    Frequency Transducer.

    They are putting in a new control system, and the bean counters cut new Frequency drives out of the contract. Three of the drives have no feed back point. Is there a Transducer I could install? Is a Sine Wave or Square wave needed?? Output Signal needs to be 4 to 20 mA Also trying to figure out the frequency range.

  2. #2
    Join Date
    Dec 2006
    Location
    What? Who? Where?
    Posts
    2,634
    Post Likes
    Why not just use a VFD rated current transducer and read amps?

    kontrol out
    "Good" - Jocko
    "Open is as open does." - Forrest Gump
    "Can't we all just get a Lon?" - Garry Jack
    "BACnet: integration or interrogation?" - The Janitor
    "Interoperability? You can't handle interoperability!" - Nathan R. Jessup
    “What’s that? Aaa… open protocols? Don’t talk about…. open protocols? Are you kidding me? Open protocols? I just hope we can hardwire an interface!” - Jim Mora Watch it here!

  3. #3
    Join Date
    Aug 2006
    Posts
    3,691
    Post Likes
    Thread Starter
    Control company, would have to install a different program and charge us for it. That would take an RI, doubt I'd get one of them. I looked at some on the Internet, not sure how I would shield them from the line side.

  4. #4
    Join Date
    May 2009
    Location
    SC
    Posts
    4,049
    Post Likes
    This might be misunderstood, they might not need the speed feedback (analog) but will need proof that it is running (digital). Get clarification on that, might just need a DP switch.

  5. #5
    Join Date
    Aug 2006
    Posts
    3,691
    Post Likes
    Thread Starter
    I just Emailed them back and said I no cure for the Frequency drives being cut out of the specs. The old ones are Square D and at least 15 years old. The computer shuts the AHU down if it doesn't get a feed back within so many minutes and goes into alarm.

  6. #6
    Join Date
    Apr 2014
    Location
    MN
    Posts
    436
    Post Likes
    What do you mean by "the computer shuts the AHU down"? Do you mean the controller for the AHU, or is there something else in play here?
    Do you have the ability to reprogram the AHU controller? It doesn't sound like you do, so I'm not sure how you'd be able to generate an analog output signal to act as an input to a controller.
    Maybe an floating to analog output generator with a relay? When the fan is running a CT could close a relay that would apply 24VAC to the "increase contact" on the AUD (ACI Product), and when it's off the 24VAC would be applied to the "decrease contact". When it's increasing the analog output of the AUD would go up to whatever voltage or mA signal indicates it's running, and the opposite when it's off.

  7. #7
    Join Date
    Aug 2006
    Posts
    3,691
    Post Likes
    Thread Starter
    If the unit goes into alarm it shuts down the equipment after X number of minutes. Not sure what they are programing the time at. I can run the temperature up and down, lock controls, for an amount of time. But other than that I can't touch anything on this new system they are putting in. BTW we almost froze a building last winter, due to the pumps being programmed like this.

  8. #8
    Join Date
    Jan 2003
    Location
    USA
    Posts
    9,437
    Post Likes
    Quote Originally Posted by madhat View Post
    BTW we almost froze a building last winter, due to the pumps being programmed like this.
    Some guys I worked with over the years swear by doing this. Argument is if the system runs out of water it could save the pumps. Seen to many times where MC may service them and fail to call anyone to reset, there they sit locked out. Freezing a building is far more a concern to me than the off chance a system runs flat and the pumps burn up. Not too often I have seen that happen. Crap freezing on the other hand...
    Propagating the formula. http://www.noagendashow.com/

  9. #9
    Join Date
    Apr 2016
    Location
    Parts unknown
    Posts
    130
    Post Likes
    Strange that a lack on analog feedback would act like a safety and shut stuff down. I would think that would be something associated with a DI from a current clamp switch.
    Seems easy enough. Whichever it is...
    AI: current transducer (like Kontrol said)
    DI: current sensor switch. Or the drive may have digital outputs or dry contacts (DO more likely)
    Or, the response of the control system to lack of AI/DI feedback could be changed

  10. #10
    Join Date
    Aug 2006
    Posts
    3,691
    Post Likes
    Thread Starter
    I'm getting tired of writing specs, sometimes on my own time, then the bean counters say we negotiated the contract and saved money. They didn't do any bartering, just cut stuff out of the contract. The drives are over 12 years old, two are dangerous to work on, they put ABB inside Econo-flex cabinets, and kept the disconnects. This was temporary two year ago, now its permanent. Let them deal with it. BTW I found the Frequency Transducers, I'd have to put two on each drive, locate them outside the drive. Then there's the box to put them in, conduit, and whether this has to be fused.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •