Thread: Condenser feeder sizing

  1. #1
    Join Date
    Sep 2019
    Posts
    1
    Post Likes

    Condenser feeder sizing

    I need to wire up a sub panel for two condensers and the electrician put 8/2 romex for feeder I can’t for the life of me find the formula for calculating if this is enough for two identical condensers with a MOCP of 30amps
    and a minimum circuit ampacity of 18.7
    With a RLA 14.1 amps and a FLA of 77


    Sent from my iPhone using Tapatalk

  2. #2
    Join Date
    Aug 2001
    Location
    Pavilion, NY
    Posts
    4,437
    Post Likes
    8/2 romex (60 deg conductor) would be placed on 40amp breaker in the main panel to the sub.

    Each condenser would be wired using 12 gauge conductor and each having a 30a breaker per article 440 of nec.

    Sent from my SM-N960U using Tapatalk
    ...