Results 1 to 12 of 12
Thread: Condenser Line Set Sizing Question
    Oct 2018
    New York
    Hello. So I have an install coming up soon for a new 3 ton Goodman or Bryant AC. Evaporator is in the attic and they want to relocate the condenser.
    Problem is theres a 3/4 suction line and 3/8 Liquid line. The air handler is already about 25-30 feet away from the condenser and they want to move it another 25 feet away, roughly 50 feet total from the indoor coil to the condenser. Goodman calls for anything 50 feet to be 7/8 suction and 3/8 liquid not sure about Bryant but if memory serves it's the same thing. Changing the line is close to impossible due to circumstances.
    My question is can I run 7/8 suction on the outside 25 feet connected to the 3/4 going to the attic.
    Should I just run the whole thing 3/4.
    Or I dont think this is practical and dont really want to do this but should I up the system to a 4 ton. I know I Will loses efficiency but more worried about losing capacity. The house is 1,300 Square feet.
    Thanks.
    Jun 2017
    Portland, OR(Previous: Arizona, Texas, Oklahoma)
    Quote Originally Posted by HVAC Guy7 View Post
    Thanks.
    I would check in the manual with the product you are about to install to see which linesets are approved for what length. If you can't find it call tech support and get an answer
    Or
    You can install it, wait a few months and install another one.
    Sent from my LM-G710VM using Tapatalk
    Jan 2014
    New England
    Why don’t you do a load calculation 1st to see what you really need, chances are you probably can get by with a tad smaller unit, negating your linesize worries.
    Here’s a free one: https://www.loadcalc.net/
    Upsize to a 4 ton? Your ductwork can handle 4 tons let alone 3 tons?
  4. Likes FreeThrowGuy liked this post.
  5. #4
    The suction line flow direction is all horizontal and down, right?
    So how much of the line run can be installed as / be changed to: 1 1/8" ? Certainly all of the line set is not inaccessible, right? Then the only part which will be undersized is the 3/4" portion and the 1 1/8" portions will contribute pretty much nothing in terms of pressure drop.
    Why are you installing a 3 or 3 1/2 ton system in a 1300 square foot residence in New York?
    PHM
    Thanks.
    PHM
    The conventional view serves to protect us from the painful job of Thinking
  6. #5
    May 2019
    Central, IL
    I second the load calc, i cool my 1200 sq ft house with 2tons , and it has short cycles on all but the hottest days ( 95+)
  7. #6
    Jan 2010
    Well the size really depends on the integrity of the envelope. So this leads us back to a proper load calculation.
  8. #7
    Southold, NY
    X-5 You need a load calc before changing anything!
  9. #8
    Jul 2000
    Guayaquil, EC
    According to the Goodman long lineset capacity loss chart for a 3-ton R410A unit, if the entire 50 ft run is 3/4" the capacity multiplier would be .93 and if it's 7/8" the multiplier would be .98 . If 1/2 the total run is 3/4" and 1/2 is 7/8" the multiplier would then be .955, so the resulting capacity would be 34,380 Btuh.
    https://docs.google.com/viewer?url=h...d%2BTP-107.pdf
  10. #9
    Jun 2017
    Quote Originally Posted by icemeister View Post
    ^ there's your educated answer
  11. #10
    Jan 2015
    San Diego, CA
    Another vote for a load calc. A lot of homes have oversized systems and if the calc shows a smaller system you may be fine with the existing suction line diameter. Sq ft alone does not mean much - things like the climate/state you live in, the number of south facing windows, glass type etc all factor into the final sizing of the unit and airflow.
    I've been using Coolcalc lately and while there are still some issues that need to be ironed out you can generate a proper ACCA approved Man J which you can give to your customer. I also find it affordable compared to other ACCA approved software.
    www.coolcalc.com
  12. #11
    Jan 2014
    New England
    https://www.alpinehomeair.com/related/IO-258T.pdf
    Page 3 dated 2018
    Says anything over 79 feet is considered long lineset. If your going with a Goodman OD unit, install guide says to install a inverted loop by Air Handler.
    Make sure to register your the equipment as manufacturers warranty decreases significantly if never register.
    So what’s your plan, a load calculation or not going to rock the boat and replace with what’s in there already?
  13. #12
    Atlanta GA area
    Tell your contractor to run the lineset up the outside of the house, then enclose it in either a lineset hiding product...
    Or a gutter downspout.
    It is done regularly... solves the problem of needing a larger lineset.
    GA-HVAC-Tech
    GA's basic rules of home heating and AC upgrades:
    *Installation is more important than the brand of equipment
    *The duct system keeps the house comfortable; the equipment only heats and cools (and dehumidifies)
    *The value of comfort, over the long term; leave economic choices behind!
    Choose your contractor wisely!