    I cannot figure out what is causing my humidity issues.

    I have been having this problem over the last few months (summer in central florida), that I never remember having an issue with in years past. When I get home everyday mid/late afternoon, my interior home temperature is 79 degrees and my humidity levels are anywhere between 53-57%. When I adjust my ac to 75-76 degrees, I notice being more uncomfortable an hour or two after getting home than when I first arrived. I'll go look at the thermostat and its reading 76-77 degrees with 60-63% humidity.

    I have been trying to figure out this problem with out much luck. I goes against my understanding about how air conditioning works that when I run the unit, my temps will drop but my humidity goes up. I should also note that my unit isn't over sized, if anything it is undersized. Here is what I have done so far with little or no improvement to the problem:

    - completely sealed chimney flu about a month ago (it was left open from the winter). Also sealed doors as best as I could. Windows are only a few years old and the seal seems fine.

    - Made sure that on all my thermostat settings, the fan is always set to auto.

    - Had a professional evaluate the system (refrigerant levels are ok, coils are good, temp differential is where it should be. He did find that the unit was short cycling. I had vacuumed out the lines about a month previously but I guess I did not clear it enough. He blew nitro through the line and flushed it out.

    - I did notice that all my chase lines in return were running into a unsealed hole. I thought the unit may be sucking in moisture from the ground, so I sealed the chase holes inside and outside with foam.

    - I did replace my old radio thermostat with an ecobee 3 about when the problem started, but it was also mid spring and humidity and temps were not near as bad. A tech I had out didn't think that could be causing my issues and everything seems to run as expected.

    I should also note that I have two units in my home. One for all the bedrooms and another for the main part of the house. I had the bedroom unit replaced inside and out (bad evaporator) about a year ago. That unit is fine. Humidity is still higher than I would like but at least when I run the air, it does go down, albeit slowly.

    If solving the issue meant getting a new unit for the main part of my home I would. But I am skeptical that it won't completely fix my issues. I really want to fix any potential underlying problems before I do that.

    Does anyone have any potential suggestions. Is there specialists out there that can handle these types of issues. I don't want to keep calling ac tech's in hopes that after hundreds of dollars, one of them has a solution.

    Please help me in my muggy home. I cannot stand feeling so uncomfortable anymore.

    Thank you in advance.

  2. #2
    Join Date
    Jun 2018
    Location
    Central Florida
    Posts
    8
    Post Likes
    Thread Starter
    FYI, unit in question is a 2.5 ton in about 1600 sq/ft

  3. #3
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Where are you measuring the RH?

  4. #4
    Join Date
    Jan 2012
    Location
    Missouri, USA
    Posts
    3,963
    Post Likes
    Have them test the static pressure and find the air handler blower performance chart. Verify airflow before anything else.

  5. #5
    Join Date
    Jun 2018
    Location
    Central Florida
    Posts
    8
    Post Likes
    Thread Starter
    Where are you measuring the RH?
    From my thermostat. I know that is not a very accurate reading and if I didn't physically feel the difference, I probably would have ignored the figures it reports. When its 74 i the house but humidity says 60%, i feel miserable.

  6. #6
    Join Date
    Jun 2018
    Location
    Central Florida
    Posts
    8
    Post Likes
    Thread Starter
    Quote Originally Posted by ksefan View Post
    Have them test the static pressure and find the air handler blower performance chart. Verify airflow before anything else.
    CAn any AC tech do that?

  7. #7
    Join Date
    Jan 2012
    Location
    Missouri, USA
    Posts
    3,963
    Post Likes
    Any tech can, most do not know how or why it is important.

  8. #8
    Join Date
    Jun 2018
    Location
    Central Florida
    Posts
    8
    Post Likes
    Thread Starter
    Quote Originally Posted by ksefan View Post
    Any tech can, most do not know how or why it is important.
    Thanks for suggesting something new. If you don't mind could you expand on what the static pressure is and why its important? I understand if you don't have the time. I'm just curious how that can affect humidity.

    edit: Watching videos on it now.

  9. #9
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,328
    Post Likes
    WHY 60% R.H. at ~ 75'F?

    2.5 Ton - 1,600 SF - Central Florida
    Return DB - Room Air - 76'F
    Return WB _________- ... 'F ?
    ___ ... Wet Bulb … ~ 66.2'F

    Supply Air DB … ... 'F ?

    Total Air Flow Rate (CFM)
    A _ 1,200
    B _ 1,100
    C _ 1,000
    D __ 900
    E __ 800

    1. A, B, C, D or E ?
    2. All of the above

    Reference document(s)?
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  10. #10
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    12,042
    Post Likes
    Cooling coil is not removing adequate moisture amounts while cooling. Usually caused by high air flow or poor cooling of the house air by the a/c.
    If you want 50%RH, the cooling coil must be less than 45^F to remove enough moisture.
    Make sense?
    Colder coil = lower moisture =lower %RH
    Keep us posted.
    Regards Teddy Bear
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •