    I have to install new carrier 2 ton condenser unit on a system with an existing aruf25b14 Goodman air handler that was installed a year ago on an old r22 condenser.
    I haven't done one of these conversions before and don't know the oil compatibility issues, but I am sure there is some. I don't want any goo clogging a new unit. I am installing a new line set so the only thing I have to flush is the evaporator. Is there an actual procedure I can find for this somewhere. Or do I have to wing it.
    Or, is there someone who has some experience with this kind of flush out there? I usually do an acetone or a r11 flush, or both on evaps and have had good success with them. I just don't know if I will have an issue getting all traces out of the evaporator. I haven't had the opportunity on the Goodman unit. I usually install the whole system.
    Any recommendations.
    I usually work on commercial HVAC, and auto air, but worked for Trane as a controls specialist before I retired. Now flipping homes.
    Any responses would be appreciated.
    Oct 2009
    Atlanta,Ga.
    I would use nitrogen to push out the old oil.I don't think you need to flush ,unless it was a burnout.It won't hurt to have a small amount of Mineral oil left.I have done this same type of job.Never flushed with a chemical.Never had a problem .Only used Nitrogen to push out the old oil .If switching from from R22 to R410A, check with Goodman .You need a different Accutator or TEV ,for R-410A.Make sure the Evaporators coil is approved for R410A.Its only a year old,So probably is ok, Double check.
    Mar 2009
    flush
    Quote Originally Posted by Gleng View Post
    I would use nitrogen to push out the old oil.I don't think you need to flush ,unless it was a burnout.It won't hurt to have a small amount of Mineral oil left.I have done this same type of job.Never flushed with a chemical.Never had a problem .Only used Nitrogen to push out the old oil .If switching from from R22 to R410A, check with Goodman .You need a different Accutator or TEV ,for R-410A.Make sure the Evaporators coil is approved for R410A.Its only a year old, So probably is ok, Double check.
    Yes I have the 410a TXV that came with the air handler. I made sure I had it.
    There was not a burn. The compressor just has bad valving, so it has to high of pressure on the low side and to low a pressure on the high side. The unit is cooling, but it runs constantly causing high electric usage. So you can have a bit of mineral oil in with the 410a oil and it will not gel? Like ester oil and mineral oil on a car ac retro fit?
    Thanks for the info that makes things easier.
    Jan 2014
    New England
    Make sure to register the OD unit, if you went with a matched Goodman OD unit, chances the manufacturer warranty will be 10/10. Guessing with the Carrier it will be 5/5. Probably to late as guessing you have the unit already.
    Southold, NY
    There is NO oil compatibility issues. Just blow the existing equipment with N2. Done
    Apr 2020
    va
    Blow it out with nitrogen. The old standard was <5% mineral oil ok with HFC refrigerant. If concerned or have a problem, test with a refractometer and change oil after operating if excess mineral.
    Should not be a problem on a ahu tube/fin. Only times I've seem where a major problem has been with plate heat exchangers where they would have to be removed and flushed or replaced if charged with mineral oil & R-410a or R-134a