    SightGlass is very thick ,,, (like honey). Anybody have any idea why this would be. Has been like this since I can remember & Operation has never Faulted.
    The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.

  2. #2
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    Are you referring to the compressor oil sightglass and the oil looks like the thickness of honey?

    It could also be just very old oil or the result of magic oil additives administered over the years.

  3. #3
    Join Date
    Apr 2005
    Location
    Australia : Queensland
    Posts
    1,900
    Post Likes
    Thread Starter
    Quote Originally Posted by icemeister View Post
    Are you referring to the compressor oil sightglass and the oil looks like the thickness of honey?

    It could also be just very old oil or the result of magic oil additives administered over the years.
    Sorry ,, I should have elaborated.

    The Liquid Line SightGlass has the appearance of the Liquid inside it is very thick.
    The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.

  4. #4
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    Quote Originally Posted by fridg View Post
    Sorry ,, I should have elaborated.

    The Liquid Line SightGlass has the appearance of the Liquid inside it is very thick.
    OK. That's old enough so it should have flare connections, so why not disconnect the SG and pour out a sample of whatever it is?

  5. #5
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is online now Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,828
    Post Likes
    Large volume oil carry-over would be my first guess.

    How is the oil level in the compressor?

    PHM

    ---------

    Quote Originally Posted by fridg View Post
    SightGlass is very thick ,,, (like honey). Anybody have any idea why this would be. Has been like this since I can remember & Operation has never Faulted.
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  6. #6
    Join Date
    Apr 2005
    Location
    Australia : Queensland
    Posts
    1,900
    Post Likes
    Thread Starter
    Quote Originally Posted by Poodle Head Mikey View Post
    Large volume oil carry-over would be my first guess.

    How is the oil level in the compressor?

    PHM

    ---------
    Full from my View ,,, the oil sight glass is a little discoloured( the glass itself not the oil. But the Liquid in the LLSG isn’t discoloured.
    The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.

  7. #7
    Join Date
    Apr 2005
    Location
    Australia : Queensland
    Posts
    1,900
    Post Likes
    Thread Starter
    Quote Originally Posted by icemeister View Post
    OK. That's old enough so it should have flare connections, so why not disconnect the SG and pour out a sample of whatever it is?
    Would like to but the Client is a Large Mom & Pop Produce Market & would only approve downtime to the Box (6mtrs x 4mtrs) it was deemed necessary.

  8. #8
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is online now Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,828
    Post Likes
    Try draining oil until the crankcase sightglass is about 1/3 to 1/2 filled. Run the compressor and watch the oil level to see if it increases. If it does - remove some more oil.

    Is the liquid line sightless clear? A gin-clear fluid? Because that is what good refrigerant looks like.

    Is it's clear but 'thick' / viscous looking ?

    PHM
    --------


    Quote Originally Posted by fridg View Post
    Full from my View ,,, the oil sight glass is a little discoloured( the glass itself not the oil. But the Liquid in the LLSG isn’t discoloured.
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  9. #9
    Join Date
    Apr 2005
    Location
    Australia : Queensland
    Posts
    1,900
    Post Likes
    Thread Starter
    Quote Originally Posted by Poodle Head Mikey View Post
    Try draining oil until the crankcase sightglass is about 1/3 to 1/2 filled. Run the compressor and watch the oil level to see if it increases. If it does - remove some more oil.

    Is the liquid line sightless clear? A gin-clear fluid? Because that is what good refrigerant looks like.

    Is it's clear but 'thick' / viscous looking ?

    PHM
    --------
    LLSG is not clear(full) but there is no flashing. The Fluid inside is just very slowly rolling around. The colour of the Fluid has a slight tinge of yellow to it.
    The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.

  10. #10
    Join Date
    Apr 2005
    Location
    Australia : Queensland
    Posts
    1,900
    Post Likes
    Thread Starter
    Quote Originally Posted by fridg View Post
    LLSG is not clear(full) but there is no flashing. The Fluid inside is just very slowly rolling around. The colour of the Fluid has a slight tinge of yellow to it.
    I am pretty confident it is just oil trapped in it ,but I have never seen a Liquid Line Sight Glass to be so lazy when only 3/4 Full.
    The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.

  11. #11
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    Quote Originally Posted by fridg View Post
    I am pretty confident it is just oil trapped in it ,but I have never seen a Liquid Line Sight Glass to be so lazy when only 3/4 Full.
    That's what we call river flow in the sightglass and i will occur when the refrigerant flow is low compared to the full flow capacity of the SG, even when the liquid is subcooled. The yellowish color is probably from the yellow mineral oil in the compressor, which was common back in the day.

  12. Likes fridg liked this post.
  13. #12
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is online now Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,828
    Post Likes
    Perhaps it is a job which was piped back in the old days when things were done properly and the correct refrigerant velocities are just less than you are accustomed to seeing. <g>

    BTW: why is the LL sightglass only 3/4 full ?

    PHM
    -------


    Quote Originally Posted by fridg View Post
    I am pretty confident it is just oil trapped in it ,but I have never seen a Liquid Line Sight Glass to be so lazy when only 3/4 Full.
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  14. Likes fridg liked this post.
  15. #13
    Join Date
    Apr 2005
    Location
    Australia : Queensland
    Posts
    1,900
    Post Likes
    Thread Starter
    Quote Originally Posted by Poodle Head Mikey View Post
    Perhaps it is a job which was piped back in the old days when things were done properly and the correct refrigerant velocities are just less than you are accustomed to seeing. <g>

    BTW: why is the LL sightglass only 3/4 full ?

    PHM
    -------
    You could be right. It was piped up more than 30years ago & no insulation on any of the PipeWork , it has Copper Saddles securing it.

    SightGlass has never been completely full & we have been doing PM’s here for well over 5 years. I conduct periodic Leak Testing OnSite & have never found a leak on the Sytem ,,, repairs have been few & far between & only Evaporator Fans have failed that I can recall.

    System seems happy & maintains Temps well & doesn’t have an extended Run Time to reach Temp & Off Cycle seems normal also.
    The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.

  16. #14
    Join Date
    Aug 2010
    Location
    Dearborn MI
    Posts
    511
    Post Likes
    Is this actually a working Kelvinator commercial belt driven compressor? If so take good care of it because you are actually preserving HISTORY! Do you have alot of the old belt driven style compressors such as Copeland, Curtis, Baker, General Electric, Brunner, Frigidaire, Mills, Par, Tecumseh (Universal) or Lehigh in your part of the world It would be so cool to see some of those compressors still operating (plus I could get rid of some of my obsolete compressor parts inventory!).

  17. Likes icemeister liked this post.
  18. #15
    Join Date
    Apr 2005
    Location
    Australia : Queensland
    Posts
    1,900
    Post Likes
    Thread Starter
    Working & is the original Unit installed with the box. Only changed the belts once in 5years & no other issues for this same period. It seems happy , that’s why I’m reluctant to upset it too much.

    We do have a few Open Drives here but the further West you go (out in the Bush) there are considerably more.

    I’m in Australia , cost of Freight would be a killer from the US.
    The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.

  19. #16
    Join Date
    Mar 2021
    Posts
    111
    Post Likes
    Quote Originally Posted by fridg View Post
    I am pretty confident it is just oil trapped in it ,but I have never seen a Liquid Line Sight Glass to be so lazy when only 3/4 Full.
    Old manufacturers had a few tricks when making old school LLSG, tricks that have been lost over the years, so what brand is it?

  20. #17
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is online now Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,828
    Post Likes
    What were the sight glass tricks?

    PHM
    -------


    Quote Originally Posted by MadeInAustralia View Post
    Old manufacturers had a few tricks when making old school LLSG, tricks that have been lost over the years, so what brand is it?
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  21. #18
    Join Date
    Mar 2021
    Posts
    111
    Post Likes
    Quote Originally Posted by Poodle Head Mikey View Post
    What were the sight glass tricks?

    PHM
    -------
    They were machined so gas pockets could not form in the top of the LLSG.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •