Results 1 to 20 of 28
Thread: How to calculate chilled water usage
    Nov 2019
    Large condo building that gets chilled water from Austin Energy used for cooling. Each condo has their own HVAC unit. Is it possible to determine chilled water usage based on CFM? For example, one unit spec is: 1,100 CFM on low fan speed with a 1” filter.
    SW FL
    Quote Originally Posted by seththomas View Post
    Is it possible to determine chilled water usage based on CFM? YES
    ___ ___ ___ Q. Total = 4.5 * CFM * Enthalpy Difference { ED }
    ____ Enthalpy in and Enthalpy out are dependent on the temperature and humidity
    ______ ED = E in - E out
    Presume the difference in Air energy = Water energy
    Or determine the annual energy use based on local Coolng Degree Days (CCD)
    and an applicable ACCA Manual J calculation for each condo unit.
    However, the room temperatures are not going to be the same.
    I presume you are investigating a utility billing method for each tenant.
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities
    Nov 2019
    Yes, I am trying to determine if there is a better way to improve the current utility billing method. The chilled water is billed based on Ton Hours. To simplify the discussion, let's assume ED = 0. So using the formula for a user operating their unit for 1 hour that is 1,100 CFM, the result would be 4.5 * 60 * 1,100 = 297,000. What does this represent in terms of Ton Hours?
    SW FL
    _______________ ...... 0 = ______ ... 0
    Assume ED = 0
    Q. Total = 0
    SW FL
    T room = 75'F
    R.H. = 50%
    E in = 28.149 BTU/lbm from Psychrometric Chart
    T supply = 55'F
    R.H. = 90%
    E out = 22.205
    ED = 5.944
    Q. Total = 4.5 * 1,100 * 5.944
    ......... = 29.423 BTU/HR
    ............ = 2.45 Tons
    A/C runs ~ 300 hours per month
    ........... _______ > 100 & < 500 depending whether
    ........................................ 1. Condo is in Vancouver, Phoenix or Miami
    ........................................ 2. Size and construction of the condo
    ...………………………………………...……...…….. Condo built in 1918 or 2018
    ........................................ 3. T-stat set-point at 71'F or 79'F
    ............ 735 Ton Hours / Month ... > 245 & < 1,225
    SW FL
    AUSTIN TX
    MET DATA
    COOLING DEGREE DAYS / MONTH
    CDD MONTH RUN TIME
    .................. HOURS / MONTH
    CDD ____ ..RUN TIME .. TON HOURS
    10 JAN 9.25 __ 22.7
    21 FEB 18.93 46.4
    58 MAR 50.52 123.9
    154 APR 129.76 318.2
    348 MAY 285.21 699.3
    517 JUN 418.05 1025.1
    593 JUL 477.28 1170.3
    616 AUG 495.15 1214.1
    429 SEP 349.10 856.0
    198 OCT 165.42 405.6
    47 NOV 41.23 101.1
    14 DEC 12.80 31.4
    3005 ANNUAL 2452.70 6014.0
    IF T-STAT set at 72'F, Add 25% - 40%
    IF T-STAT set at 78'F, Subtract 20%
    Nov 2019
    Supply Air temp and RH
    Quote Originally Posted by dan sw fl View Post
    T room = 75'F
    R.H. = 50%
    T supply = 55'F
    R.H. = 90%
    E out = 22.205
    ED = 5.944
    How is the supply air temperature and relative humidity determined when the chilled water is pumped through the coils of the HVAC unit and most of the supply air is from inside the unit with only a small percentage of fresh air.
    Nov 2019
    How does the temperature of the chilled water factor into the equation
    Doesn't the temperature of the chilled water that runs through the coils factor into the determination?
    SW FL
    and
    Equipment Performance data is available from vendors though their AHU Selection software.
    + KNOWN Real Life situations.
    SW FL
    Doesn't the
    temperature of the chilled water (CW) that runs through the coils factor into the determination?
    YES, Standard CW temperature = 45'F.
    Coil Approach temperature is in the ballpark of 10'F
    depending the number of coil rows.
    http://www.ref-wiki.com/technical-in...mperature.html
    SW FL
    EERE Technical Fact Sheet
    __________ ______ SIZING
    ________________ Equipment Selection
    ……………………………….. Life-Cycle Analysis
    http://www.advantekinc.com/downloads...tSelection.pdf
    JANUARY 2002
    _____________ is or is becoming OutDated in several aspects.
    Southold, NY
    Probably easier and more accurate too just install flow meters for each user!
    Nov 2019
    [QUOTE=dan sw fl;25805305]YES, Standard CW temperature = 45'F.
    I checked with Austin Energy and the CW temperature is 44'F. I assume this factor does not directly enter into the equation, but only affects how long the blower needs to run for the temperature in the unit to reach the set temperature. In other words, if the CW temperature were warmer, the blower would need to operate for a longer period of time to reach the set thermostat temperature, correct?
  14. #14
    Southold, NY
    [QUOTE=seththomas;25805394]
    That depends on the difference between return air and supply air temperature and CFM's!
    How accurate is that 44°F? 10% deviation could be a lot!
  15. #15
    Aug 2009
    Prattville, Alabama
    This.
    If somebody was to charge me for something I'm using, I'd be upset if they can't show me how they measure how much I'm using. Especially if the billing method changed.
    In honor of RichardL: "Ain't 'None' of us as smart as 'All' of us".
  16. #16
    Nov 2019
    Flow meter
    Do you have any recommendations for flow meters?
  17. #17
    Nov 2019
    Apparently the "standard" in Austin is to allocate based on total electrical usage in each unit. This makes little sense to me since other appliances use so much more electricity than the HVAC when cooling. So someone using their 30 amp 240 v dryer a lot will get a larger allocation for chilled water.
  18. #18
    SW FL
    [QUOTE=pecmsg;25805397]
    That depends on the difference between Return Air and Supply Air temperature and CFM's!
    CW Supply Temperature is generally within ~0.8'F of design.
    _____________________________________
    THE BIGGEST UNKNOWNS are the Condo Room Temperatures.
  19. #19
    Southold, NY
    [QUOTE=dan sw fl;25805435]
    I agree but without knowing the exact temperature (Supply, return, CFM’s) how can you calculate usage accurately?
  20. #20
    SW FL
    CW flow meter use needs to be validated
    based on review of the CW Flow Diagram
    to determine how the Secondary CW loops are actually arranged and controlled.
Tags for this Thread