a Server Room. Probably dozens of outlets. At least 100 amps.

    Their air conditioning went down and all of the little fans on the individual servers ramped up to full speed. I had no idea they were variable speed until then. But they had so many servers with so many of those little fans the amps got so high that it finally blew a fuse in the main panel. And in that process it also welded in the pull out disconnect.

    I could not pull it out with all my might. Getting very late in the day, probably a Friday, so I told the guy in charge to call a commercial electrician as soon as possible and to make sure to tell them it was an emergency and they would likely have to pay to have an electrical wholesaler to open up to get parts.

    I'm sure it was all code when initially installed and if the electrical code changed, then they would have been grandfathered in.
    I do a triple evac with nitro to remove non condensables.

  17. #15
    Join Date
    May 2020
    Location
    NJ
    Posts
    13
    Post Likes
    I will edit my original statement:

    A 100 or 200A service rated disconnect installed on a new service or upgrade today, according to the 2020 code change that we are speaking about, won't have anything for the assailant to walk away with, the disco is made up of a lever or breaker.

  18. #16
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,456
    Post Likes
    So, nothing wrong with having a pull out disconnect on a 100 or 200 amp panel serving other panels?

    For what it is worth, and just so it is said, I hate those pull out disconnects. I don't care what the amperage.



    Quote Originally Posted by Bythenumbers View Post
    I will edit my original statement:

    A 100 or 200A service rated disconnect installed on a new service or upgrade today, according to the 2020 code change that we are speaking about, won't have anything for the assailant to walk away with, the disco is made up of a lever or breaker.
    I do a triple evac with nitro to remove non condensables.

  19. #17
    Join Date
    May 2020
    Location
    NJ
    Posts
    13
    Post Likes
    Quote Originally Posted by BBeerme View Post
    So, nothing wrong with having a pull out disconnect on a 100 or 200 amp panel serving other panels?
    Not that I know of, but I am not sure which exact model you are speaking about. I have never seen a pull out disco for this purpose. Most are for line-to-line loads only (such as 240V AC) and don't have any provisions for neutrals.

    For what it is worth, and just so it is said, I hate those pull out disconnects. I don't care what the amperage.
    My understanding is that pull out discos available today are just meant to be really cheap. I bought a couple dozen on sale for $6 at Home Depot a few years back to use for resi condensing units.

    In that instance they really serve no purpose, they are just for the lazy HVAC guys who don't want to have to walk into the house and shutoff the breaker. The same way as we have to install an outlet in close proximity to HVAC equipment for their convenience. yet we don't have to install an outlet near the electrical panel, nor a light. You would think electrical code would help electrician more than HVAC guys!

    Yes, I am joking (mostly )

  20. #18
    Join Date
    Sep 2012
    Location
    thomaston, ct
    Posts
    505
    Post Likes

    New NEC 2020 change



    200amp pull out disconnect, no thanks!

    Sent from my iPhone using Tapatalk

  21. #19
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes
    I would be very leery of a pull-out type disconnect at anything over maybe 30-40 amps. Picture the arc-flash of pulling one out slowly with a 100-200 amp load? <g>

    Disconnects of any size generally have an over-center action and strong springs to actually snatch the contacts open quickly. Pull-outs would always be subject to the slowness of the person operating them. And they could stick part way out - that might get exciting. <g>

    PHM
    --------



    Quote Originally Posted by BBeerme View Post
    So, nothing wrong with having a pull out disconnect on a 100 or 200 amp panel serving other panels?

    For what it is worth, and just so it is said, I hate those pull out disconnects. I don't care what the amperage.
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  22. Likes jlanesey liked this post.
  23. #20
    Join Date
    Aug 2001
    Location
    Pavilion, NY
    Posts
    4,437
    Post Likes
    I for 1 am not a big fan of pulling out

    Sent from my SM-N960U using Tapatalk
    ...

  24. Likes jlanesey, shellkamp liked this post.
+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •