    Question %OA Increase & Increased Air Filtration Energy Consumption

    Due to COVID-19, there is an large demand for increased fresh air and increased air filtration, particularly in shared spaced. I'm trying to figure out the below questions, but am not sure how to go about calculating energy increase for these situations...

    In a 300,000 sq ft* building that has approximately 300,000 CFM of AHUs that were previously getting 20% outdoor air and are now getting 100% outside air, what would the energy increase (in kwh) be to condition 300,000 CFM of outside air instead of 240,000 CFM of return air and 60,000 CFM of outside air? Assume EER of 12 for both situations. Unit operates 2080 hrs per year. Neglect capacity of chiller plants/boiler plants/etc.

    Separately, what if MERV-14 filters were used instead of MERV-8 filters? What would the energy increase (in kwh) be for 300,000 CFM of fans for 2080 hrs per year? Assume ballpark average for pressure drops.

    Thank you in advance.

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Quote Originally Posted by ixratskrad View Post
    Due to COVID-19, there is an large demand for increased fresh air and increased air filtration, particularly in shared spaced. I'm trying to figure out the below questions, but am not sure how to go about calculating energy increase for these situations...

    In a 300,000 sq ft* building that has approximately 300,000 CFM of AHUs that were previously getting 20% outdoor air and are now getting 100% outside air, what would the energy increase (in kwh) be to condition 300,000 CFM of outside air instead of 240,000 CFM of return air and 60,000 CFM of outside air? Assume EER of 12 for both situations. Unit operates 2080 hrs per year. Neglect capacity of chiller plants/boiler plants/etc.

    Separately, what if MERV-14 filters were used instead of MERV-8 filters? What would the energy increase (in kwh) be for 300,000 CFM of fans for 2080 hrs per year? Assume ballpark average for pressure drops.

    Thank you in advance.
    You cant go from 20% to 100% without MAJOR increases in BTU transfer!

    Energy increase roughly 500% increase!

  3. Likes stanbyyourword liked this post.
  4. #3
    Join Date
    Mar 2005
    Posts
    1,762
    Post Likes
    how bigs a piece of string? so many variables starting with Climate location
    Keep it simple to keep it cool!

  5. #4
    Join Date
    Nov 2001
    Posts
    195
    Post Likes
    The question can't be answered without knowing your weather conditions. Where I live, you can run 100% OA all year long with no energy penalty. In Miami, the penalty is massive.

    By the way, ASHRAE's emerging advise is to not go to 100% air but upgrade to a high-MERV filter. See this YouTube video preso from ASHRAE. The discussion about using recirc with a good filter vs. 100% OA is early in the presentation. The filtration discussion starts at 22:30.

    https://www.youtube.com/watch?v=GNl4...ature=youtu.be

  6. Likes stanbyyourword liked this post.
  7. #5
    Join Date
    Jun 2020
    Location
    Florida
    Posts
    72
    Post Likes
    I agree that there are too many unknowns to help answer your question. Without knowing your design conditions, it is unclear if it is advisable to load your equipment with 100% outdoor air.

    With those disclaimers, using $0.13/kWh, I came up with $1,123,166.97 (lol - definitely don't go to the bank with this number!! So many unknowns that it could be off by several decimal points!!)

    I basically used dimensional analysis and these calculators to solve for the change in total load (sensible + latent):


    It was a fun academic exercise - interested to see what you come up with.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •