    Compressor does have run cap

    Came accross a very old Singer comfortmaker AC yesterday. Everything was butchered on this.

    Found wire connection on comp cap burnt off. Could not find matching burnt wire, The more I studied this, there is no run cap in this circuit, only a hard start kit........and it runs and starts fine.

    Verified, no amp draw through only wire to cap or start terminal at compressor. Draws about 23amp on line 1. Cannot verify compressor info, no name plate is removed.

  2. #2
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    Quote Originally Posted by timjimbob View Post
    Came accross a very old Singer comfortmaker AC yesterday. Everything was butchered on this.

    Found wire connection on comp cap burnt off. Could not find matching burnt wire, The more I studied this, there is no run cap in this circuit, only a hard start kit........and it runs and starts fine.

    Verified, no amp draw through only wire to cap or start terminal at compressor. Draws about 23amp on line 1. Cannot verify compressor info, no name plate is removed.
    It'll run but the amp draw will be too high. They're getting maybe 4 SEER out of it.

  3. #3
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,568
    Post Likes
    Thread Starter
    Amazing that it restarts pretty easily.

  4. #4
    Join Date
    Jun 2003
    Location
    Chicago, IL
    Posts
    6,067
    Post Likes
    If it has a start kit it will start. It won't run very efficiently though. Throw a 35 cap on there, it will be better than nothing. If you really want to get the right cap, try a bunch of different ones and use the one that gives the lowest amp draw on C of the compressor.

  5. #5
    Join Date
    Jun 2014
    Location
    Anderson County, SC
    Posts
    145
    Post Likes
    Quote Originally Posted by craig1 View Post
    If it has a start kit it will start. It won't run very efficiently though. Throw a 35 cap on there, it will be better than nothing. If you really want to get the right cap, try a bunch of different ones and use the one that gives the lowest amp draw on C of the compressor.
    Seriously man? I hope that was a joke.

    Lets do this the correct way. 2652 x Amps / Voltage across cap ='s required cap size. It can be done in under 30 seconds. When you guys have one of those cap's that looks like it had been in the ocean and can't read the #'s, use that formula. Will work every time. You get your amps to plug in the formula off your start wire (herm) coming off cap. Your voltage comes from (c) and (herm).

  6. #6
    Join Date
    Nov 2011
    Location
    St. Louis
    Posts
    7,473
    Post Likes
    Quote Originally Posted by BagsOfFlex View Post
    Seriously man? I hope that was a joke.

    Lets do this the correct way. 2652 x Amps / Voltage across cap ='s required cap size. It can be done in under 30 seconds. When you guys have one of those cap's that looks like it had been in the ocean and can't read the #'s, use that formula. Will work every time. You get your amps to plug in the formula off your start wire (herm) coming off cap. Your voltage comes from (c) and (herm).
    Uh...I believe this formula is for determining what a cap is actually measuring under load - not what it's supposed to be...
    Is the Religious Right to blame for Christianity's decline?

    They argued that, as the Religious Right became increasingly visible and militant, it became associated with Christianity itself. And if being a Christian meant being associated with the likes of Jerry Falwell, many people—especially political moderates and liberals—decided to simply stop identifying as Christians altogether.

    http://www.theamericanconservative.c...nitys-decline/

  7. #7
    Join Date
    Apr 2012
    Location
    Charlotte Area NC
    Posts
    848
    Post Likes
    Correct

  8. #8
    Join Date
    Jun 2014
    Location
    Anderson County, SC
    Posts
    145
    Post Likes
    Quote Originally Posted by hurtinhvac View Post
    Uh...I believe this formula is for determining what a cap is actually measuring under load - not what it's supposed to be...
    Dang, yes this formula does determine the correct size of the field capacitor.

  9. #9
    Join Date
    Apr 2012
    Location
    Charlotte Area NC
    Posts
    848
    Post Likes

    Compressor does have run cap

    The link has more info than that, says it isn't reliable to calculate "needed" uf..

  10. #10
    Join Date
    Nov 2011
    Location
    St. Louis
    Posts
    7,473
    Post Likes
    Quote Originally Posted by BagsOfFlex View Post
    Dang, yes this formula does determine the correct size of the field capacitor.
    Negative. It does not determine the correct size needed. It merely determines what the installed cap is actually delivering.
    Is the Religious Right to blame for Christianity's decline?

    They argued that, as the Religious Right became increasingly visible and militant, it became associated with Christianity itself. And if being a Christian meant being associated with the likes of Jerry Falwell, many people—especially political moderates and liberals—decided to simply stop identifying as Christians altogether.

    http://www.theamericanconservative.c...nitys-decline/

  11. #11
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by BagsOfFlex View Post
    Dang, yes this formula does determine the correct size of the field capacitor.
    No, it only tells you the capacitor's uF under load. Not what size capacitor to use.

  12. #12
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Quote Originally Posted by craig1 View Post
    If it has a start kit it will start. It won't run very efficiently though. Throw a 35 cap on there, it will be better than nothing. If you really want to get the right cap, try a bunch of different ones and use the one that gives the lowest amp draw on C of the compressor.
    This way should work when you have no way of getting model numbers. Is there a tag on cabinet saying total amps ?

  13. #13
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    19,249
    Post Likes
    Quote Originally Posted by BagsOfFlex View Post
    Dang, yes this formula does determine the correct size of the field capacitor.
    I would suggest you try this experiment on your next service call:

    Test a known good, properly sized capacitor, (say a 40 mfd) with the formula, then replace the capacitor with a known good capacitor that is 10 mfd lower (a 30 mfd). Re-run the test, and see what your results show.

    Then come back on here and explain what you found.
    Instead of learning the tricks of the trade, learn the trade.

  14. Likes kdean1 liked this post.
  15. #14
    Join Date
    Apr 2012
    Location
    Charlotte Area NC
    Posts
    848
    Post Likes
    I guess the test was never performed

  16. #15
    Join Date
    Jan 2014
    Posts
    83
    Post Likes
    Quote Originally Posted by Danielandersen2 View Post
    I guess the test was never performed
    Doing that on my 4 ton ac tomorrow. Lets find out together.

  17. #16
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    Quote Originally Posted by crispE View Post
    Doing that on my 4 ton ac tomorrow. Lets find out together.
    Sometimes it's more expedient to just take someone else's word for something, especially when there are several someone elses saying exactly the same thing. A large number of people in agreement doesn't mean that they're correct, but in this case they are indeed correct.
    I apply the capacitance formula almost on a daily basis. You measure the voltage across the capacitor terminals, and then the amperage of the start lead coming off of the capacitor. The actual capacitance of the capacitor is then

    2653 x start amps/ capacitor voltage

    This only works on sinusoidal 60 hz power sources BTW. You can plug the capacitor directly into a wall outlet and use this formula to determine the capacitance value. Somebody tell me, "what size capacitor is the wall outlet supposed to have connected to it?" If that question doesn't make sense, reread the thread.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •