Thread: Low suction, normal head pressures. Confused.

  1. #1
    Join Date
    Feb 2013
    Location
    Metro Atlanta
    Posts
    291
    Post Likes

    Low suction, normal head pressures. Confused.

    Hi all (yall)

    I was doing a PM for a customer and when taking the refrigerant readings, I have come to a complete brain fart as to why the system was doing this.

    Readings:

    Indoor temp: 70 F
    Outdoor temp: 68 F
    Suction Pressure: 65 PSIG (roughly 10 degrees)
    Discharge Pressure: 205 PSIG (roughly 72 degrees)
    Suction temp: 61 F
    Discharge temp: 64
    Superheat: 51 F
    Subcool: 8 F

    Trane R410A system has a design subcool of 10 +/- 3 degrees so my subcooling is within the threshold.

    I did not see a filter drier on either the suction or discharge lines to take a temperature drop across to see if there is more than a 2 degree difference aka change that out. I was going to say something along the lines of a restriction after the TXV within the cap tubes that is starving the evap coil giving me a low suction/very high superheat.

    Since my job at this moment is to keep a unit running and make sure that happens through the most basic of ways (contactor changes, new dual run cap or start, etc) I have to call into dispatch and turn the PM into a service call.

    So, with that said, anyone want to give their 2 cents as to what the problem might be? I want to know just in case I come across this again.

    Thanks,

    Michael

  2. #2
    Join Date
    Jul 2006
    Location
    Prata di Pordenone Italy
    Posts
    8,069
    Post Likes
    I would say a combination of low charge and restricted metering device.
    on tranes the drier is inside the unit

  3. #3
    Join Date
    Jul 2013
    Location
    Richmond, VA
    Posts
    6,027
    Post Likes
    With such high superheat and normal subcooling, I would be willing to bet that TXV is malfunctioning and it's undercharged by 1-2 pounds. Sensing bulb could be low on charge or something fouled up the needle. Fortunately, that's probably a bolt on TXV so it's real easy to change out.

  4. Likes ksefan liked this post.
  5. #4
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    The SC might be normal , but the normal head for a r410 system w/ a 68* ambient should be closer to 300psi and the normal suction press should be closer to 110psi w/70* IDB. Those p/t's sound more like r22.

  6. Likes kdean1, buttwheat liked this post.
  7. #5
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    22,115
    Post Likes
    As others have said it sounds like a TXV and maybe low on juice. Check the serial number, it may need the snake oil to clean the goo out of the TXV.

  8. #6
    Join Date
    Feb 2013
    Location
    Metro Atlanta
    Posts
    291
    Post Likes
    Thread Starter
    But if the system was low on refrigerant wouldn't that show a low head pressure and suction as well? Right off the bat I would have a high superheat and low subcooling, no?

    By seeing that it had 8 degrees subcooling would mean that the condenser has the refrigerant it needs to operate at design subcool specs with the threshold of +/- 3 degrees. Unless I'm not reading the data plate right isn't that what it means?

    I don't want to sound like I know the game and that I'm better because I'm not but looking back on what I learned in school as a reference seems to conflict. Then again theory and reality are opposites most of the time.

    The serial started with a 14 and I remember something trane made that did in fact clog up the TXV and yes some oil had to be put in to dissolve it. Our company has been going around and applying the oil to those with such serial numbers that were infected.

  9. #7
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    22,115
    Post Likes
    Quote Originally Posted by pmck94 View Post
    But if the system was low on refrigerant wouldn't that show a low head pressure and suction as well? Right off the bat I would have a high superheat and low subcooling, no?

    By seeing that it had 8 degrees subcooling would mean that the condenser has the refrigerant it needs to operate at design subcool specs with the threshold of +/- 3 degrees. Unless I'm not reading the data plate right isn't that what it means?

    I don't want to sound like I know the game and that I'm better because I'm not but looking back on what I learned in school as a reference seems to conflict. Then again theory and reality are opposites most of the time.

    The serial started with a 14 and I remember something trane made that did in fact clog up the TXV and yes some oil had to be put in to dissolve it. Our company has been going around and applying the oil to those with such serial numbers that were infected.
    You are showing low head.

    Look at it this way. If everything is working properly you would have 8°-12° SC and 10°-20° SH.

    So lets look at just the SH side first. What causes high SH, low on charge or a restriction. 8° SC would discount the low on refrigerant right. That leaves a restriction.

    If you have a correct charge and a restriction you would have higher SC right. Since you have normal SC and a restriction you must be short on charge.

    Does this explain better or is there other info I should consider?

  10. #8
    Join Date
    Jul 2013
    Location
    Richmond, VA
    Posts
    6,027
    Post Likes
    With a normally operating TXV on an undercharged system, you'll find that SH may be normal with some subcooling. Not until you reach 0-3 degrees SC will your SH start to increase.

    See, as the system loses refrigerant, the TXV will open more and more to keep the SH normal (10 degrees), so there's always a column of liquid before the TXV. When it's fully open and still not enough refrigerant is in the evaporator, then your SH starts to rise.

    In your case, you have an almost normal column of liquid behind the TXV, but it's closing down way more than necessary. There's no reason to have 50 degrees SH if you have 8 degrees SC other than a restriction (TXV being the restriction). It's also undercharged because if it were charged fully, your SC would be well above normal (15-30 degrees).

    Sent from my XT1080 using Tapatalk

  11. #9
    Join Date
    Jul 2010
    Location
    nebraska
    Posts
    2,810
    Post Likes
    Only ways your liquid line can be colder than the ambient is if there's a restricting before the pressure port or the condensing coil is wet.

  12. #10
    Join Date
    Feb 2007
    Location
    Fremont, Indiana
    Posts
    3,275
    Post Likes
    Quote Originally Posted by martyinlincoln View Post
    Only ways your liquid line can be colder than the ambient is if there's a restricting before the pressure port or the condensing coil is wet.
    But it's not!
    68 deg ambient/liquid line saturation 71.4 deg........ close, but not....

    Quote Originally Posted by CircusEnvy View Post
    With a normally operating TXV on an undercharged system, you'll find that SH may be normal with some subcooling. Not until you reach 0-3 degrees SC will your SH start to increase.

    See, as the system loses refrigerant, the TXV will open more and more to keep the SH normal (10 degrees), so there's always a column of liquid before the TXV. When it's fully open and still not enough refrigerant is in the evaporator, then your SH starts to rise.

    In your case, you have an almost normal column of liquid behind the TXV, but it's closing down way more than necessary. There's no reason to have 50 degrees SH if you have 8 degrees SC other than a restriction (TXV being the restriction). It's also undercharged because if it were charged fully, your SC would be well above normal (15-30 degrees).

    Sent from my XT1080 using Tapatalk
    To the op, correct answer was given above with txv malfunction on top of low charge!
    Member of the "Work Exchange Program"
    "Will work for knowledge"

    "Everyone is a genius. But if you judge a fish on its ability to climb a tree, it will live its whole life believing that it is stupid"
    A Einstein

  13. #11
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,021
    Post Likes
    Bad TXV. Not necessarily low on charge. Many times I've had normal subcooling and a ll restriction. The subcooling skyrockets when some knucklehead jams a bunch of refrigerant in it to get the suction pressure above freezing.

    If it's a copeland compressor from 2014 I can almost guarantee the TXV needs some of the magic miracle additive ac renew

  14. #12
    Join Date
    Feb 2013
    Location
    Metro Atlanta
    Posts
    291
    Post Likes
    Thread Starter
    Bad TXV I get but someone please tell more about a low charge on top of that?

  15. #13
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,021
    Post Likes
    I don't think it's low on charge

  16. #14
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    How can the SC be perfect and be used as a "cornerstone" for a good running system when the lo side is lo and the hi side is also lo?

    A good running system has a good suction press, a good hi side press, a good SH and a good SC.

  17. Likes kamersoutdoor liked this post.
  18. #15
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes
    At start up you'll likely have high head for a while until you get a large column of liquid built up. With a real good restriction you are cooling more than you are pumping and the pressures get close to ambient saturation points when the start to happen subcooling goes down..... Much like checking subcooling in say fifty or below outdoor temps. You would think it would subcool real good yet remains around 4 or 5 degrees

    Sent from my XT1080 using Tapatalk

  19. #16
    Join Date
    Feb 2007
    Location
    Fremont, Indiana
    Posts
    3,275
    Post Likes
    Correct me if I'm wrong, but if I close my txv(restrict), subcool increases (as in refrigeration, close your valve and sight glass clears)
    Member of the "Work Exchange Program"
    "Will work for knowledge"

    "Everyone is a genius. But if you judge a fish on its ability to climb a tree, it will live its whole life believing that it is stupid"
    A Einstein

  20. #17
    Join Date
    Feb 2007
    Location
    Fremont, Indiana
    Posts
    3,275
    Post Likes
    Or high subcool with restricted captube.
    Restriction causes liquid to stack in condenser, so if txv is restricted, he would have higher subcooling than under normal operation....... thus low charge
    Member of the "Work Exchange Program"
    "Will work for knowledge"

    "Everyone is a genius. But if you judge a fish on its ability to climb a tree, it will live its whole life believing that it is stupid"
    A Einstein

  21. #18
    Join Date
    Jul 2010
    Location
    nebraska
    Posts
    2,810
    Post Likes
    Quote Originally Posted by kamersoutdoor View Post
    But it's not!
    68 deg ambient/liquid line saturation 71.4 deg........ close, but not....

    68 ambient with a 64 degree liquid line is what he posted. The liquid line can not be cooler than ambient with a dry coil. He's flashing liquid before the service valve.

  22. Likes kamersoutdoor liked this post.
  23. #19
    Join Date
    Feb 2013
    Location
    Metro Atlanta
    Posts
    291
    Post Likes
    Thread Starter
    Okay, so with what you guys are saying is making sense. The more I think about the clearer it becomes. But I am still lost. I feel like I need a refresher course with refrigeration..

  24. #20
    Join Date
    Feb 2013
    Location
    Metro Atlanta
    Posts
    291
    Post Likes
    Thread Starter
    I just looked back on my notes,

    Low side pressure: 65 PSI (10*F)
    High side pressure: 210 PSI (72*F)
    Liquid line temp: 64*F
    Suction line temp: 61*F
    Superheat: 51*
    Subcooling: 8*
    Outdoor ambient: 60*F
    Indoor ambient: 70*F

    Trane R410a system

    Model: 4TTR3036E1000AA
    Serial: 1410386J3F

    Have at it

+ Reply to Thread
Page 1 of 3 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •