Thread: YMC2 york chiller - "evaporator - low pressure" Fault

  1. #1
    Join Date
    Mar 2018
    Posts
    53
    Post Likes

    YMC2 york chiller - "evaporator - low pressure" Fault

    Suddenly, i got this fault on YMC2 chiller: "evaporator - low pressure" and system doesn't run anymore.

    2 min after starting it, it surges, shuts down and shows "evaporator - low pressure" fault.

    I haven't found any refrigerant leak.

    Expansion valve is actuating.

    Enough water flow rates. Inlet chilled water and condensing water temperature are correct.

    Any thoughts?

  2. #2
    Join Date
    Nov 2011
    Location
    CO
    Posts
    9,745
    Post Likes
    Did you verify the transducer is reading correctly?

  3. #3
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    1,238
    Post Likes
    Verify transducer is reading correct.
    Verify your leak detector is working.
    Take your water pressure drops with only one gauge, pressure drop on sales order screen is in feet water column not PSID.
    Could be divider in water box has failed or evaporator tubes are dirty.


    Sent from my iPhone using Tapatalk

  4. #4
    Join Date
    Sep 2008
    Location
    Sunrise,fl
    Posts
    136
    Post Likes
    Did you check the variable flow actuator and the liquid level sensor

  5. #5
    Join Date
    Aug 2019
    Location
    LA
    Posts
    166
    Post Likes
    Level in condenser? VGD moving?

  6. #6
    Join Date
    Jan 2013
    Location
    United Kingdom
    Posts
    336
    Post Likes
    Upload a history log for us to look at ?

  7. #7
    Join Date
    Mar 2018
    Posts
    53
    Post Likes
    Thread Starter
    - Pressure transducer reading is good;
    - I've used same manometer for water pressure drop;
    - Leak detector is working
    - There is no variable flow actuator
    - VGD is moving

    But....

    Today i've checked condenser level sensor. No good news.

    I've set level control valve to MANUAL and I was able to start it and get it running. I had stable operation at 30% level control valve command. Anything below 30% and condenser level got high, visor got 100% filled and chiller started to surge.

    However, I have two chillers running in parallel. Parameters below were taken when they both were at 55% input load, 13C CWET, 7C CWLT.

    Chiller A, which is working properly:
    -Active level setpoint = 46%
    -Condenser refrigerant level = 46,8%
    -Condenser refrigerant visor at about 25%
    -Level control valve command = 23% (automatic mode)

    Chiller B, which is the subject of this matter:
    -Active level setpoint = 35%
    -Condenser refrigerant level = 10,1%
    -Condenser refrigerant visor at about 50%
    -Level control valve command = 31,2% (manual mode)

    As we can see, condenser liquid level sensor from chiller B is not reading correctly, as it reads only 10% when actual level is higher than chiller A which has 45% reading.

    I operated chiller B like this for like 2hrs. At the moment i set the valve back to auto, valve was closing and it started to surge and shutdown.

    Anything I can do other before replacing liquid level sensor?

    ive uploaded some pictures.

    PS.: As you can see, march 30th i got low pressure warning as well, but its not related. operator closed chilled water valve with chiller running.
    Attached Thumbnails Attached Thumbnails 20200403_170151.jpg   chiller A.jpg   Chiller B visor.jpg   chiller b.jpg   history log.jpg   chiller B - system.jpg  

  8. #8
    Join Date
    Aug 2019
    Location
    LA
    Posts
    166
    Post Likes
    U can try to recalibrate but I would think it will not work. Replacement should be easy. Just set 0 before u add refrigerant back.

  9. #9
    Join Date
    Mar 2015
    Location
    PA
    Posts
    292
    Post Likes
    I would try to calibrate it first. https://docs.johnsoncontrols.com/chi...YrMgBWZPWVI5Mg

  10. #10
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    1,238
    Post Likes
    If you need the chiller on line drive the liquid level control valve to open and pull the electrical connector off the valve , power loss will but valve back to auto. Other wise get the tech letter on how to calibrate , if it will not calibrate just the head can be replaced and get you on line.


    Sent from my iPhone using Tapatalk

  11. #11
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    1,238
    Post Likes
    There is a 30 page tech letter that covers all the styles. It has part numbers in it.


    Sent from my iPhone using Tapatalk

  12. #12
    Join Date
    Aug 2019
    Location
    LA
    Posts
    166
    Post Likes
    I would not pull power from valve actuator, that is a falling film evaporator. If the refrigerant level is to high in evaporator it could cause much worst issues.

  13. #13
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    1,238
    Post Likes
    Let him know why.


    Sent from my iPhone using Tapatalk

  14. #14
    Join Date
    Aug 2019
    Location
    LA
    Posts
    166
    Post Likes
    Your can cause carry over and loss of liquid seal

  15. #15
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    1,238
    Post Likes
    Loss of liquid seal alarming is now ignored below 40% FLA with the new software. To eliminate false warnings. It was found that the loss of seal at low loads has no ill effect.


    Sent from my iPhone using Tapatalk

  16. #16
    Join Date
    Aug 2019
    Location
    LA
    Posts
    166
    Post Likes
    True but force the refrigerant in to the evaporator and run the condenser dry will have I’ll effects.

  17. #17
    Join Date
    Mar 2018
    Posts
    53
    Post Likes
    Thread Starter
    Anybody could share the link to sensor callibration?

    Do I need to change all the sensor or only part of it?

  18. #18
    Join Date
    Jan 2013
    Location
    United Kingdom
    Posts
    336
    Post Likes
    I could email you the document but your email is not in your profile

  19. #19
    Join Date
    Mar 2018
    Posts
    53
    Post Likes
    Thread Starter
    i've attached a photo of the sensor board.
    Attached Thumbnails Attached Thumbnails WhatsApp Image 2020-04-07 at 2.46.10 PM.jpeg  

  20. #20
    Join Date
    Mar 2018
    Posts
    53
    Post Likes
    Thread Starter
    i've updated my profile with my email

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •