Results 1 to 12 of 12
Thread: York YS question
    Apr 2019
    Western IN.
    York YS question
    I have a York YS and oil is logging in evap, unit tripping on oil sep low level.
    Customer recently replaced the slide valve positioning potentiometer themselves.
    Oil level in seperator is mid sg on bottom glass, foams at times on top of oil.
    Current operating conditions are:
    92%fla. Disch temp 139 Dif oil press 111. Did filter press 2.8 Oil temp 128.
    Cond wtr 91 lvg 86 ret. Cond Approach 3.2
    Chw lv 42. Ret 55 ( Chw ret temp sensor bad reads 99). Evap Approach 2.9
    Disch S ht 45 slide valve 82%
    Unit has microboard 031 01730 000 with031 02005 001 eprom. Not the upgrade kit.
    Last recorded service was 06/2018. Any ideas ?
    Jan 2015
    Somewhere making cold water
    Calibrate slide potentiometer 1st
    Apr 2019
    Western IN.
    Thank you!
    Aug 2019
    LA
    Does it trip on start up or after running a wile. Is there any oil on dry side?
    Apr 2019
    Western IN.
    It trips during run conditions, a little oil on fry side, maybe a 16th or 8th glass
    Apr 2019
    Western IN.
    Dry side
    Aug 2019
    LA
    There has been issues with oil coolers. Also does the unit unload fully during operation? Glide ring on shaft is another place oil escapes to evap
    BC,Canada
    Eductors working?Had sight glasses in ours to watch.
    Running long time at low load usually was our culprit though.
    Dec 2014
    New Mexico
    I remember a green letter from long ago about some oil separators you just could not run below 30% FLA . I think they were on S2 compressor bodies.
    I have a hard time believing that you are oil logged at 45F discharge superheat. Some oil, sure but not severely. Any oil in your secondary oil separator aight glass would indicate a dirty filter in the secondary oil separator drain line. That’s probably where your missing oil is.
  11. Likes IndustrialTech, stanbyyourword liked this post.
  12. #11
    Nov 2011
    CO
    Is the eductor actually working?
    You can pinch the liquid line valve back a bit at full load to get the oil back quicker.
  13. #12
    Apr 2017
    Raleigh, North Carolina
    Have had similar Issues.
    Eductor Block Jet Pump Pistons get stuck if the oil isn't maintained correctly.
    They run around $1200 new make sure you look at your compressor number because there is more then one style block.
    See the Brass Piston in the image below the lower Piston is stuck and even with a press we couldn't remove it. This is the S0 Block
    Sent from my SM-G988U using Tapatalk
  14. Likes stanbyyourword liked this post.