+ Reply to Thread
Results 1 to 20 of 25
Thread: gas smell - dont understand
    Oct 2002
    Plano, TX
    Confused by this.
    Have a attic system. The supply vents register high natural gas levels and it smells like it. Likewise, flue has high levels.
    I read zero on the co detector and cannot find NG level anywhere at the burners. I also checked the attic and short return ducting for any gas. None.
    I guess I have a bad heat exchanger, but I would expect a high reading on CO, not NG. Flame looks good.
    Virginia
    Quote Originally Posted by timjimbob View Post
    Confused by this.
    What is the CO level in the flue?
    Is the CO reading Stable?
    Does the CO continue to rise on Shutdown or decrease to zero?
    Do the O2 levels change when the blower comes on?
    Model Number of this unit please.
    Oct 2002
    Plano, TX
    O2 Oxogen??.
    Virginia
    O2 Oxogen??.
    Yes. O2 percentage from a combustion test.
    Oct 2002
    Plano, TX
    "Does the CO continue to rise on Shutdown or decrease to zero?" What is the significance of this question?
    Virginia
    Tells you if the gas valve is leaking after shutdown.
    Oct 2002
    Plano, TX
    Wouldn't I want to check combustion gas level, not CO?
    Virginia
    Doing both would be prudent.
    Cincinnati, Ohio
    How did you measure gas in the flue? What testers are you using?
    captain CO
    Oct 2002
    Plano, TX
    used fieldpeice combustion gas meter a foot from the termination. Real high.
    Cincinnati, Ohio
    Fieldpiece does not make a natural gas leak detector. What is the model #?
    captain CO
    Oct 2002
    Plano, TX
    Infocon Gas-mate and fieldpiece scm4
    Cincinnati, Ohio
    Is the furnace running when you detect gas in the flue? Any chance there is some type of battery charger in the house?
    captain CO
  14. #14
    Oct 2002
    Plano, TX
    Only detects gas when unit if firing. Nothing on "fan only" Vacant house. No painters, or chargers.
  15. #15
    Oct 2002
    Plano, TX
    REplaced system.. had a chance to tear into the furnace and heat exchanger. No rust and all gromets seem tight. I guess I will never know what happened now.
  16. #16
    Jan 2010
    CT
    Mustg be a link Dangerous!
  17. #17
    Cincinnati, Ohio
    Most gas leak detectors are temperature sensitive. They will react to changes in temperature alone.
    captain CO
  18. #18
    Apr 2010
    California
    Never discount the possibility of a dry "P" trap emitting sewer gas. Remember that natural gas is odorless, except for the odorizer that is added to it, and some sewer gas methane can get real close that smell. I have been fooled before....just sayin.
  19. Likes armandomartinez liked this post.
  20. #19
    Oct 2002
    Plano, TX
    Quote Originally Posted by lzenglish View Post
    I always check this out, but I didn't consider on a positive pressure system. It had no trap. Too late know I should have checked.
  21. #20
    Apr 2010
    California
    An Attic Air handler with "NO "P" TRAP"? Gee, that's "ODD".....!!!!And just what is a Residential "Positive Pressure System", as opposed to a "Standard Residential System"? Not trying to throw rocks, just offering up more food for thought. Take Care..