Results 1 to 15 of 15
Thread: Air handler vibrating when heat pump in heat mode
    Jan 2013
    Had a customer call me about a Trane AH causing heavy vibration when the heat comes on, when the unit is in cool mode it all works well with no vibration.. I ran the heat pump in cool mode and disconnected the orange reverse valve outside and immediately it starts to vibrate at the air handler. Im thinking replace TXV with check valve still under wareanty. Both indoor and outdoor coils were clean as well as air filter and blower wheel
    Trane AH
    M#GAF2A0A30S21SAA
    S#121415TD2V
    TrAne HP
    M#4TWB3030C1000AA
    S#12174M9N4F
    OD temp 64F
    R410
    Suction 130 psi
    Liquid 400 psi
    Compressor max amps rated 11.5 actual 7.8
    OD fan max amps rated .74 actual .7
    Capacitor was rated 40/5uf and tested the same
    Indoor was 70F
    Blower motor max rated 1.7 actual 1.4
    Jan 2012
    Missouri, USA
    What was sh/sc in heat mode?
    Jan 2013
    I didnt take SH or SC..I also spoke to Trane tech support and he also told me that he would suggest replacing the Outdoor TXV and filter drier
    Nov 2019
    Jacksonville, Fl
    Ive had a changeover valve not complete its travel and create a hammering type noise/vibration. Did your pressures bounce around at all? Amperage at O on valve coil wire? I had to dig a set of analog gauges out to catch it.
    Jan 2013
    I finally found the issue..homeowner had a different company replace the compressor and they never put back the rubber mount legs and the idiot thought that the muffler was a filter drier and removed it and added a second filter drier
    I would have had the homeowner call them with you present and have them come fix the problem they created
    Virginia
    Quote Originally Posted by pctech View Post
    JosA and JosB ....
    Dec 2019
    westchester ny
    I'm curious why the rubber mounts were only a problem in heating mode
    Jan 2013
    This is a base model Trane heat pump they kinda make noise during heat mode, the amps increase during winter time causing the motor on the compressor to vibrate and produce noise especially refrigerant pulsing thru discharge line
    Southold, NY
    So how does the amperage increase in heat mode?
    Jan 2013
    Same way a dirty condenser increases head pressure,amps and compressor becomes noisy..remember theres a filter inside when the evap becomes the condenser plus its warmer when heat is on during winter season. Ive always noticed that during my check ups on most systems when checking outdoor unit
    Float'N Vally, MS
    Quote Originally Posted by Ac_man View Post
    Same way a dirty condenser increases head pressure,amps and compressor becomes noisy..remember there’s a filter inside when the evap becomes the condenser plus it’s warmer when heat is on during winter season. I’ve always noticed that during my check ups on most systems when checking outdoor unit
    I don't know about all this.....
    But on Trane, this will cause pulsations/vibrations for sure...
    Life is too short, Behappy!
    TFMM
    Apr 2006
    Tyler, Tx
    I thought the vibration was at the Air Handler?
    Philippians 4:13
    I can do all things in him that strengthen me.
    Apostle Paul inspired by GOD.
  14. #14
    Float'N Vally, MS
    Quote Originally Posted by Artietech View Post
    Pulsating refrigerant through the lines and coil does present a vibration. I have seen this with higher SEER equipment with larger coils especially.
    TFMM
  15. #15
    Jan 2013
    The vibration was traveling from the heat pump thru the line sets all the way to the air handler