    Quote Originally Posted by timjimbob View Post
    OK Use larger walk-in box.
    #2 "Equipment NOT designed for the parameters it is operating in will use way more power." Only parameter that may be off is AHU temperatures may be 75 to 80 ambient. Not that far off. CU is within parameter.

    I have free HPCU from jobs all the time. same with AHU.

    Not all applications are restaurant and health code. Hunting camp, beer storage, morgue
    There's a product called CoolBot. Turns a window shaker into a W I Cooler system It does work but eventually kills the window shaker. Usually after the box is filled. See it with hunters out here 2 or 3 times a season. I collect my service call and tell them when they want a reliable system let me know.

    Your set up will probably work but is labor intensive. reliability is another issue.

  2. #42
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    30,638
    Post Likes
    That's why I wouldn't do it. Someone could get sue happy, call in another for a second opinion, and that second opinion would say the install is completely the wrong application.


    Quote Originally Posted by pecmsg View Post
    There's a product called CoolBot. Turns a window shaker into a W I Cooler system It does work but eventually kills the window shaker. Usually after the box is filled. See it with hunters out here 2 or 3 times a season. I collect my service call and tell them when they want a reliable system let me know.

    Your set up will probably work but is labor intensive. reliability is another issue.
    I do a triple evac with nitro to remove non condensables.

  3. #43
    Join Date
    Sep 2002
    Posts
    29,901
    Post Likes
    You know I'm with you on this, right? <g>

    Although I do disagree in the details you want to apply.

    I'll help you do what in you want in any way I can but I think you will get further ahead faster by putting the condensing unit outside the box and the air handler in the box. Or the air handler on top with two big 90º ells down into the box.

    Do you have a garage at your house?

    PHM
    ---------



    Quote Originally Posted by timjimbob View Post
    Compressor motor heat is rejected through the condenser on a refrigerant cooled compressor.
    Hey, Tesla didn't do a study of drive time listenership to determine how powerful the first transmitter needed to be. I just need someone with a spare cooler box- maybe a florist?
    PHM
    --------
    The conventional view serves to protect us from the painful job of Thinking

  4. #44
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,459
    Post Likes
    Thread Starter
    Florist shop. Room temp is 72 degrees. Box temp is 40 degrees where outside hpcu is installed in the walk-in box. Plenty of room and no nsf concerns.

    Parameters of a residential hp.. outside ambient is 40 and inside room temperature is 72 degrees. Same temperatures.

    Heat from compressor is removed through the freon to the condenser coil. Hermetic compressors are refrigerant cooled.

  5. #45
    Join Date
    Oct 2011
    Location
    Harrisburg, NC
    Posts
    1,534
    Post Likes
    In NC they just passed code about this... using comfort cooling products in refrigeration. So its not a matter of IF or Who, but is it allowed?

    It was brought to the attention of our department by the NC State Board of Refrigeration Contractors that some businesses are using after-market controls attached to comfort cooling equipment to act as refrigeration units for produce cooling. The aftermarket controls and devices that force the comfort-cooling unit to cool to a lower temperature than it was designed for is not in compliance with the manufacturer's installation instructions and is therefore in violation of the NC Building Code. We clarified that this is a violation of NCMC 304.1 and/or 1101.2 if this occurs in a building or process where the NC Building Code is applicable. These sections are reprinted next:
    304.1 General. Equipment and appliances shall be installed as required by the terms of their approval, in accordance with the conditions of the listing, the manufacturer's installation instructions and this code. Manufacturer's installation instructions shall be available on the job site at the time of inspection.1101.2 Factory-built equipment and appliances. Listed and labeled self-contained, factory-built equipment and appliances shall be tested in accordance with UL 207, 412, 471 or 1995. Such equipment and appliances are deemed to meet the design, manufacture and factory test requirements of this code if installed in accordance with their listing and the manufacturer's installation instructions.
    If the cooling unit is located in a structure, and performing a purpose that meets the definitions of Industrial Equipment, then it is outside the scope of the NC Building Code, reference NCGS 143-138 paragraph b9, but it may be subject to other agency and licensure rules.

    I can't fix it if it won't stay broke..

  6. Likes R600a liked this post.
  7. #46
    Join Date
    Oct 2011
    Location
    Harrisburg, NC
    Posts
    1,534
    Post Likes
    Quote Originally Posted by timjimbob View Post
    Florist shop. Room temp is 72 degrees. Box temp is 40 degrees where outside hpcu is installed in the walk-in box. Plenty of room and no nsf concerns.

    Parameters of a residential hp.. outside ambient is 40 and inside room temperature is 72 degrees. Same temperatures.

    Heat from compressor is removed through the freon to the condenser coil. Hermetic compressors are refrigerant cooled.
    Ok. After seriously considering this setup. Why would you choose a heat pump condensing unit?

    If to 'run in heat to cool the space', aren't you just moving the compressor inside the cooler?

    This, as I see what you are thinking, is a 1hp condensing unit on top of a cooler piped to a 9,000btu evap. (Btu and HP are just random numbers)

    Except that instead of the compressor being on top with the condenser coil, it's inside the cooler with the evap (in your plan, the coil of the HP).

    How would this benefit over a standard cooler install with the condenser on top of the box inside the store?

    Sent from my remote link to R2D2 using Tapatalk

    I can't fix it if it won't stay broke..

  8. #47
    Join Date
    Jul 2019
    Location
    Oklahoma home its in the name
    Posts
    7,551
    Post Likes
    Quote Originally Posted by BadDaddy420 View Post
    Ok. After seriously considering this setup. Why would you choose a heat pump condensing unit?

    If to 'run in heat to cool the space', aren't you just moving the compressor inside the cooler?

    This, as I see what you are thinking, is a 1hp condensing unit on top of a cooler piped to a 9,000btu evap. (Btu and HP are just random numbers)

    Except that instead of the compressor being on top with the condenser coil, it's inside the cooler with the evap (in your plan, the coil of the HP).

    How would this benefit over a standard cooler install with the condenser on top of the box inside the store?

    Sent from my remote link to R2D2 using Tapatalk
    I think the main point was to use cheaper equipment which is not a good reason in my opinion.

    Sent from the Okie state usin Tapatalk

  9. #48
    Join Date
    Oct 2011
    Location
    Harrisburg, NC
    Posts
    1,534
    Post Likes
    Quote Originally Posted by R600a View Post
    I think the main point was to use cheaper equipment which is not a good reason in my opinion.

    Sent from the Okie state usin Tapatalk
    Which is probably why NC wrote the code.

    Sent from my remote link to R2D2 using Tapatalk

    I can't fix it if it won't stay broke..

  10. Likes R600a liked this post.
  11. #49
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,459
    Post Likes
    Thread Starter
    I repeat, Using conventional hp equipment will not push it outside it’s design envelope. Hpcu is inside a 40 degree environment (cooler box). The ahu, rejecting heat, is in an comfortable 75 degrees inside a building.
    Why is this any different from a heat pump installed in a house?
    The outside unit that is typically called condensing unit containing the compressor rejects much of its compressor motor heat out the condenser coil, not the compressor shell. So heat is not added to the cooler box.

    I have built many walk-in coolers that cool non-food products. Private hunting camps use walk-in coolers and are built by members on a budget who could care less on “pretty”.
    Let’s forget energy and health codes for now.

  12. #50
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    32,874
    Post Likes
    OK

    You put the condenser in the Walk In box, fire it up, it pulls down begins to frost and ice over. Time for defrost Woosh

    What's going to happen to the condensate
    What's going to happen to the box temperature (your in a confined space)


    Now when defrosts complete you have a large Pull Down can it handle it?

  13. Likes R600a liked this post.
  14. #51
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    32,874
    Post Likes
    Another thought How are you going to start if that box is 70 +°? Heat pumps dont like hot pull downs!

  15. Likes R600a liked this post.
  16. #52
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,459
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    Another thought How are you going to start if that box is 70 +°? Heat pumps dont like hot pull downs!
    Good point, but older conventional walk-in compressors often overload on start-up. CC regulator keeps it under control. I don't see much anymore on scroll cooler CU.

  17. #53
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    32,874
    Post Likes
    Quote Originally Posted by timjimbob View Post
    Good point, but older conventional walk-in compressors often overload on start-up. CC regulator keeps it under control. I don't see much anymore on scroll cooler CU.
    Heat pumps dont like 70° ambient heat mode!

  18. #54
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    32,874
    Post Likes
    Dont get me wrong theres ways around that but it involves more controls and $

  19. Likes R600a liked this post.
  20. #55
    Join Date
    Sep 2002
    Posts
    29,901
    Post Likes
    I like the idea of the idea - but I can't see any good reason to do it this way. Nothing about it provides a benefit which can't be had easier, cheaper, and better.

    Reverse cycle defrost systems work well and fast and cheap - but to my knowledge you have to built the condensing unit. Something I like, and would like to try, is a single TXV system. It doesn't even have to work very well in defrost as the defrost times are incredibly short. The system doesn't really even stabilize it's operation before the frost is gone. <g>

    A nice thing about converting a refrigeration condensing unit for reverse cycle defrost is that they typically have a single-feed coil.
    PHM
    --------