    rheem furnace short cycle

    Hello techs , I had a home owner call saying a company installed his furnace & had to redue the flue pipes after it failed inspection from the bldg department, know his furnace short cycles after the new flue pipes installed ,i want to share few pictures & get some opinion on what could be wrong with the piping. Am not sure if i want to get involved with someone's problem,but figured to share the job.plz update

    rheem M# R92PA0601317MSA


    Sent from my SM-G950U using Tapatalk

  2. #2
    Join Date
    Mar 2018
    Location
    Virginia
    Posts
    2,214
    Post Likes
    What exactly do you mean by short cycle. Is the furnace inducer running and then shutting down before ignition takes place?

    Sent from my SM-G960U using Tapatalk
    "I think Quantum tunneling would work great... "

    "Call a technician for God's sake. Or we'll see you on the news or the Dark Side of the Moon."

  3. #3
    Join Date
    Aug 2014
    Posts
    291
    Post Likes
    Thread Starter
    not sure, I havent seen the job yet ,trying not to get involved with job, but the main reason I posted is to share pictures on how the flue pipe install looks.

    Sent from my SM-G950U using Tapatalk

  4. #4
    Join Date
    Mar 2018
    Location
    Virginia
    Posts
    2,214
    Post Likes
    I mean it looks absolutely horrible in every way. I don't know if there's much more to say than that if you don't want to get the details or get involved...and honestly I don't blame you for passing it up.

    Sent from my SM-G960U using Tapatalk
    "I think Quantum tunneling would work great... "

    "Call a technician for God's sake. Or we'll see you on the news or the Dark Side of the Moon."

  5. #5
    Join Date
    Aug 2014
    Posts
    291
    Post Likes
    Thread Starter
    i appreciate your comment , even though am not getting involved in the job , I still would like to learn from the job pictures, to me it looks like the termination pipe on the outside wall I believe is the intake pipe. is ran 2ft vertical then needed & the flue piping by the furnace not only looks ugly but the intake pipe is pitched way to much, if possible i would like to hear some details from your end ?

    Sent from my SM-G950U using Tapatalk

  6. #6
    Join Date
    Jan 2020
    Location
    Winnipeg Canada
    Posts
    1,155
    Post Likes
    It's hard for me to make a judgment from these pictures....
    But it looks like one run has a bit of a reverse pitch to it.
    And I also see both intake and exaust have downspouts on them.
    If in fact one of the pipes has a reverse slope in one area then that will effectively make a trap and you'll be dealing with a blockage and short cycling or not running at all.
    It's also not a good idea to have a downspout on the exaust of the furnace as it will be recycling the exaust and starving for oxygen among other problems.....
    However this is only based on what I can see. And I'm making the assumption that these two downspouts are from the same unit.
    You don't squat with your spurs on.
    And you NEVER put the torches away before pressure testing.

  7. #7
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    4,968
    Post Likes
    Quote Originally Posted by Restaurant mech View Post
    It's hard for me to make a judgment from these pictures....
    But it looks like one run has a bit of a reverse pitch to it.
    And I also see both intake and exaust have downspouts on them.
    If in fact one of the pipes has a reverse slope in one area then that will effectively make a trap and you'll be dealing with a blockage and short cycling or not running at all.
    It's also not a good idea to have a downspout on the exaust of the furnace as it will be recycling the exaust and starving for oxygen among other problems.....
    However this is only based on what I can see. And I'm making the assumption that these two downspouts are from the same unit.
    X2. Hard to make out the intake or exhaust from those pictures but if the exhaust is on top it will have real problems real quick. Rheem should have pictures in their installation manual as to what is acceptable. Guarantee what is pictured is not in there.

    Sent from my SM-G965W using Tapatalk

  8. #8
    Join Date
    Oct 2019
    Location
    MN
    Posts
    24
    Post Likes
    Hard to say without seeing full venting application, and info on length of run/ size and specs of furnace it is served... all limitations and sizes are different to each specific piece of equipment.

  9. #9
    Join Date
    Mar 2018
    Location
    Kansas Flatlands
    Posts
    746
    Post Likes
    No mfg recommends close sweep 90's for an install. The outfit that put this in obviously used the install manual for a pad to lay down to put their knees on. Is that electrical pvc conduit used for flue material. Ya I bet this is having pressure switch issues. By the way who decided the best place to take this out was directly at some kind of fence?

  10. #10
    Join Date
    Aug 2014
    Posts
    291
    Post Likes
    Thread Starter
    I would say the company that originally installed it.

    Sent from my SM-G950U using Tapatalk

  11. #11
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    32,796
    Post Likes
    Quote Originally Posted by theoldscroll View Post
    No mfg recommends close sweep 90's for an install. The outfit that put this in obviously used the install manual for a pad to lay down to put their knees on. Is that electrical pvc conduit used for flue material. Ya I bet this is having pressure switch issues. By the way who decided the best place to take this out was directly at some kind of fence?
    I see stickers on every fitting. cant read the warning but can see the arrows. Never have I seen that on Sch 80 conduit. That has to be some new exhaust piping!

  12. #12
    Join Date
    Aug 2014
    Posts
    291
    Post Likes
    Thread Starter
    yes there from the same unit ,anyways I never heard back from the owner, thanks again

    Sent from my SM-G950U using Tapatalk

  13. #13
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    13,204
    Post Likes
    Quote Originally Posted by nytech28 View Post
    Hello techs , I had a home owner call saying a company installed his furnace & had to redue the flue pipes after it failed inspection from the bldg department, know his furnace short cycles after the new flue pipes installed ,i want to share few pictures & get some opinion on what could be wrong with the piping. Am not sure if i want to get involved with someone's problem,but figured to share the job.plz update

    rheem M# R92PA0601317MSA

    If you put an email address in your profile, or email me (address is in my profile), I can get the installation manual off to you for review.

    From the middle picture you posted, the left PVC pipe (the vertical one) should be the exhaust pipe, and the horizontal pipe in that same picture, should be the combustion air pipe.
    Instead of learning the tricks of the trade, learn the trade.

  14. #14
    Join Date
    Aug 2014
    Posts
    291
    Post Likes
    Thread Starter
    I have the installation manual , I was able to find & download ,the illustration for the flow pipe is not near to what's installed on the job, I didnt get involved with job ,but sure did learn how to deal with similar situations in future, am happy to share more future missup jobs ,thanks for taking the time to look into this.

    Sent from my SM-G950U using Tapatalk

  15. #15
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    14,236
    Post Likes
    Seeing that fence my first thought was duplex. From what I have seen you can use short 90's but they add about double the equivalent footage of a long sweep. If that is PVC conduit is it even rated for use as a flue? I know you have to watch as there are 2 different types of the white PVC the one I believe they refer to as cellcore is not rated for venting as it will sag as it gets warm.

  16. #16
    Join Date
    Apr 2006
    Location
    Tyler, Tx
    Posts
    1,371
    Post Likes
    https://www.centrotherm.us.com/InnoF...t-Lengths.aspx

    Looks the product is for Flue Venting....first time I have seen it...
    Philippians 4:13
    I can do all things in him that strengthen me.
    Apostle Paul inspired by GOD.

  17. #17
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    11,888
    Post Likes
    Quote Originally Posted by nytech28 View Post
    Hello techs , I had a home owner call saying a company installed his furnace & had to redue the flue pipes after it failed inspection from the bldg department, know his furnace short cycles after the new flue pipes installed ,i want to share few pictures & get some opinion on what could be wrong with the piping. Am not sure if i want to get involved with someone's problem,but figured to share the job.plz update

    rheem M# R92PA0601317MSA


    Sent from my SM-G950U using Tapatalk
    This is what the code enforcement passed?

    Shame on them.

    The flue gas clearly will recirculate.

    Both point downwards, and terminate next to a fence.


    Sent from my iPhone using Tapatalk

  18. #18
    Join Date
    Aug 2014
    Posts
    291
    Post Likes
    Thread Starter
    The inspection failed the 1st time & I believe the flue piping was repiped according to home owner, I didnt get involved with job, I only shared the job pictures.

    Sent from my SM-G950U using Tapatalk