+ Reply to Thread
Results 1 to 6 of 6

Thread: Rheostat and hard start kits.

  1. #1
    Join Date
    Jul 2016
    Posts
    1
    Post Likes

    Rheostat and hard start kits.

    Hello!

    I'm new to the site and hope I got the right location to ask a question.I've read many positive articles about "hard start kits" for A/C compressors . I'm not versed in electric theory of what happens during compressor start-up, but may I ask if the start kit operates similar to a DC motor rheostat?

    I remember having to start large DC motors in industry using multiple hand activated levers that had to be pushed down and clicked in place before going to the next lever.There were 4-5 levers and when the first lever is depressed,the motor starts to turn very slowly and as each lever is depressed (at the control box) the motor increases speed.It is done gradually and slowly .So, I likened it to a hard start kit.Am I right? Or out of touch!!
    Thanks

  2. #2
    Join Date
    Jun 2013
    Location
    N. Canada
    Posts
    878
    Post Likes
    No, an ac "hard start kit" is a correctly sized start capacitor paralled across the compressor's run capacitor via a nc relay.

    This relay is opened when a specific v is built up in the compressor.

  3. #3
    Join Date
    Jan 2021
    Posts
    14
    Post Likes
    These are spiff items at my company. I never installed one yet because I'm still figuring out when it would be practical to put one in. I was thinking of just sending it on any outdoor unit over five years old but what would be some good indicators that the compressor could use one?

  4. #4
    Join Date
    Jan 2020
    Location
    Winnipeg Canada
    Posts
    2,507
    Post Likes
    Quote Originally Posted by JehanDM View Post
    These are spiff items at my company. I never installed one yet because I'm still figuring out when it would be practical to put one in. I was thinking of just sending it on any outdoor unit over five years old but what would be some good indicators that the compressor could use one?
    Generally speaking you'd install one on a compressor that doesn't want to start easily.
    I've only installed a few, but those were on unit's that would trip the breaker when trying to start. Or they would start slow with an ungodly groaning noise for a few seconds.
    All it really is is adding a start capacitor and relay.

  5. #5
    Join Date
    Apr 2010
    Location
    ... sitting in the Hollywood Hawaiian Hotel, listening to the air conditioner hum
    Posts
    1,208
    Post Likes
    Quote Originally Posted by JehanDM View Post
    These are spiff items at my company. I never installed one yet because I'm still figuring out when it would be practical to put one in. I was thinking of just sending it on any outdoor unit over five years old but what would be some good indicators that the compressor could use one?
    Its been awhile since I've dealt with single phase power, but when I was doing residential, the only times I ever found a hard start kit to be truly necessary was due to a particular mix of equipment that I used to run into a lot, albeit about 10 years ago. I never suggested one "just because."

    When replacing Carrier cased evap coils, if they were keeping the old condenser. This was the old units, the ACA coils with the piston, on the the 38CK condensers that had recip compressors. When we changed the coils to the ATAs or ALAs, those have hard shut-off TXVs, and often, those compressors didnt like that, so they got a HS kit as well.

    I would assume that this particular problem is not much of a thing anymore. Rest of the times were just a handful of times where you give the customer that line about how the compressor was locked up and you ran it backwards and it's now working but they really should replace it, but I suggest this hard start kit in the meantime while you plan for a new unit and you never hear from them again.

    The great professors of the art are not immune from the malignancy of matter and the eternal cussedness of inanimate objects.

  6. #6
    Join Date
    Jan 2021
    Posts
    14
    Post Likes
    Another dumbass question? How do you run a compressor backwards? They turned me into an IAQ / turnover guy because I can sell, but it seems like I'm going to have to fend for myself on the technical side. The ones we use don't need a relay we just hook it up to the capacitor on the herm terminal.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •