    Charged an old R22 unit today with MO-99. Ended up with pretty much the same pressures as R22! Was interesting to see as I've never used it before. Outdoor ambient of 80...49 degree suction line. 75psi on the low side...225 on the high. Seemed to be performing well.
    Jul 2011
    DFW, TX.
    Supply air temp, superheat and subcooling?
    Sent from my LM-G820 using Tapatalk
    Quote Originally Posted by CEAS-AC-TECH View Post
    Supply air temp - cold...i didn't measure directly. I usually do. I just checked with my hand quick.
    Superheat/subcool - didn't have a mo99 pt chart handy. It had a txv. Now that I look..two different pt charts give me two different temperatures? According to one, my txv was working accordingly....and according to the other...my txv is stuck open?? Weird. Forgot to check subcool. Its got a leak. I was there converting and charging dye. Gotta go back.
    Probably 25 yr old system.
    Jul 2019
    Oklahoma home its in the name
    My boss tried mo99 back when r22 was really high and he had so many problems that he switched them all back at his own expense and won't touch r22 replacements ever again.
    Sent from the Okie state usin Tapatalk
  5. Likes CEAS-AC-TECH, theoldscroll liked this post.
  6. #5
    Quote Originally Posted by R600a View Post
    What kind of problems was he having? This was the first time i've used it, and it seemed to be working pretty good. R22 is on the way out...at least here in Canada. So I opted for the more affordable MO99. One thing I was thinking about is the gas charge in the R22 txv bulb when using MO99...if it would work ok. The things I read it's supposed to work with no component changes.
  7. #6
    Oct 2009
    Atlanta,Ga.
    i have been using MO99(R438A) for over 5 years.I have not had any problems with it.
  8. #7
    Jan 2020
    Winnipeg Canada
    I've used mo99 quite a bit. Never had any issues what so ever.
    Only thing to take note is that suction pressure will be a few psi lower than r22.
    So if you were reading 49 deg suction then would actually be 53-55 deg.
    You don't squat with your spurs on.
    And you NEVER put the torches away before pressure testing.
  9. #8
    Jul 2019
    Quote Originally Posted by desol View Post
    I think it was mainly capacity problems but I don't really know. He hates it with a passion.
  10. #9
    lol. My old boss didn't like it either...he said it wasn't quite the same. He did Ice plants...that were full of R22. I never used it there but we had a jug hanging around. I just do res and light commercial. No big stuff. That could be where the difference is.
    Engineering says it should work.
  11. #10
    Jul 2019
    I just realized I was mixed up. He had problems with r422b.
  12. #11
    Ha! Turns out it was my boss not yours! Anyway...had a nice cold suction line when I left the job today.
  13. #12
    If the vapor line temp was at 49° and you had a saturation pressure of 75PSIG. You had zero SH.
  14. Likes CEAS-AC-TECH liked this post.
  15. #13
    Mar 2015
    Tx
    I used a lot of 422 and no problems. You were not trying to mix it with r22 ?
  16. #14
    Jul 2019
    Quote Originally Posted by oldguy1949 View Post
    I am shure he recovered the r22.
  17. #15
    Mar 2018
    Kansas Flatlands
    Nothing will be as good as the real stuff. period. The real difference is when it's 106 outside.
  18. Likes CEAS-AC-TECH liked this post.
  19. #16
    Jul 2019
    Quote Originally Posted by theoldscroll View Post
    And the condenser is dirty and the fan blade is not set to the proper depth.
  20. #17
    Jul 2013
    Richmond, VA
    Yup. Unless I’m replacing a compressor, R22 goes in. I’ve used MO99 with some inconsistent results. RS44B works well, but the issue is I’m not carrying 5 different flavors of retrofits on my truck so on the off chance I can recharge an 18 year old system. This late in the game, aside from commercial systems, R22 systems are at the age of replacement if a major refrigeration repair is needed.
  21. Likes pacnw liked this post.
  22. #18
    Jul 2019
    Quote Originally Posted by CircusEnvy View Post
    I have been trying to convince him to let me try and repair a leak on a 15 ton package unit we take care of and convert it to 407c or whichever one it is that everyone says is the best.
  23. #19
    That's what I thought. It was fluctuating between 49 and 52. The system has a new txv...there should be superheat.
    I used the dew point column on the pt chart for checking the saturated suction temperature on mo99...and 75PSIG was 49 degrees.
  24. #20
    Float'N Vally, MS
    We used "NU22" (422B) in the beginning of this mess and was told to be the next best thing....
    No problems EXCEPT capacity loss. Most systems are over sized, but...
    Hit a couple that were sized "correctly" and got in a bind. Dropped it like a hot bolt!
    Went to 407c on "replacements" and never turned back.
    Life is too short, Behappy!