    REME HALO-LED

    Looks like a new LED version with zero ozone is coming out. I was about to install a regular REME HALO in my home but this is coming out end of November. Would it be a good idea to wait? Any thoughts? Thank you!!

    https://www.rgf.com/products/air/hal...-air-purifier/

  2. #2
    Join Date
    Dec 2015
    Location
    Austin
    Posts
    149
    Post Likes
    Thanks for the pointer. This device has piqued my interest.

    As far as VOCs goes testing with GC/MS and PID meters in homes is the only way to know
    Unfortunately RGF is is unlikely to provide the sort of testing needed - Before and after test with GC/MS and PID meters in real homes with typical mix of VOCs.

    What they have provided in the past - Test of a single VOC at unusually high concentration in a large fish tank - is Not the final determination. Often these tests show remarkable results. They just don't translate to real homes. I learned this by testing the MoleKule which also uses UVA LEDs.

    Still I will consider buying one test. The device will definitely Not produce any ozone. UV LEDS only produce UVA radiation which means no ozone.

    Will this device still produce Hydrogen Peroxide which RGF claimed was the magic sauce in the HALO? If not will it be as effective (if it even was effective) as the HALO?
    Is this new device just a quick response to the MoleKule (which doesn't work) and Bird device?

    Thanks again for for link.

  3. #3
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,258
    Post Likes
    Snake oil.

  4. #4
    Join Date
    Dec 2008
    Posts
    6
    Post Likes
    Thread Starter
    Quote Originally Posted by randyf View Post
    Will this device still produce Hydrogen Peroxide which RGF claimed was the magic sauce in the HALO? If not will it be as effective (if it even was effective) as the HALO?
    Is this new device just a quick response to the MoleKule (which doesn't work) and Bird device?
    I asked RGF and their response was:

    "The LED unit utilizes the same technology which we incorporate into all our products."

    Kind of vague and I do not see mention of hydro-peroxides on the LED description like on the regular HALO description.

  5. #5
    Join Date
    Dec 2015
    Location
    Austin
    Posts
    149
    Post Likes
    Quote Originally Posted by nicu2001 View Post
    I asked RGF and their response was:

    "The LED unit utilizes the same technology which we incorporate into all our products."

    Kind of vague and I do not see mention of hydro-peroxides on the LED description like on the regular HALO description.
    Thanks for inquiring.

    Not only vague but BS. Probably talking from someone in sales/marketing. He may not know better.
    But
    - UV Leds only radiate in the UVA frequency range. This frequency range does not produce Ozone.
    - The HALO uses a UVC blub that does radiate in the UVC frequency range and produces Ozone.

    Recently PCO devices have come on market that use UVA LEDs. No ozone and much longer life span. But effectiveness destroying VOCs is unknown - despite any claims by manufacturers.

    Classic PCO (photo catalytic oxidation) works as follows:
    1. UV photons radiate a catalyst that produces a very short lived, very reactive compound called - Hydorxyls.
    2. Hydroxyls break down the carbon/hydrogen bounds in VOCs
    3. VOCs are then converted to H20 and CO2.
    See -https://www.explainthatstuff.com/how-photocatalytic-air-purifiers-work.html

    Of course all the above is in a perfect world and perfect worlds don't exist.
    POTENTIAL problems include
    - partial break down products that are more toxic than the original VOC
    - excess Ozone
    - Only works at very high VOC levels. Not the levels we find in our home.

    Still PCO technology has been verified and studied in academic laboratories for decades. It's not hocus pocus although some/all commercial implementations might be.

    BUT - Commercial implementations, RGF, MOLEKULE and dozen or so other companies have not adequately demonstrated effectiveness in Real living spaces - homes.
    Most of the evidence comes from test chamber the size on big fish tanks, with unusual mixtures and concentrations of VOC - not the type of pollutants we find in our homes.

    RGF - to their credit- did a spin off on classic PCO with the HALO.
    They used UVC and a catalyst to produce Hydrogen Peroxide and Ozone that spews in the living space. The claim being that a much larger area will be covered. With Classic PCO all the action happens at the catalyst, not in the living space. Don't know if this claim was bullshit or not but a lot of folks reported positive results. Could be many reports are just confusing the smell of ozone with clean air. I don't know because there are no reports of before and after VOC reading with objective test gear in real rooms.

  6. Likes ksefan liked this post.
  7. #6
    Join Date
    Nov 2019
    Posts
    9
    Post Likes
    Quote Originally Posted by randyf View Post
    Of course all the above is in a perfect world and perfect worlds don't exist.
    POTENTIAL problems include
    - partial break down products that are more toxic than the original VOC
    - excess Ozone
    - Only works at very high VOC levels. Not the levels we find in our home.
    Have you gotten to do any testing yet? We would like to install a unit that has an added filtration system of some sort to improve the IAQ of our home. This version seems to fit the bill, but your point about the partial breakdown of VOCs is quite concerning.

  8. #7
    Join Date
    Dec 2015
    Location
    Austin
    Posts
    149
    Post Likes
    Haven't tested the new RGF device yet.
    Here's my suggestion for you:

    Determine if you even have a VOC issue.

    Use the service of https://homeaircheck.com/products/ or https://homeaircheck.com/products/
    Both companies will provide a test kit to take a sample. You return and in a week you will have results. If you levels are below 500ng/liter, you do not have a problem. Other wise you might. IMHO - its advisable to see if you have issues before spending money to remediate, especially with gear that is undetermined to work.

    If your worried about particulates these can be effectively handled by low cost HEPA filters or even the return air filters you are currently using.

    What are particulates - https://www.engineeringtoolbox.com/p...zes-d_934.html. Fascinating.

    I'll be interested in seeing how this plays our on your end.

    Good luck and please post any followup you might have.

  9. #8
    Join Date
    Nov 2019
    Posts
    9
    Post Likes
    Thanks. We are getting a new system installed next week with aeroseal and insulation. We decided to pass and purchase higher quality system air filters and to be more diligent with changing them.

  10. Likes ga-hvac-tech liked this post.
  11. #9
    Join Date
    Dec 2015
    Location
    Austin
    Posts
    149
    Post Likes
    Sounds good.

    I've really been impressed with the aeroseal process. I've heard from reputable source of remarkable results.

    Once all is said and done you should have any concerns with particulates. Just keep in mind that particulates and VOCs are two different animals.

    If you do decide to ever test for VOCs, in addition to the resources I mentioned, check out these guys.
    https://www.assaytech.com/

    Should be cheaper and accurate but with less specificity.

  12. #10
    Join Date
    Apr 2020
    Posts
    2
    Post Likes
    Quote Originally Posted by Strawbearlyjamm View Post
    Thanks. We are getting a new system installed next week with aeroseal and insulation. We decided to pass and purchase higher quality system air filters and to be more diligent with changing them.
    aeroseal is a scam

  13. #11
    Join Date
    Aug 2006
    Posts
    3,604
    Post Likes
    Why don’t you get a Standard UV with the Quartz Bulb. I installed a Sanuvox R+ on my Central Unit July 12, 2013. Just replaced the depleted lamp on March 4, 2020. The Self monitoring system told me the Three Years of lamp life we’re almost up, and gave me a weak lamp message. The Lamp life is three years of actual run time, which it monitors. My unit runs fifteen minutes out of every hour, to UVA the air. Visitors remark how the house has no odor to it. Years ago in a Hospital setting, we had to remove the lamps, and place them in a test unit, to see if they still worked. One thing I noticed was, that if the lamps had dust or any film on them they were either weak or shot. I pull mine from time to time and wipe the lamp with Isopropyl. It’s always come up clean.

  14. #12
    Join Date
    Mar 2018
    Location
    Kansas Flatlands
    Posts
    748
    Post Likes
    Quote Originally Posted by dandy1 View Post
    aeroseal is a scam
    I saw a live demo where holes and a 4x4 in piece of screen in a section of ductwork were sealed. Seemed to me to have some sort of a place in the industry. My thought was throw it out there, like reme's and humidifers, many will not want it just from the expense.

    Somebody wants a Reme, sell em a Reme. Someone wants a cover for their A/C, sell them one. Why not? If they think it's worth it and want to "pay you" for it....

  15. #13
    Join Date
    Sep 2005
    Location
    Atlanta GA area
    Posts
    47,384
    Post Likes
    Quote Originally Posted by Strawbearlyjamm View Post
    Thanks. We are getting a new system installed next week with aeroseal and insulation. We decided to pass and purchase higher quality system air filters and to be more diligent with changing them.
    IMO... this is the first place to go...

    If there are occupants in the home who have serious medical issues... one of the active air filtration systems (Honeywell or AprilAire)... is a viable option.

    Media style (4 or 5 inches thick) is the place to start!
    GA-HVAC-Tech

    Your comfort, Your way, Everyday!

    GA's basic rules of home heating and AC upgrades:
    *Installation is more important than the brand of equipment
    *The duct system keeps the house comfortable; the equipment only heats and cools (and dehumidifies)
    *The value of comfort, over the long term; leave economic choices behind!
    Choose your contractor wisely!

  16. #14
    Join Date
    Sep 2020
    Posts
    11
    Post Likes
    Most filters on the market are designed to capture particles like dust and pollen, but don’t catch gases like VOCs (volatile organic compounds) or radon. That would require an adsorbent, like activated carbon. (according to the review)
    So while many air purifiers are good at filtering pollutant particles out of the air (dust, smoke, pollen, etc.), they are not necessarily very good at removing gaseous pollutants like VOCs or radon from the air that may accumulate from adhesives, paints, or cleaning products. Allergens that are embedded into furniture or flooring are also not captured by them.
    The best advice is to address the source of indoor air pollution and ventilate your home.

  17. #15
    Join Date
    Jan 2021
    Posts
    1
    Post Likes
    I just installed this in my home and I’m having issues with the noise it makes during start up. It resonates through my metal ductwork. I replaced the first one but it still does it. Seem like it’s normal from what the manufacturer says. They say it’s the self cleaning brushes. It wakes me up at night so if this is truly how it is I would nt recommend it unless you have ductboard.