We don't normally double filter paths to the return air chamber as it can cause too much pressure drop in the system.
An ACCA manual D ought to be performed to see if there is enough Available Static Pressure (ASP) remaining for proper performance.
If the blower calls for .5" of static pressure & a simple static pressure shows it is much higher; then steps need to be taken to correct the problem.
I understand your desire to keep the ducts reasonably clean, especially with pets in the house.
The installer may be right; however, I would do some testing to verify if it is a workable situation.
Determine if leaving filters in the two highest dust generating rooms imbalances the airflow delivery too much.
You need to realize that those room returns have a pressure drop for the filter plus the grille; therefore those areas need to be large enough to result in a low 300-fpm velocity or lower through the grille & filter. That calls for oversized areas as compared to what usually exists for the required airflow of each room; if those filter grilles were sized just for the return area of the individual room they probably won't be big enough.
Looking at the sizing it looks like they were sized for the entire return air; I won't take time to try to figure it because I don't know the requirements of the rooms, etc.