    Have you ecer experienced a motor do this?

    I helped a coworker wire an indoor blower motor for a fan coil unit. When operating in the CCW position it over amps pulling 20 amps when it rated for about 8. It's a marathon 1/2 HP, 120vac. The internal overload is opening. It will ramp up and then down a couple of times then the overload that's it out. It will run all day as long as a load isn't put on it. It will operate in the CW position with the blower wheel not moving any air cause it's spinning the wrong direction all day. Just wondered if anyone else has experienced this with a new motor.

  2. #2
    Join Date
    Apr 2016
    Location
    Parts unknown
    Posts
    130
    Post Likes
    If you have 120V to motor, it's wired properly and cap is within spec it's a bad motor.
    I would double check everything, including motor spec before condemning it.

    You say ramp up and down but it doesn't sound like an ECM. No such thing as ramp up and down if it's not

  3. #3
    Join Date
    Aug 2009
    Location
    Huntsville, Alabama.
    Posts
    2,642
    Post Likes
    Thread Starter
    Yeah I know it's bad.

  4. #4
    Join Date
    Apr 2016
    Location
    Parts unknown
    Posts
    130
    Post Likes
    So you wanted to know if anyone's gotten a bad motor out of the box before. Ok

  5. #5
    Join Date
    Aug 2009
    Location
    Huntsville, Alabama.
    Posts
    2,642
    Post Likes
    Thread Starter
    No that's not I wanted to know. I ask to see if anyone has experienced a motor displaying a similar symptom, I assumed this was an area professionals only commented.

  6. Likes RezAtDorsia liked this post.
  7. #6
    Join Date
    Apr 2016
    Location
    Parts unknown
    Posts
    130
    Post Likes
    Peace and love brother, peace and love!

  8. #7
    Join Date
    Aug 2010
    Location
    Living rent free
    Posts
    6,570
    Post Likes
    Quote Originally Posted by Ricky Dale View Post
    No that's not I wanted to know. I ask to see if anyone has experienced a motor displaying a similar symptom, I assumed this was an area professionals only commented.
    Lol..right.
    "If you can’t describe what you are doing as a process, you don’t know what you are doing." ~ W. Edwards Deming

    All those who wander..are not lost.

    Do NOT..mistake my kindness for weakness.

    The early bird may get the worm..but the second mouse gets the cheese.

  9. #8
    Join Date
    Oct 2012
    Location
    Wisconsin
    Posts
    6,676
    Post Likes
    Do you have the blower panel/door open while you're checking amp draw?

  10. #9
    Join Date
    Feb 2013
    Location
    In a house with windows and doors on it.
    Posts
    282
    Post Likes
    More info needed what kind of system, motor application?

    Sent from my SM-G900V using Tapatalk

  11. #10
    Join Date
    Aug 2009
    Location
    Huntsville, Alabama.
    Posts
    2,642
    Post Likes
    Thread Starter
    No sir door is on and the unit is under normal operating conditions. the excessive amp draw is immediate. it's an indoor fan motor in a 4 pipe fan coil unit. The motor is bad out of the box just wondered if anyone has gotten one that did this. Bad internal overload, built incorrectly.

  12. #11
    Join Date
    Apr 2003
    Location
    Maple Grove, MN
    Posts
    3,907
    Post Likes
    Every once in a while those little Chinese factory workers like to play funny little pranks like this on us dumb Americans. Ha, ha, looks like they got us again. Well played little Chinese dudes!

  13. Likes lions_lair, knave liked this post.
  14. #12
    Join Date
    Apr 2016
    Location
    Indianapolis, In
    Posts
    73
    Post Likes
    Just found out issues with a 20 hp return fan that couldn't ramp up over 35%. Manufacturer put wrong rpm motor on the fan from the factory. Right HP, right make, just wrong rpm.
    Amperage way over at 100% speed. But I agree anything coming from China makes me suspect.

  15. #13
    Join Date
    Apr 2016
    Location
    Parts unknown
    Posts
    130
    Post Likes
    Sounds like the internal overload is fine...
    The construction of any electric motor stator is very precise, if there is a slight short between windings, between turns even, it will throw the entire thing off. Even if it ohms out ok, the defect may not occur until it is put under the thermal stress of actually running or running under a load.

    Don't forget that motors are dynamic and can behave differently in operation than what may be expected from meter testing. Not by design but because of defects. This happens with grounds too.

  16. #14
    Join Date
    Oct 2012
    Location
    Wisconsin
    Posts
    6,676
    Post Likes
    Quote Originally Posted by Ricky Dale View Post
    No sir door is on and the unit is under normal operating conditions. the excessive amp draw is immediate. it's an indoor fan motor in a 4 pipe fan coil unit. The motor is bad out of the box just wondered if anyone has gotten one that did this. Bad internal overload, built incorrectly.
    I had a trane condenser fan motor that way.

    Put a brand new motor in and it would just sit there and hum. It was getting the full 460 Volts and the run capacitor was good.

    Got another new motor and put it in and it was good.

  17. #15
    Join Date
    Aug 2009
    Location
    Huntsville, Alabama.
    Posts
    2,642
    Post Likes
    Thread Starter
    No the internal overload isn't find that's what is opening to stop the motor before it cooks it's self. It's was wired incorrectly when it was built. Every now and then we get one that does crazy things cause it was screwed up on the assembly line.

  18. #16
    Join Date
    Apr 2016
    Location
    Parts unknown
    Posts
    130
    Post Likes
    Quote Originally Posted by Ricky Dale View Post
    No the internal overload isn't find that's what is opening to stop the motor before it cooks it's self. It's was wired incorrectly when it was built. Every now and then we get one that does crazy things cause it was screwed up on the assembly line.
    Nothing in your story has anything to do with the overload except that it is doing its job opening when the motor gets too hot.
    If that is what you're saying, I don't know how you think you can tell the symptoms are caused by an incorrectly "wired" overload. They are generally imbedded in the windings itself. Not many ways you can wire that incorrectly.
    If you mean the motor was wired incorrectly, the overload is working by opening!

    Don't mean to harp on this but saying an overload is bad because it's working is a lack of understanding of its function and is why people change parts unnneccessarily (not this case, of course):
    "Overload is open. Motor must be bad"
    Change motor
    "Same thing. Oh... The fan contractor was bad, single phasing the motor"
    Think further than the symptom!
    (Once again, not referring to OP, just the mentality of parts changers in general)

  19. #17
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    30,556
    Post Likes
    If the motor / blower was windmilling backwards when not powered up, you might see that extra high amp draw on a perfectly good motor trying to start against all of that extra load.

  20. #18
    Join Date
    Apr 2016
    Location
    Parts unknown
    Posts
    130
    Post Likes
    *Some overloads are snap-action discs mounted externally (but not serviceable)

  21. #19
    Join Date
    Apr 2016
    Location
    Parts unknown
    Posts
    130
    Post Likes
    Quote Originally Posted by BBeerme View Post
    If the motor / blower was windmilling backwards when not powered up, you might see that extra high amp draw on a perfectly good motor trying to start against all of that extra load.
    True...
    causes problems (over-amp and over-voltage alarms/faults) and necessitates extra programming changes for VFDs also (just FYI).

  22. #20
    Join Date
    Aug 2009
    Location
    Huntsville, Alabama.
    Posts
    2,642
    Post Likes
    Thread Starter
    It wasn't wind milling backwards at any time. It would not operate with a load on it CW or CCW without tripping the 'internal" overload. A weak/bad or improperly overload when the 12 year old child labor kids made it. Thanks for you all's insight.