Results 1 to 20 of 48
Thread: Humidity Problem with Daiken Ductless MiniSplit
    Aug 2015
    We had a Daiken ductless mini-split system installed in May (2 ton Daikin mini split heat pump system with (2) 7,000 Btu wall mount heads, and (1) 12,000 Btu wall mount head). The system seemed to work well at first, but the longer we ran it continuously, the higher the humidity rose in our home. We contacted the installer and he ran some data logging to determine the humidity levels. Despite them climbing above 70%, he says these are standard levels and the unit is working as expected. Does anyone have any experience with this problem and/or suggest some solutions? Thank you in advance!
    SW Wisconsin
    Humidity should go down, not up, during longer it runs; there is a problem...
    Also, depending on sensible temps 55% & lower is standard; never 70%.
    Ohio
    Are the units maintaining temperature?
    I need a new signature.....
    Aug 2015
    Quote Originally Posted by I_bend_metal View Post
    Yes, they seem to maintain temperature. In fact, if the temp is high and they run in cooling mode, the humidity is fine, it's only when there is no cooling load necessary and the fan is running. This happens mostly overnight when the outside temps drop.
    Aug 2015
    Quote Originally Posted by udarrell View Post
    That is what I assumed, because when it hit 70% you could certainly tell by the quality of air and room comfort. Do you have any suggestions as to how to deal with it?
    Madison, WI/Cape Coral, FL
    Fan "on" will make the %RH higher because of the evaporation of the moisture on the coil at the end of cycle. Fan "auto" should help.
    During low/no cooling loads and high outdoor dew points expect plus the moisture from the occupants expect high indoor %RH. Adding small whole dehumidifier like the Ultra-Aire wll provide low %RH without cooling.
    Regards Teddy Bear
    Most minis you don't have a choice, fan is on low all the time when not running. Are these inverter?
    Southold, NY
    Fan should be in AUTO and will ramp down to extreme low when compressor is off.
    X-2 on Inverter?
    Southold, NY
    Are the penetrations in the wall properly sealed?
    Fan shuts off? OK, I'm not familiar with Daikin units.
    Aug 2015
    Apparently, on the units we have (as with most mini-splits) there is no way to turn off the fan. Some quick research shows that Daikin makes models where there fan has a switch for on/auto.
    Aug 2015
    Both the installer and the product rep came out to make sure they were properly installed, so I would have to say yes according to them.
    Aug 2015
    X-2 on Inverter?
    The fan might ramp down, but it never shuts off. Not sure what X-2 on Inverter means, I can provide model details if that would help.
  14. #14
    Aug 2015
    Yes, it looks like they utilize an inverter type compressor
  15. #15
    Aug 2015
    Quote Originally Posted by teddy bear View Post
    Regards Teddy Bear
    Unfortunately, I don't have a fan auto mode. Are you suggesting a whole house humidifier?
  16. #16
    Southold, NY
    Please post the model of the indoor and outdoor units
  17. #17
    Southold, NY
    Aug 2015
    Unfortunately, that is not the remote I have. It most likely is a higher end model of the Daikin brand.
  19. #19
    Quote Originally Posted by Hammer09 View Post
    I am suggesting setting up the cooling to provide a <50^F dew point supply air to the home. During long cooling runs, you will have 50%RH. During low/no cooling loads, you will need a small whole house dehumidifier to maintain <%RH.
    Make sense?
    Regards Teddy Bear
  20. #20
    Jun 2001
    Louisville, KY
    Drop the continuous fan speeds to ultra low setting. It's done with the remote. Can also use the dry mode at night.
Tags for this Thread