Ok, I had a customer who has a Friedrich MR24DY3F outdoor with two indoors that came with the system. She had an issue with the system so I went to check it out. I found that the outdoor board was showing a 53vdc steady. It should bunch between 60-130vdc. I disconnected the wire at the outdoor going to the indoors and there it was between 60-130vdc as should be. Spoke with Friedrich and found the controller board was bad. I was told that they no longer make the board and the entire system needed to be replace due to the indoors won't communicate to a different outdoor as the one that is there. To the customers luck I was able to locate the exact same outdoor unit at the supply house that they had saving them having to replace the entire system which is only 6 years old. I even double check with Friedrich which they told me if it is the same outdoor unit I will be fine. I installed the unit and now I have a communication error. I check wiring all was good. I did my communication check and I get 60-130vdc at the outdoor going to the indoor now and I have the same at the wire I disconnected from the indoor showing the communication is coming back. But I still have the error. What could it be. I'm at a lost and friedrich is closed on the weekends. Please help!
Thank you
Thank you