Thread: 240v 3phase high leg question.

  1. #1
    Join Date
    Sep 2010
    Location
    miami,fl.
    Posts
    2,253
    Post Likes

    240v 3phase high leg question.

    So 3 phase 240 volt has a high leg. 2 of the 3 legs measured to ground measure 120v. While the high leg to ground measures 240v to ground. So let’s say originally the unit was a 3 phase. Some time later some one put in a single phase unit 240v. Yes you have to be sure the wire gauge (awg) is sized for now the higher amp draw. But besides that if you chose one line and the high leg line to line measures 240v. Electrically when applied to a single phase 240v unit can it cause damage? I would guess no because it’s still 240v. But on the other hand I want to say yes because some how electrically its not the same. What is your experience on this?

  2. #2
    Join Date
    Feb 2018
    Location
    Bay Area, Ca
    Posts
    3,203
    Post Likes
    Quote Originally Posted by anthonyac1 View Post
    So 3 phase 240 volt has a high leg. 2 of the 3 legs measured to ground measure 120v. While the high leg to ground measures 240v to ground. So let’s say originally the unit was a 3 phase. Some time later some one put in a single phase unit 240v. Yes you have to be sure the wire gauge (awg) is sized for now the higher amp draw. But besides that if you chose one line and the high leg line to line measures 240v. Electrically when applied to a single phase 240v unit can it cause damage? I would guess no because it’s still 240v. But on the other hand I want to say yes because some how electrically its not the same. What is your experience on this?
    None. Never done this. I am in interested to read future posts.

    Sent from my SM-G955U using Tapatalk

  3. #3
    Join Date
    Sep 2013
    Location
    Wi
    Posts
    1,026
    Post Likes
    No damage but don't take any 120 volt load off of it.

  4. Likes lions_lair, Zamoramax liked this post.
  5. #4
    Join Date
    Sep 2010
    Location
    miami,fl.
    Posts
    2,253
    Post Likes
    Thread Starter
    Quote Originally Posted by Galt View Post
    No damage but don't take any 120 volt load off of it.
    Of course not because it’s not supplying 120v. You will feed 240v to your 120v load.

  6. #5
    Join Date
    Sep 2013
    Location
    Wi
    Posts
    1,026
    Post Likes
    usually high leg will run 165 170 to ground. I remember a cafe a few towns over that had central AC installed where the guy moved some breakers around. I had installed some counter top receptacles years earlier and the cook told me ever since the AC was put in one receptacle had more power in it. but they liked it cause the meat slicer worked way better in that one.

  7. Likes lions_lair liked this post.
  8. #6
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    I would not use the "high leg" for single phase loads. Typically it's the B phase but code changes now allow for the C phase to be used. The high leg should be clearly marked in red or orange.

  9. #7
    Join Date
    Aug 2010
    Location
    Living for the Lord
    Posts
    6,837
    Post Likes
    We call it the wild leg, around here. And it's 190 volts here. Never heard of 240v to ground on the high leg.

    Sent from my LG-K540 using Tapatalk
    "If you can’t describe what you are doing as a process, you don’t know what you are doing." ~ W. Edwards Deming

    All those who wander..are not lost.

    Do NOT..mistake my kindness for weakness.

    The early bird may get the worm..but the second mouse gets the cheese.

  10. #8
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    The high leg should be 208 measured to ground.

    See this Mike Holt forum discussion.

    https://forums.mikeholt.com/showthread.php?t=146083
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  11. #9
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    2,413
    Post Likes
    You can use the high leg on 240 volt single phase but can’t pull 120 volts off the high leg. The unit doesn’t care what the phase to ground voltage is.

  12. #10
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    Quote Originally Posted by R123 View Post
    You can use the high leg on 240 volt single phase but can’t pull 120 volts off the high leg. The unit doesn’t care what the phase to ground voltage is.
    It's not phase to ground. It's phase to phase I believe the OP was referring to.

  13. #11
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    2,413
    Post Likes
    Quote Originally Posted by VTP99 View Post
    It's not phase to ground. It's phase to phase I believe the OP was referring to.
    That’s my point..... the unit doesn’t care what voltage you measure from phase to ground. It only cares what the phase to phase voltage is.

  14. #12
    Join Date
    Feb 2011
    Location
    Chicagoland
    Posts
    128
    Post Likes
    With a center tapped 120/240 delta system, the high-leg to ground should be close to 208 as was stated. Check your reading again, maybe with an analog meter to be sure, because that does not read kosher. If it is 240 call the poco.

    And no way, do not, in my opinion, connect any equipment 240, or 208, phase to ground.

    The equipment does see the amps and voltage, but sine waves are different phase to ground vs phase to phase. It could operate, but don't know how happy it would operate.

    Pulling power from only one transformer of the bank could be a problem depending on the loading design.

  15. Likes Zamoramax liked this post.
  16. #13
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    Quote Originally Posted by R123 View Post
    That’s my point..... the unit doesn’t care what voltage you measure from phase to ground. It only cares what the phase to phase voltage is.
    Yes and if you use the high leg for 1 of the phases and 1 of the two lower voltages for the second phase would you not have a imbalance between phases ?

  17. #14
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    2,413
    Post Likes
    Quote Originally Posted by VTP99 View Post
    Yes and if you use the high leg for 1 of the phases and 1 of the two lower voltages for the second phase would you not have a imbalance between phases ?
    The way your wording this isn’t really right. I think you mean “legs” not “phases” as a single phase unit only uses 1 phase which is 1 transformer winding between 2 wires (or legs). As far as imbalance, you really can’t have an imbalance on a single phase unit that the unit sees. Now as far as the set of 3 phase transformers goes, it depends. It depends on the transformer setup, the sizes of the transformers, and whether it’s open or closed delta transformers. If there are 3 equally sized transformers on the poles wired in the closed delta configuration, then it doesn’t matter.

  18. Likes Zamoramax liked this post.
  19. #15
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    Quote Originally Posted by anthonyac1 View Post
    So 3 phase 240 volt has a high leg. 2 of the 3 legs measured to ground measure 120v. While the high leg to ground measures 240v to ground. So let’s say originally the unit was a 3 phase. Some time later some one put in a single phase unit 240v. Yes you have to be sure the wire gauge (awg) is sized for now the higher amp draw. But besides that if you chose one line and the high leg line to line measures 240v. Electrically when applied to a single phase 240v unit can it cause damage? I would guess no because it’s still 240v. But on the other hand I want to say yes because some how electrically its not the same. What is your experience on this?
    R123 here's the original post and this is what I'm referring to.
    Attached Images Attached Images  

  20. #16
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    In a building with the service configuration as you have described, it was common practice to put 120v loads on the A and C phase legs in panels that used blank outs where the B phase leg busbar was located, and only three phase loads could use the high leg in conjunction with the other two legs.

    I would recommend avoiding using the high leg for any purpose without also using the other two legs in a 3-phase configuration for supplying power to the same appliance, so that all three legs have an even load.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  21. #17
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    2,413
    Post Likes
    Quote Originally Posted by VTP99 View Post
    R123 here's the original post and this is what I'm referring to.
    I read the original post and I’m not saying to wire from the high leg to neutral. I’m saying to wire from PHASE TO PHASE.

  22. #18
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    Quote Originally Posted by R123 View Post
    I read the original post and I’m not saying to wire from the high leg to neutral. I’m saying to wire from PHASE TO PHASE.
    Yes, and that would be 240 volts which is outside of most 208/230 rated equipment.
    Attached Images Attached Images  

  23. #19
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Single phase equipment connected to the Delta system in question would have to be listed for 240 volts.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  24. #20
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    2,413
    Post Likes
    Quote Originally Posted by VTP99 View Post
    Yes, and that would be 240 volts which is outside of most 208/230 rated equipment.
    208/230 volt is nominal voltage, not min and max. The voltage utilization range for 208/230 is something like 187-252 volts so 240 volts would be acceptable. If what you said was true, almost all residential equipment wouldn’t work in residences as they almost always have 240 volts single phase service and equipment is 208/230 on the nameplate.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •