Thread: Rheem HP bouncing off HP limit

  1. #1
    Join Date
    Nov 2016
    Location
    Huntsville, Alabama
    Posts
    952
    Post Likes

    Rheem HP bouncing off HP limit

    This old Rheem RQPL package unit (R410A) works great in cooling but has unsteady high pressure in heat mode. The discharge pressure sort of levels off in high 300s/low 400s then over a few minute time span it will creep up to a brief touch of 700 PSI and then drop back down to low 400s. Then, it will creep up creep up and then relief again. It doesn't drop off suddenly but drops down slowly at the same rate as it was climbing before.

    I reckon it is crap in the system and that changing the outdoor TXV + drier will solve the problem... but this is the first time I have seen a txv act this way, maybe it is not contamination but another type of txv failure?. The motor (bulb) is properly attached and insulated.

  2. #2
    R600a's Avatar
    R600a is offline Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    31,872
    Post Likes
    I would be inclined to check the blower capacitor and amp draw just to be sure the blower is not on the verge of quitting and maybe not moving enough air.

    Sent from the Okie state usin Tapatalk
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

  3. #3
    Join Date
    Aug 2008
    Location
    Hibbing, MN
    Posts
    1,301
    Post Likes
    Start with the basics. Is the indoor coil clean? How is the airflow over the indoor coil? Filters?
    If God didn't want us to eat animals... He wouldn't have made them out of MEAT.

  4. Likes R600a, Bazooka Joe liked this post.
  5. #4
    Join Date
    Dec 2006
    Location
    Vancouver, B.C.
    Posts
    1,731
    Post Likes
    What is your superheat and subcooling showing as?

    Temp split across the evaporator?
    Quickly, I must hurry, for there go my people and I am their leader!

  6. Likes R600a liked this post.
  7. #5
    Join Date
    Nov 2016
    Location
    Huntsville, Alabama
    Posts
    952
    Post Likes
    Thread Starter
    In heating mode it never got stable enough to get a reading. Thats what I was zeroing in on. Up/down up/down I'll be going back today to verify evap condx and evaluate whether the unit is worth investing in.

  8. #6
    Join Date
    Apr 2006
    Location
    Tyler, Tx
    Posts
    1,793
    Post Likes
    Quote Originally Posted by Tom Thermo View Post
    In heating mode it never got stable enough to get a reading. Thats what I was zeroing in on. Up/down up/down I'll be going back today to verify evap condx and evaluate whether the unit is worth investing in.
    What are the temps on all four pipes of the reversing valve?
    Philippians 4:13
    I can do all things in him that strengthen me.
    Apostle Paul inspired by GOD.

  9. Likes Tom Thermo liked this post.
  10. #7
    Join Date
    Nov 2016
    Location
    Huntsville, Alabama
    Posts
    952
    Post Likes
    Thread Starter
    I didn't measure the temps but there was no apparent mixing i.e. hot and cold, no warm. Switched hot and cold no problem. Heat worked, ac worked, but heat pressure unsteady. I'll look more at that if I can during the transient. So you're saying maybe the reversing valve is wandering and restricting the compressor discharge flow.

  11. #8
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Sounds more like a slight over charge, and non condensables in it.

  12. #9
    Join Date
    Mar 2018
    Location
    Kansas Flatlands
    Posts
    833
    Post Likes
    Quote Originally Posted by beenthere View Post
    Sounds more like a slight over charge, and non condensables in it.
    BINGO

  13. #10
    Join Date
    Nov 2016
    Location
    Huntsville, Alabama
    Posts
    952
    Post Likes
    Thread Starter
    OK I'll go get the numbers in cooling mode. We're going to get to the bottom of this yet! haha It has been running without issue for years but maybe the 700 psig overspikes finally woke up the problem.

    It could be the exuberator valve.

  14. #11
    Join Date
    Nov 2016
    Location
    Huntsville, Alabama
    Posts
    952
    Post Likes
    Thread Starter
    I just checked my records and I have never put gages on this unit since I have been maintaining it since 2017. Time for JobLink and my exuberator adjuster.

  15. #12
    Join Date
    Dec 2006
    Location
    Vancouver, B.C.
    Posts
    1,731
    Post Likes
    410a HP limit is typically set at 600. Why is this system running up until 700? What is the switch set for?
    Quickly, I must hurry, for there go my people and I am their leader!

  16. #13
    Join Date
    Nov 2016
    Location
    Huntsville, Alabama
    Posts
    952
    Post Likes
    Thread Starter
    OK there is no switch. Smooth sailing in cooling mode but as soon as that reversing valve switches over the discharge pressure goes to 700. Maybe an internal pressure relief opens?
    gotta go

  17. #14
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    You are giving it five minutes off time before switching between heat and cool correct

  18. #15
    Join Date
    Nov 2016
    Location
    Huntsville, Alabama
    Posts
    952
    Post Likes
    Thread Starter
    Negative pec. Thanks. it minor spike at switchover, then rises to peak 700 then drops back down to 420 then slow rise back to 700 and slow back down. One minute cycle. I am confident this thing has not been doing the same thing for 3 years. Interesting I can see the same 1 minutes cycle on much
    smaller scale in cooling mode

  19. #16
    Join Date
    Nov 2016
    Location
    Huntsville, Alabama
    Posts
    952
    Post Likes
    Thread Starter
    It must be kicking out on thermal overload. I haven't seen that yet, imm too scared to let it go that long. The call was for no heat. But ac, 8 SH ... 34 Deg sc

  20. #17
    Join Date
    Nov 2016
    Location
    Huntsville, Alabama
    Posts
    952
    Post Likes
    Thread Starter
    Test forum update new fone

  21. #18
    R600a's Avatar
    R600a is offline Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    31,872
    Post Likes
    Quote Originally Posted by Tom Thermo View Post
    Test forum update new fone
    Coming in loud and clear.

    Sent from the Okie state usin Tapatalk
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

  22. #19
    Join Date
    Apr 2004
    Location
    Minnesnowta
    Posts
    2,364
    Post Likes
    I vote for a dirty indoor coil
    Wisdom has been chasing you, but you have always been faster.

    In your darkest hour, when the demons come, call on me brother and we shall fight them together.

    A Veteran is a person, who at some point in their life, wrote a blank check payable to the United States of America for payment up to and including their life.
    Gene Castagnetti-Director of the National Memorial Cemetery of the Pacific in Hawaii

  23. #20
    Join Date
    Apr 2020
    Location
    Garner NC
    Posts
    10,833
    Post Likes
    Quote Originally Posted by Tom Thermo View Post
    It must be kicking out on thermal overload. I haven't seen that yet, imm too scared to let it go that long. The call was for no heat. But ac, 8 SH ... 34 Deg sc
    It looks Overcharged For sure (High SC standing out) with an odd restriction possibly at the filter dryer. It would be kicking out on high head, thermal OL would be if the CFM stopped..

    Remove the sensing bulb first, if it clears up your on the Right track...Try recovery of some of the refrigerant from the high side before the filter dryer.Ive seen lots of partial restrictions confuse other techs to adding refrigerant when the looked at the low side...

    Is the condenser clean and CFM not running backwards?
    Last edited by Unlimited1; 10-20-2020 at 09:48 PM.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •