Results 1 to 12 of 12
Thread: Subcooling Question
    Apr 2020
    Subcooling Question
    Could anyone answer this question please as I am a bit stumped?
    How can I check the correct saturation temperature for subcooling if my high side gauge is on the liquid line service port just after the expansion device? That won’t give me the correct pressure reading will it?? The unit is an LG UM42. R410a.
    Many thanks
    Southold, NY
    liquid line AFTER the valve
  3. Likes Fender60 liked this post.
  4. #3
    Dec 2006
    Vancouver, B.C.
    Subcooling Question
    Without looking up the unit I’m going to assume this unit has a condenser mounted TXV with a “low pressure liquid line” that runs between the TXV and the evaporator coil.
    Do you have a service tap on the hot gas line? It may not be a perfect solution but should get you close enough.
    Why do you need to know the subcooling for that unit?
    Does it have a receiver in it?
    How does the manual suggest charging the unit?
    Edit: added missing quotation marks
    Quickly, I must hurry, for there go my people and I am their leader!
  5. #4
    Oct 2011
    Chicagoland Area
    There is so much wrong with your post. Doesn't make any sense.
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING
  6. #5
    Dec 2006
    Vancouver, B.C.
    Why don’t you tell us how you came across this job and what experience you have. It’s hard to help you if we don’t know your capabilities.
  7. #6
    Atlanta GA area
    Generally... mini's are charged by weighing in the charge... from a vacuum...
    What does the install manual say???
    GA-HVAC-Tech
    GA's basic rules of home heating and AC upgrades:
    *Installation is more important than the brand of equipment
    *The duct system keeps the house comfortable; the equipment only heats and cools (and dehumidifies)
    *The value of comfort, over the long term; leave economic choices behind!
    Choose your contractor wisely!
  8. #7
    Southold, NY
    Quote Originally Posted by thatguy View Post
    Proof that
    A little knowledge can be a dangerous thing!
  9. Likes ga-hvac-tech liked this post.
  10. #8
    Mar 2017
    Quote Originally Posted by ga-hvac-tech View Post
    If its a new install often the condenser will have enough charge for a moderate sized lineset. I was shocked when I installed a Fujitsu that the manual stated it had enough juice for up to 66 ft of lineset. It was a 2 ton fujitsu condenser. Pretty amazing in my book. Typical residential jobs will easily have a 35+ ft of lineset and often I end up usually putting in about a 1lb of charge or so.
  11. #9
    May 2014
    Bay Area California
    Probably a mini-split.
    Quote Originally Posted by 2sac View Post
    I do a triple evac with nitro to remove non condensables.
  12. #10
    You have a mini-split unit? So there is no liquid outside of the outdoor unit while cooling - right?
    In heating mode the small line is liquid though, isn't it?
    Why do you want to check the sub cooling? Just a technical curiosity? Or is there some requirement of the job for knowing the sub cooling?
    PHM
    Quote Originally Posted by ant27lfc View Post
    Many thanks
    PHM
    The conventional view serves to protect us from the painful job of Thinking
  13. #11
    Apr 2006
    Tyler, Tx
    If you suspect low subcooling
    1. Find the leak
    2. Find the leak.
    3. Recover refrigerant
    4. Pressurize with nitrogen
    5. Find the leak
    6. Read the install manual
    7. Calculate how much charge to weigh in based on manual
    8. Evacuate system
    9. Weigh in charge
    On most minisplit you cannot check liquid line subcool.
  14. #12
    Apr 2020
    Garner NC
    upon lookup the LG UM42 is a pancake AH..the SC info is on the outdoor unit...