    I am working on a project where we are replacing all equipment with controllers that are BACnet MSTP with the exception of two larger Intellipak AHU's. I need to integrate with these two units via BACnet(MSTP preferred, but IP is ok). The 1U54 interface module is configured for Comm4. What options do I have to make this happen?

    The solutions I have found online are:
    1. Niagara Driver offered from Maxline
    a. Seems pricey for just 2 units
    2. Trane BCI-I modules
    a. Not much online by way of purchase/pricing.

    Any recommendations, solutions, or sourcing of?

    Thanks!
    Attached Images Attached Images  

  2. #2
    Join Date
    Jun 2009
    Location
    StL, MO
    Posts
    730
    Post Likes
    BCI-I is the way to go IF the unit supports it. In other words, not all Intellipacs can be converted to BACnet communications. Give your local Trane rep the serial number and they will tell you if there is a BCI-I kit that is available.
    Older units are more likely to support Lonworks via the LCI-I.