    Hi, thank you for all the help wanted to ask you about the gas furnace it was built 1972 is 125,000 BTU we want to replace that also what size would be need?

  2. #22
    Join Date
    Nov 2016
    Posts
    31
    Post Likes
    Thread Starter
    we are looking at 80% and 95% 96%

  3. #23
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,334
    Post Likes

    FURNACE SIZING, SELECTION, OPERATING COST

    Quote Originally Posted by QC91 View Post
    Hi, thank you for all the help wanted to ask you about the gas furnace it was built 1972 is 125,000 BTU
    we want to replace that also what size would be need?
    42,200 BTU/HR Heat Loss at 35'F

    SELECTION: 60,000 BTU/HR at 90%
    ... BLOWER MUST BE CHECKED AS SUFFICIENT FOR THE SELECTED CONDENSER & COIL SIZE

    ESTIMATE : $864 per year [ 2,100 HDD ] based on $1.28 / therm Natural Gas

    ATTACHMENTS
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  4. #24
    Join Date
    Nov 2016
    Posts
    31
    Post Likes
    Thread Starter
    Thank you for all the help

Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •