Results 21 to 40 of 55
Thread: Walkin cooler This will work.. Just need someone to do it for me
  1. #21
    Float'N Vally, MS
    Let's look at this (as if it works)
    1) HP C.U. inside of a walking is taking up valuable real estate.
    2) Equipment NOT designed for the parameters it is operating in will use way more power. Very inefficient.
    3) Is there a better way to do this... Yes
    Then why??
    Oh, you got stuff laying around that you want to put to use... Go for it!
    Life is too short, Behappy!
    TFMM
  2. #22
    Southold, NY
    I can get a new 1/2 HP refrigeration condensing unit and evaporator for around $1500.
    What are you doing about the heat generated by the compressor inside the WI?
    Never seen a WI with extra space for a condensing unit.
    Don't forget that HPCU is not NSF certified so cant keep food in there.
  3. #23
    Jan 2010
    Not gonna happen or you'd have seen it done already. Anyone here seen this done ?
  4. #24
    Southold, NY
    Ive seen A/C condensers hooked up to W I Evaps. They somewhat work.
  5. #25
    Jan 2010
    Yes and even window shakers but a heat pump inside a walk-in cooler ?
  6. #26
    Southold, NY
    Wasn't Kramers Thermo Bank a Heat Pump?
  7. #27
    Jan 2010
  8. #28
    Southold, NY
  9. #29
    May 2014
    Bay Area California
    Probably on the Wall of Shame.
    I do a triple evac with nitro to remove non condensables.
  10. Likes Core_d liked this post.
  11. #30
    Dec 2012
    columbus, OH
    Quote Originally Posted by ammoniadog View Post
    The thing you call a heat pump condensing unit is actually going to be an evaporator. The real condenser (the thing you will be putting in the kitchen) is designed to have a return air temperature of about 70°F.
    You state that this kitchen will be 80°F? That's pretty good as far as kitchen temps go, but it's pretty horrible for a heat pump air handler. That's right on the ragged edge of where that thing will be able to function without tripping it's high pressure switch (if it has one).
    Hey, I just came up with an idea for you. Instead of a "condensing" unit and an air handler, Why not get yourself 2 "condensing" units? One inside of the box and one on the outside. That way you will be good for a kitchen temperature of around 110° or so (and you'll have a spare compressor for "just in case").
    Just make sure you have really high ceilings in that kitchen (and inside of the cooler) to avoid recirculation issues.
    Great idea!
    Get a 2 ton cu and a 5 ton ah..
  12. Likes Poodle Head Mikey liked this post.
  13. #31
    I don't think so - and there was no reversing valve. They just saved up (banked - get it? <g>) some heat to help maintain hot gas for defrost.
    PHM
    I
    PHM
    The conventional view serves to protect us from the painful job of Thinking
  14. #32
    The other way. The low suction is going to reduce compressor capacity - not increase it.
    Quote Originally Posted by Core_d View Post
    PHM
  15. #33
    Virginia
    Just think …. no more cleaning nasty walkin coils , just replace the air filter and go home !
  16. #34
    I don't know how he is going to deal with the R-410 charged HP.
    But let's toss around some general numbers -
    A 2 ton R-410 compressor (not condensing unit!) running a 30º suction will be pumping about 17,000 BTU's per hour. Charge it with R-407C and it will pump about 12,000 BTU's.
    A 10 by 20 by 8 working walk-in box at 34º will have a load of about 12,000 BTU's per hour.
    If the AH and the CU have pistons - that will work.
    TXV's will have to be changed to match the refrigerant.
    Stay with R-410 and it will short cycle.
    So??? What is this box going to be like?
    PHM
  17. #35
    Southold, NY
    More like 24 - 36K BTU's depending!
  18. #36
    Dec 2012
    columbus, OH
    Nothing you can do about “low suction pressure” in a cooler... but, a larger air handler or “kitchen unit” would eliminate any concern about high head and get the most capacity possible out of it.
  19. #37
    Dec 2012
    columbus, OH
    Did i read this correctly? The outdoor unit is setting on the floor in the cooler and the indoor unit is keeping the cooks nice and toasty in the kitchen?
  20. #38
    Southold, NY
    I don't know many commercial kitchens that are much below 100°f but over sized condenser will help............….Until it gets packed with grease.
  21. #39
    Oct 2002
    Plano, TX
    Quote Originally Posted by behappy View Post
    Then why??
    OK Use larger walk-in box.
    #2 "Equipment NOT designed for the parameters it is operating in will use way more power." Only parameter that may be off is AHU temperatures may be 75 to 80 ambient. Not that far off. CU is within parameter.
    I have free HPCU from jobs all the time. same with AHU.
    Not all applications are restaurant and health code. Hunting camp, beer storage, morgue
  22. #40
    Oct 2002
    Plano, TX
    Compressor motor heat is rejected through the condenser on a refrigerant cooled compressor.
    Hey, Tesla didn't do a study of drive time listenership to determine how powerful the first transmitter needed to be. I just need someone with a spare cooler box- maybe a florist?