Thread: I'm not Proud to do this...but customer could not afford new system or coil.

  1. #1
    Join Date
    Sep 2009
    Location
    Marietta, GA
    Posts
    3,719
    Post Likes

    I'm not Proud to do this...but customer could not afford new system or coil.

    The customer could not afford a new system nor could he afford to get a new coil installed. Actually its an A/H so it would have been a new A/H... so I just did whatever I could do for him and gave no guarantee it will hold up or no other leak will form. Found 3 nicks on distribution capillary tubes... well trying to fix the last one it snapped off where it entered the coil . LOL, can't believe I jerry ragged that sucker too. Four leaks fixed... Worked great when I was done but I think next time I won't do that..
    Attached Images Attached Images   
    wHen I diE I hOpe gOd haS mErcy oN my SiNful LifE

  2. Likes ksefan liked this post.
  3. #2
    Join Date
    Aug 2008
    Location
    Hibbing, MN
    Posts
    1,301
    Post Likes
    I’ve been know to do that from time to time.
    If God didn't want us to eat animals... He wouldn't have made them out of MEAT.

  4. #3
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    You did good for what you were presented. Blame that on the installer for not inspecting that coil before commissioning.

  5. #4
    Join Date
    Mar 2008
    Location
    kansas
    Posts
    2,521
    Post Likes
    As long as you got paid,and didn’t rape the customer I see no issues
    Honeywell you can buy better but you cant pay more

    I told my wife when i die to sell my fishing stuff for what its worth not what i told her i paid for it

  6. Likes kdean1 liked this post.
  7. #5
    Join Date
    Sep 2009
    Location
    Marietta, GA
    Posts
    3,719
    Post Likes
    Thread Starter
    Quote Originally Posted by VTP99 View Post
    You did good for what you were presented. Blame that on the installer for not inspecting that coil before commissioning.
    The system is super old. I think close to 19-20 yrs old. So it must of been installed right... Ah naw.. wait a minute.. I just remembered.. there was no FD on the LL... damn installers. Loll

    Don't worry I did install a bi-flow FD on the LL. Recharged with 407c. Unit is Bryant hp system.

    So the leaks interestingly leaked where there were plastic zip ties were attached. Who knew after so long the zip tie rubbing with the cap tube make nicks and eventually make it leak. I hope next year the customer changes the system before another major break down.
    wHen I diE I hOpe gOd haS mErcy oN my SiNful LifE

  8. Likes VTP99 liked this post.
  9. #6
    Join Date
    Sep 2009
    Location
    Marietta, GA
    Posts
    3,719
    Post Likes
    Thread Starter
    Quote Originally Posted by crazzycajun View Post
    As long as you got paid,and didn’t rape the customer I see no issues
    Definitely got paid and it was very reasonable for the customer.

  10. #7
    Join Date
    Oct 2012
    Location
    riverside calif
    Posts
    794
    Post Likes
    I see no shame here
    Sent from the van with the a/c on.

  11. #8
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    22,116
    Post Likes
    A tip I got from this site years ago for nicked distributor tubes. Strip out a section of #18 stat wire. Wrap it around the tube where the leak is keeping the wire tight to itself. Then solder over the whole thing. The tight wrap on the wire keeps the solder from entering the distributor tube. I have done it a couple times.

  12. #9
    Join Date
    Jun 2006
    Posts
    745
    Post Likes
    You did nothing wrong.

  13. #10
    Join Date
    May 2004
    Location
    SE Pennsylvania
    Posts
    2,617
    Post Likes
    It worked, you did good. Problem is too many people want to condemn every piece of equipment that doesn't work or they don't feel like fixing which seems to be acceptable these days.

  14. Likes RMSG01, bigdmike liked this post.
  15. #11
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Happens everyday in the commercial end.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  16. Likes ga-hvac-tech, RMSG01 liked this post.
  17. #12
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes
    Quote Originally Posted by BNME8EZ View Post
    A tip I got from this site years ago for nicked distributor tubes. Strip out a section of #18 stat wire. Wrap it around the tube where the leak is keeping the wire tight to itself. Then solder over the whole thing. The tight wrap on the wire keeps the solder from entering the distributor tube. I have done it a couple times.
    Ive done this.


    Sent from my iPhone using Tapatalk

  18. Likes ga-hvac-tech liked this post.
  19. #13
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes
    Ide be surprised if the tube sheet does not leak. Calls like these can come back to bite you. And you may have stated no warranty but that doesn’t mean the customer is going to roll over if a problem comes up shortly down the road.

    Nothing wrong with repairing a rub out on a distributor of anywhere else but, ide make it crystal clear and put it in righting that if the coil leaks next week you are at square one and get pictures of the leaks you are repairing and advise you dont know if there are other leaks or not even if you know there is not.


    Sent from my iPhone using Tapatalk

  20. Likes ga-hvac-tech, kdean1 liked this post.
  21. #14
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,739
    Post Likes
    Quote Originally Posted by mofotech View Post
    Definitely got paid and it was very reasonable for the customer.

  22. Likes VTP99 liked this post.
  23. #15
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,457
    Post Likes
    No shame in what you did. I would do that every day of the week. If I can see the leak, I will fix it. When they occur right at the tube sheet, I can fix about half of those, the other half no way.
    I do a triple evac with nitro to remove non condensables.

  24. #16
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,828
    Post Likes
    You should be damned proud. You did the right thing and you have the skills required To do it. Any fool can sell a new one or walk away.

    PHM
    ----------

    Quote Originally Posted by mofotech View Post
    The customer could not afford a new system nor could he afford to get a new coil installed. Actually its an A/H so it would have been a new A/H... so I just did whatever I could do for him and gave no guarantee it will hold up or no other leak will form. Found 3 nicks on distribution capillary tubes... well trying to fix the last one it snapped off where it entered the coil . LOL, can't believe I jerry ragged that sucker too. Four leaks fixed... Worked great when I was done but I think next time I won't do that..
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  25. Likes BBeerme, bigdmike liked this post.
  26. #17
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    22,116
    Post Likes
    You know I love the way this site will get behind someone for doing the right thing in one thread but then if they happen to do something wrong in another turn around and smack them around a bit if they need it.

    Not saying the OP has done anything wrong in this or any other thread just you can see the backing in this thread.

  27. #18
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    I guess it's a form of check & balance. Personally I like it when a tech does what's the best interest of his customer.
    Now if that same tech willfully wrongs his customer I think it's appropriate to call him out.

  28. #19
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,457
    Post Likes
    Couple of weeks ago I saw a refer leak on a condenser coil on an Intellipak, oil running down from midway in the coil. Got that building maybe a year ago. My first time there doing a PM. I do a quote for three hours just to determine if it was repairable.

    That may sound like a lot of time to some, just to determine if it was repairable, but it's probably a few grand to replace that coil. And you've got travel time, time to check in and out with tenant, packing equipment to and from the roof, then doing all of the paperwork.

    As it turned out, it took the full three hours.

    Now keep in mind, I learned early on how important a leak check and repair is, and I got very good at it. And I almost never condemn a piece of equipment, repairs are cheaper and last a long time when done properly.

    So, on this unit, verified a current leak with my H-10. But for the life of me, couldn't locate it with the soap bubbles. For those of that don't know what Intellipak is, the condenser coil is in the order of something like 6' x 8' feet and three or four tube passes deep.

    Anyway, the coil was repaired in that same spot by the previous contractor, so fins already cut/ripped away.

    Just couldn't pin point the leak, had to be on an inner pass that I couldn't get my mirror to. So, if I can't get my mirror to it, no way the torch is going in there.

    Then it took me almost an hour just to do the paper work. Why? Because I couldn't figure out how to get the old coil out, and the new coil in. Well, that's not entirely correct, taking things apart is easy. But how to get it back together? And how many men?

    I've replaced a few of those before, but this one was different. I eventually figured it out. Instead of going up through the top like the others, there's just a few screws, and it slides out the side. It'll be a bit tricky with the crane, but definitely doable.

    Put a note in the write up that if I'm not on that job, the man hours [and other potential problems] would go way over the quote.

    Bottom line, if I could have repaired that coil, I would have. We as a company would have made less, but as a service to the customer, it would have been the right thing to do. And as a side note, I absolutely know when I make a diagnoses like that, if they call for a second opinion, I am 100% covered.
    I do a triple evac with nitro to remove non condensables.

  29. Likes kdean1 liked this post.
  30. #20
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes

    I'm not Proud to do this...but customer could not afford new system or coil.

    Quote Originally Posted by BBeerme View Post
    Couple of weeks ago I saw a refer leak on a condenser coil on an Intellipak, oil running down from midway in the coil. Got that building maybe a year ago. My first time there doing a PM. I do a quote for three hours just to determine if it was repairable.

    That may sound like a lot of time to some, just to determine if it was repairable, but it's probably a few grand to replace that coil. And you've got travel time, time to check in and out with tenant, packing equipment to and from the roof, then doing all of the paperwork.

    As it turned out, it took the full three hours.

    Now keep in mind, I learned early on how important a leak check and repair is, and I got very good at it. And I almost never condemn a piece of equipment, repairs are cheaper and last a long time when done properly.

    So, on this unit, verified a current leak with my H-10. But for the life of me, couldn't locate it with the soap bubbles. For those of that don't know what Intellipak is, the condenser coil is in the order of something like 6' x 8' feet and three or four tube passes deep.

    Anyway, the coil was repaired in that same spot by the previous contractor, so fins already cut/ripped away.

    Just couldn't pin point the leak, had to be on an inner pass that I couldn't get my mirror to. So, if I can't get my mirror to it, no way the torch is going in there.

    Then it took me almost an hour just to do the paper work. Why? Because I couldn't figure out how to get the old coil out, and the new coil in. Well, that's not entirely correct, taking things apart is easy. But how to get it back together? And how many men?

    I've replaced a few of those before, but this one was different. I eventually figured it out. Instead of going up through the top like the others, there's just a few screws, and it slides out the side. It'll be a bit tricky with the crane, but definitely doable.

    Put a note in the write up that if I'm not on that job, the man hours [and other potential problems] would go way over the quote.

    Bottom line, if I could have repaired that coil, I would have. We as a company would have made less, but as a service to the customer, it would have been the right thing to do. And as a side note, I absolutely know when I make a diagnoses like that, if they call for a second opinion, I am 100% covered.
    I had a carrier Evap coil like that. 15 ton air handler four to five rows deep. First time I got there it was practically dry and put in three sticks of leak stop and charged it up. Anyway it didn’t work and it was very easy to find with the H 10. Could not make bubbles. I was picking up the leak around the tube sheets but figured it may have been in the middle of a tube and was traveling under the nickel coating.

    I wasn’t so much concerned about the cost of the coil for the customers sake but was more concerned about the wait time. Carrier did not have the coil sitting on a shelf and would not have one until they did a factory run something like four months out and it was cool in a office along with some warehouse space


    Sent from my iPhone using Tapatalk

+ Reply to Thread
Page 1 of 5 12345 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •