Trane voyager YCH600

2.3K views 3 replies 3 participants last post by  mrcool  
#1 ·
trane unit seem to be in default mode, i lowered the DA setpoint, lowered space temp and only first stage runs, no flashing at rtrm, tried to put a conventional tstat on rtrm but it wound not work is there something i need to jump or set to get the conventional tstat to work, this is a SZVAV but there are no vav on this system, i dont know why they did this. thanks in advance
 
#2 ·
Have you tried running in test mode to see if the other compressor runs? Is the unit set up for 3 stage cooling? Did you check for coil voltage on the compressor contactor?
 
#4 ·
Lddc, first time i went there DA was set at 65, lowered it to 50 and second stage (comp 2+3) ran for ten min , then back to first stage , did the test it runs fine , checked pin from board and contactor no 24v, CHEYENNE2020 , baysens zsm with remote sensor, seem to be in default mode cause my zone temp wont drop below 74, i was reading the manual and it said that if the cool indicator was blinking that it is in default, now wound the cool indicator be the snowflake, because that was blinking, --- i set the baysen zone temp to 62 and yesterday they said it was fine, stopping there today to see what temp the zone is
 